Thread: Tev Question
    Aug 2003
    Puerto Rico
    Tev Question
    Ok I have this unit it haves a low temp 1/2 horsepower 404A condensing unit remote unit 50 feet away is de refrigeration unit with a 1/4 evaporator coil I want a 32-40F temp what type of valve I would use???
    Feb 2001
    Tampa Florida
    1,076
    Your information is lacking. But if you have a unit that requires 3,000 btu/hr, then a 1/4 ton TEV would be appropriate. If the evaporator is equipped with a distributor, then you require an externally equalized TEV.
    The matter of location distance between the evaporator and condensing unit does not alter the size of the TEV, so if the refrigerator already has a TEV just use the one the manufacturer provided.
    St. Louis, MO
    509
    Depending upon where the compressor and evaporator balance at desired operating conditions, you may need an evaporator pressure regulator (EPR), or a crankcase pressure regulator (CPR), or perhaps both.
    If suction pressure runs too low for your desired 32-40F temperature, causing a high TD, then an EPR would be necessary. If suction pressure runs too high for compressor operation, then a CPR would be necessary.
    More information concerning the components would help here.
    Prof Sporlan
  1. Newbie with a question
    By AcidSlasher in forum Fundamentals
    Last Post: 07-03-2006, 11:20 AM
  2. quizy type question thingy
    By rbartlett in forum Chit Chat & Service Stories
    Last Post: 06-02-2006, 09:22 PM
  3. Quick question about using a fridge in an RV
    By Definca in forum Fundamentals
    Last Post: 19-07-2005, 07:43 AM
  4. A/C Question
    By Latte in forum Air Conditioning
    Last Post: 24-08-2004, 08:19 PM
  5. Urgent, Kirchoff question
    By Peter_1 in forum Fundamentals
    Last Post: 20-01-2004, 03:12 PM