Results 1 to 18 of 18
Thread: PTC & NTC Probes.
30-05-2008, 11:37 PM #1
PTC & NTC Probes.
Can anyone give advice on the correct way to test PTC & NTC probes please.
30-05-2008, 11:42 PM #2
Re: PTC & NTC Probes.
Check the resistance against a table supplied by the manufacturer.
and go get a cuppa
30-05-2008, 11:45 PM #3
30-05-2008, 11:59 PM #4
31-05-2008, 12:01 AM #5
31-05-2008, 12:05 AM #6
31-05-2008, 12:05 AM #7
31-05-2008, 12:14 AM #8
A quick look around the web seems to show that a set voltage will give a set resistance.
Have a read here, maybe it will help...
A glossary slightly modified from that given in a US government publication: MIL-PRF-23648D. Note that the term being described is in bold typeface.
A thermistor is a thermally sensitive resistor that exhibits a change in electrical resistance with a change in its temperature. The resistance is measured by passing a small, measured direct current (dc) through it and measuring the voltage drop produced.
The standard reference temperature is the thermistor body temperature at which nominal zero-power resistance is specified, usually 25°C.
The zero-power resistance is the dc resistance value of a thermistor measured at a specified temperature with a power dissipation by the thermistor low enough that any further decrease in power will result in not more than 0.1 percent (or 1/10 of the specified measurement tolerance, whichever is smaller) change in resistance.
The resistance ratio characteristic identifies the ratio of the zero-power resistance of a thermistor measured at 25°C to that resistance measured at 125°C.
The zero-power temperature coefficient of resistance is the ratio at a specified temperature (T), of the rate of change of zero-power resistance with temperature to the zero-power resistance of the thermistor.
A NTC thermistor is one in which the zero-power resistance decreases with an increase in temperature.
A PTC thermistor is one in which the zero-power resistance increases with an increase in temperature.
The maximum operating temperature is the maximum body temperature at which the thermistor will operate for an extended period of time with acceptable stability of its characteristics. This temperature is the result of internal or external heating, or both, and should not exceed the maximum value specified.
The maximum power rating of a thermistor is the maximum power which a thermistor will dissipate for an extended period of time with acceptable stability of its characteristics.
The dissipation constant is the ratio, (in milliwatts per degree C) at a specified ambient temperature, of a change in power dissipation in a thermistor to the resultant body temperature change.
The thermal time constant of a thermistor is the time required for a thermistor to change 63.2 percent of the total difference between its initial and final body temperature when subjected to a step function
The resistance-temperature characteristic of a thermistor is the relationship between the zero-power resistance of a thermistor and its body temperature.
The temperature-wattage characteristic of a thermistor is the relationship at a specified ambient temperature between the thermistor temperature and the applied steady state wattage.
The current-time characteristic of a thermistor is the relationship at a specified ambient temperature between the current through a thermistor and time, upon application or interruption of voltage to it.
The stability of a thermistor is the ability of a thermistor to retain specified characteristics after being subjected to designated environmental or electrical test conditions.Brian - Newton Abbot, Devon, UK
31-05-2008, 12:14 AM #9
Warm them up and cool them down and see if the resistance changes, as Chillin says you will need a chart to check e.g. 1200 ohms at 20 c 400 ohms at 5 c.
Or put a new one on and see if its reading the correct temperature now. It would be wise to check what offsets have been programed into the control the probe is wired to as it may have been adjusted for whatever reason.
Or do as Brian says.......MUST TYPE QUICKER
JonLast edited by monkey spanners; 31-05-2008 at 12:17 AM. Reason: slow digits
31-05-2008, 12:21 AM #10
31-05-2008, 12:23 AM #11
Hi Testech.
Follow the link supplied below.
Download Tech Bulletin No 15.
And on the first page of 21 detailed pages is how to test ntc and ptc probes.
http://www.invensyscontrolseurope.co...lBulletins.htm
31-05-2008, 01:51 PM #12
Thank's Guys, I sure have a lot of info to work on now !
01-06-2008, 09:12 AM #13
The answer they expected was perhaps simple, when warming up the sensor, the resistance increases for a PTC and decreases for an NTC.
Most modern small controllers like Eliwell, Dixell accept both and you have to program this in the instrument.
Eliwell NTC's have a blue wire and PTC a grey wire.
If you connect a PTC to a controller which was programmed for an NTC you will see +/- 110°C (230°F) for +/-20°C (68°F) ambient.It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
01-06-2008, 07:15 PM #14
and go get a cuppa
01-06-2008, 08:57 PM #15
Very simple.....
PTC is 1k ohm
NTC is 10K ohm
Chemi
06-06-2008, 06:50 PM #16
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
06-06-2008, 07:14 PM #17
Transvestites are men who like to eat, drink, and be Mary.
06-06-2008, 10:01 PM #18
Wow, just change the probe. I dont have the time to mess around on site and would be surprised if you all did. I mean that in the nicest possible way of course!!
K type Probes "Where can i get them UK"
By 4Qman in forum Tools and CalculatorsReplies: 5Last Post: 25-11-2007, 04:26 PM -
Electronic controller probes wired wrong
By Electrocoolman in forum Trouble ShootingReplies: 3Last Post: 12-11-2007, 06:39 PM -
thermomax 100 probes
By john howie in forum IndustrialReplies: 11Last Post: 27-01-2007, 06:58 PM -
Why cant the industry standardise probes
By Latte in forum Chit Chat & Service StoriesReplies: 3Last Post: 25-11-2006, 09:23 PM