    Single Phase Compressor Connections



    Have you ever wondered which way around the 3 connections go on a single phase Compressor Motor?

    Open the attached and print of for a useful reminder.

    See page 2 for diagram!
    Cheers Grizzly



  2. #2
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Single Phase Compressor Connections

    Nice one Grizzly..

    taz

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Single Phase Compressor Connections

    And when using a multimeter....

    For a single phase compressor your highest resistance reading between any two connection points should be found from the start (S) terminal to the run (R) terminal.

    Once you determine where you get your highest
    reading, this will identify the common (C) terminal as
    the terminal you were not using when you found the
    highest reading.

    Write down or remember the highest reading value for the moment.

    The next test will be from the common (C) terminal to each of the other two compressor terminals, S and R.

    Whichever has the highest reading from the common (C) terminal will be the start (S) winding terminal and the lowest reading will be from the common (C) terminal to the run (R) terminal.

    If the compressor windings are good the resistance values will add up correctly. For example, if the highest reading found was 10.5 ohms (S to R). Then the next highest reading was 8.4 (C to S), then the lowest would have to be 2.1 (C to R) for the compressor windings to be good. (C to S) + (C to R) =
    (S to R) would indicate the compressor windings are
    good for a single phase compressor.

    Normally your readings may not be exact to the decimal point (your meter could round up or down the values) but should be really close if the compressor windings are good.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

Similar Threads

  1. start single phase capacitor
    By dear.mr.davidov in forum Electrical
    Replies: 7
    Last Post: 13-07-2010, 07:25 AM
  2. Replies: 15
    Last Post: 17-04-2009, 03:50 PM
  3. SR2 50 models electric SBY diagonostics made simple
    By absolute-zero in forum Transport
    Replies: 5
    Last Post: 04-01-2008, 05:11 PM
  4. Variable speed drives for single phase motors
    By PRESS in forum Air Conditioning
    Replies: 10
    Last Post: 10-12-2007, 07:23 PM
  5. Single phase contactor
    By Andy T in forum Commercial
    Replies: 9
    Last Post: 23-10-2006, 01:45 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •