    AHU drains



    Hi all,

    Can anyone explain to me how to work out the size of a trap off of a ducted AHU. The trap should be equal to the suction pressure, what does this mean?

    thanks



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: AHU drains

    The pressure on the suction side of the fan must not be greater than the "lock" created by the water inside the trap.

    First you have to decide what this pressure is likely to be, then convert it in to something useful like "mm of Water column" (Hint: 1 bar = 10 meter of WC).

    Say that you have designed the AHU and it's ductwork to operate with a pressure of -10mBar, then:
    0.01 x 10 = 0.1 meter or 100 mm
    In this example, 100 mm would be the MINIMUM height of the water in the trap.

    In real life,
    Make the trap as big as you can, also remember to put 2 unions in it so it can be taken apart for cleaning purposes.

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: AHU drains

    And don't forget to fill it with water when it is installed.

    If not then the suction pressure can keep it dry and allow the coil drain pan to overflow.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Feb 2007
    Location
    Bedford
    Posts
    38
    Rep Power
    0

    Re: AHU drains

    Viking is right make the as big as you can, You dont want a call back and the evaporator tray is full of water, and its leaked all into the ceiling or floor.

    Freecool

  5. #5
    Join Date
    May 2008
    Location
    UK
    Posts
    170
    Rep Power
    16

    Re: AHU drains

    Thanks guys

    I'll give em some depth as I think calculating precise measurements will be a bit of a bore, no pun intended.

  6. #6
    Join Date
    Jun 2005
    Location
    California
    Posts
    394
    Rep Power
    19

    Re: AHU drains

    This is an excellent article on the subject.
    http://hvacindia.org.in/journals/2002oct/article05.html

Similar Threads

  1. drains
    By Temprite in forum Commercial
    Replies: 10
    Last Post: 24-03-2008, 07:41 PM
  2. condensate drains
    By bangoman in forum Air Conditioning
    Replies: 3
    Last Post: 27-01-2008, 06:00 PM
  3. Drains Legislation
    By Mike6994 in forum Technical Discussions
    Replies: 4
    Last Post: 03-12-2007, 10:10 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •