    carrier 30hs 160



    hey everyone! I'm working on a older carrier chiller and im in the process of checking the individual tubes in the chiller barrel and was wondering if anyone knows how many tubes can be plugged before it affects the capacity. there are two seperate circuits each with 129 tubes that are 5/8in dia and 9' 2 1/2" long. its a 160 ton unit, any help will be appreciated



  2. #2
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    53
    Posts
    282
    Rep Power
    15

    Re: carrier 30hs 160

    is 10 % of the total tube that can cancel during your case would be 12 as maximum permitted by any manufacturer

  3. #3
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24

    Re: carrier 30hs 160

    .

    10% plugged tubes at random is considered acceptable.

    You may want to reconsider this if the defective tubes are all grouped together as it may show an underlying problem and affect the evaporators performance.

    Any more than that will need a re-tube, which can be done but is a first-class hassle in terms of work and cost - it may not be viable with a chiller that age.

    You may want to look at your TEV after you plug any amount of tubes to make sure that the superheat is still within acceptable limits, especially at reduced loads.

    One other thing with Carrier chillers of a certain vintage: the TEV entry point, if I recall, is at the base of the evaporator tube sheet and the suction exit is at the top. Carrier evaporators are configured with the water entry and exit points at the top of the bundle and a set of weirs inside that direct the water flow up and down, contra-flow over the tubes. Over time in non-sealed systems sediment may collect in the lowest points and block off some of the lowest tubes, affecting performance to the point where the evaporator becomes seriously undersized due to the reduced water contact. This is the part where the risk of tube-stress is greatest.

    If you have that many tubes to plug and are at the stage of invasive surgery, so to speak, why not drift a few tubes out and have a look at the cause of any damage suspected?


    .
    Last edited by Argus; 29-10-2009 at 10:07 AM.

  4. #4
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: carrier 30hs 160

    As p earlier posts the max recommended by Carrier is 10%, are they leaking internally or at the tube sheets.
    Carrier can supply Elliott two peice brass blanking plugs. If you are going to remove tubes, they have stay tubes that are crimped to position the internal plastic baffle plates in position. They are not removable and should be plugged if leaking internally, they are indicated in the service and installion manual supplied with chiller if you can find the manual.
    If tubes are leaking at tube sheet first try hand re-rolling with tube expander.

  5. #5
    Join Date
    Nov 2005
    Location
    Ireland
    Posts
    23
    Rep Power
    0

    Re: carrier 30hs 160

    Quote Originally Posted by Magoo View Post
    As p earlier posts the max recommended by Carrier is 10%, are they leaking internally or at the tube sheets.
    Carrier can supply Elliott two peice brass blanking plugs. If you are going to remove tubes, they have stay tubes that are crimped to position the internal plastic baffle plates in position. They are not removable and should be plugged if leaking internally, they are indicated in the service and installion manual supplied with chiller if you can find the manual.
    If tubes are leaking at tube sheet first try hand re-rolling with tube expander.
    Hi All,

    Sorry for hijacking your post Joshieboy but it might be of assistance to you as well.
    We have also found a leak in one of the evaporator tubes and have got the Elliott two brass piece of Carrier to plug the tube. Our problem is, the leak is in one of the swagged tubes but it is also next to the cross separator of the 1st and 2nd pass of the end plate so we can't use the Elliott piece at that end (the lip of the brass ring is in the way). Is there tapered plugs that can be used to seal the tubes available from a UK wholesaler, the ones here in Ireland don't know what I'm talking about.

    Thanks in advance

  6. #6
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: carrier 30hs 160

    Trim the side off to clear partition divider, so long as you have at least half the shoulder there, it is there to stop the whole thing going up the tube. Don't forget the loctite on taper plug and barrell outer sealing to tube, clean tube surface and use the loctite cleanining spray as well.

  7. #7
    Join Date
    Nov 2005
    Location
    Ireland
    Posts
    23
    Rep Power
    0

    Re: carrier 30hs 160

    Thanks for your reply Magoo

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. carrier fault codes
    By richelli in forum Trouble Shooting
    Replies: 5
    Last Post: 18-06-2010, 07:35 AM
  3. carrier 30HS
    By Joeheath in forum Air Conditioning
    Replies: 8
    Last Post: 24-11-2009, 08:59 PM
  4. Carrier Pro Dialog Plus help
    By borodave1973 in forum Air Conditioning
    Replies: 5
    Last Post: 11-11-2007, 06:47 PM
  5. carrier remote
    By superswill in forum Trouble Shooting
    Replies: 2
    Last Post: 26-04-2006, 09:17 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •