    Ok I have this unit it haves a low temp 1/2 horsepower 404A condensing unit remote unit 50 feet away is de refrigeration unit with a 1/4 evaporator coil I want a 32-40F temp what type of valve I would use???



  2. #2
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25
    Your information is lacking. But if you have a unit that requires 3,000 btu/hr, then a 1/4 ton TEV would be appropriate. If the evaporator is equipped with a distributor, then you require an externally equalized TEV.

    The matter of location distance between the evaporator and condensing unit does not alter the size of the TEV, so if the refrigerator already has a TEV just use the one the manufacturer provided.

  3. #3
    Join Date
    Mar 2001
    Location
    St. Louis, MO
    Posts
    509
    Rep Power
    24
    Depending upon where the compressor and evaporator balance at desired operating conditions, you may need an evaporator pressure regulator (EPR), or a crankcase pressure regulator (CPR), or perhaps both.

    If suction pressure runs too low for your desired 32-40°F temperature, causing a high TD, then an EPR would be necessary. If suction pressure runs too high for compressor operation, then a CPR would be necessary.

    More information concerning the components would help here.
    Prof Sporlan

Similar Threads

  1. Newbie with a question
    By AcidSlasher in forum Fundamentals
    Replies: 4
    Last Post: 07-03-2006, 11:20 AM
  2. quizy type question thingy
    By rbartlett in forum Chit Chat & Service Stories
    Replies: 25
    Last Post: 06-02-2006, 09:22 PM
  3. Quick question about using a fridge in an RV
    By Definca in forum Fundamentals
    Replies: 1
    Last Post: 19-07-2005, 07:43 AM
  4. A/C Question
    By Latte in forum Air Conditioning
    Replies: 4
    Last Post: 24-08-2004, 08:19 PM
  5. Urgent, Kirchoff question
    By Peter_1 in forum Fundamentals
    Replies: 4
    Last Post: 20-01-2004, 03:12 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •