    Fujitsu iceing up.



    Hi everyone.
    Fujitsu split air con Mod:AOY36ACF3L:
    Indoor evap is heavaly iced, checked cond on roof also ice on suc pipe back to accumilator, for now have turned unit off to defrost, have not connected guages until defrost is complete, will then run system to check..Any ideas why so much build up of ice??
    Unit is cooling security control room with quite a bit of kit in there as well as personel, outdoor unit does have thermostat for defrosts, is it worth increasing num of these also..
    Thanks in advance..



  2. #2
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: Fujitsu iceing up.

    1) Lack of airflow, ie ductwork/filter/fan not correct
    2) Short of refrigerant
    3) Set too low a temperature
    4) control system fault (thermistor, tx valve etc)

    These apply no matter what system you're looking at. It's usually one of these that causes indoor coil ice up
    Last edited by paul_h; 06-05-2008 at 12:38 PM.

  3. #3
    Join Date
    Mar 2005
    Location
    Lanzarote
    Age
    41
    Posts
    372
    Rep Power
    20

    Re: Fujitsu iceing up.

    Could it be something similar to what was happening in this thread http://www.refrigeration-engineer.co...ead.php?t=5926 (scroll down a bit)

  4. #4
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: Fujitsu iceing up.

    If the outdoor unit continues to cool even when the indoor coil has ice on it then the coil frost prevention function is not operating or the unit has no coil frost prevention mode.
    Typical problem when low air humidity in the occupied space such as computer rooms.
    1/Confirm with equipment supplier what the coil frost prevention mode specification is.
    2/ Measure the RH & WB on coil conditions to see if the unit is operating within the manufacturers indoor temperature limits.

  5. #5
    Join Date
    Sep 2007
    Location
    England
    Age
    53
    Posts
    55
    Rep Power
    17

    Re: Fujitsu iceing up.

    Thanks guy's, unit short of gas..

  6. #6
    Join Date
    Feb 2007
    Location
    SIDE OF THE ROAD
    Posts
    262
    Rep Power
    18

    Re: Fujitsu iceing up.

    hi

    my thinking of short of gas is a low temp after expansion and icing up at the start of the evaparator and then coming back on the suction warm resulting in high discharge...i have never come across a system short of gas icing back to the compressor....this to me would be blend incorrect i.e 407c or filter/fan/coil problem anyone agree?

    rgrd phil

  7. #7
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Fujitsu iceing up.

    The thing with a/c low gas charge is that the evaporator starts to ice up and reduce the airflow over the coil.

    The liquid within the frozen section then moves along the coil to find somewhere to boil off. Eventually the whole coil is blocked solid and the evaporation now continues along the suction line and accumulator.

    If it isn't a gas shortage then it can also be a stuck compressor relay running the motor when the evaporator fan is off.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  8. #8
    Join Date
    Feb 2005
    Location
    Aberdeen
    Age
    48
    Posts
    168
    Rep Power
    20

    Re: Fujitsu iceing up.

    Compressor relay comes to mind. Especially on ye ole fujitsu's

    Jase

  9. #9
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: Fujitsu iceing up.

    Quote Originally Posted by Jase View Post
    Compressor relay comes to mind. Especially on ye ole fujitsu's

    Jase
    Only the small ones with the comp relay on the indoor PCB. Not larger ones like this aoy36.

Similar Threads

  1. your opinons on fujitsu please
    By acgibo in forum Air Conditioning
    Replies: 18
    Last Post: 26-08-2009, 05:06 PM
  2. Fujitsu or not?
    By LRAC in forum Air Conditioning
    Replies: 14
    Last Post: 29-08-2007, 09:45 AM
  3. desperately seeking fujitsu
    By rbartlett in forum Air Conditioning
    Replies: 7
    Last Post: 04-08-2007, 09:06 PM
  4. R22 Fujitsu FCUs on new Inverter Multi-Condenser?
    By Makeit go Right in forum Air Conditioning
    Replies: 3
    Last Post: 09-01-2007, 11:22 PM
  5. Fujitsu
    By Abe in forum Air Conditioning
    Replies: 9
    Last Post: 21-07-2006, 08:36 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •