    Expansion Joints in the cold store floor



    Though out of many installations, we never faced any probloems due to expaiosn joints in the cold store flooring, in one case since the RCC has shrunk a lite bit near the cold store doors, it had created lots of problems on the Bottom gaskets.

    The Cold store is @ 60 x 40 x 12 M in size. There are Four doors , 2 on each side of 40 m side.

    The Architech had no clue on this shrinkages & its effects. Are there any rules / logics on doing the expansions joints in the flooring?



  2. #2
    Join Date
    Sep 2006
    Location
    Venezuela
    Posts
    259
    Rep Power
    18

    Re: Expansion Joints in the cold store floor

    smpsmp45
    Normally the upper slap is a floting block. It is 150 to 200mm thick and it rests over the isolation bed of poliurethene or polistirene sheet. As you know between the slap and the isolation one instal a polipropilene film 100micrones in order the upper slap slide over the isolation sheet.
    When you cool down (very slowly) the cold room, you will have a a litle shrick all around. It is more or less 5 mm.
    After the cold room arrive its final temperature we seal the groove with a plastic sealeant for low temperature applications.
    I hope it may help
    regards
    gwapa

  3. #3
    Join Date
    May 2007
    Location
    India
    Posts
    688
    Rep Power
    17

    Re: Expansion Joints in the cold store floor

    Hi Gwapa,

    That is what we are doing & have experienced over last 15 years or so. Only in One case, suffenly we came across this issue. Though may be someone else has faced this as well?

Similar Threads

  1. Cold room floor
    By Andy AC in forum Commercial
    Replies: 8
    Last Post: 19-02-2009, 04:26 PM
  2. Replies: 15
    Last Post: 17-06-2008, 11:07 PM
  3. Freezer Floor Patch and Expansion Joints
    By nh3wizard in forum Technical Speculations
    Replies: 4
    Last Post: 04-09-2006, 08:30 PM
  4. expansion valve aint cold
    By justinworne in forum Trouble Shooting
    Replies: 6
    Last Post: 26-07-2006, 10:52 PM
  5. Low Temperature Cold Store
    By iceman007 in forum Commercial
    Replies: 12
    Last Post: 16-11-2005, 11:23 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •