    E5 alarm on Daikin 3MXS52E -outdoor unit.



    Hello!

    Outdoor :3MXS52EV1B
    Indoor :2pcs FTXS25D3, one FTXS35D.

    Customer's got several times alarm's on outdoor unit. Latest alarm was E5 when i checked. I reset alarm and connect RSUK0919 -monitor and test four hours. Everything seem's to be a normal and no alarms.
    I put heating mode and 29 celsius set temp with autofan every three indoor units to get heavy load but no E5.
    Totally pipe line is 55m and customer added 500grams R410a.

    Sample of RSUK monitor's data :

    OUTDOOR :
    Freq HZ:102
    Current :12,2 Amp (Max)
    OutdrTH: 12,5 c
    Heatex :1,5 c
    DischTH :83 c
    FinTH :31 c
    OutFan :660rpm

    INDOOR
    Req Freq :F9
    IntakeTH :29 c
    LiquidTH :53
    Fan :M

    Have anyone guess what's causing problem?
    Last edited by basti; 23-04-2008 at 05:37 PM.



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: E5 alarm on Daikin 3MXS52E -outdoor unit.

    I'm afraid that you are operating the system outside of the design specification.

    The maximum allowable equivalent pipe length is 50m total, with a trim charge of 0.02kg/m above 30m.

    If you have added 0.5kg, it is overcharged as well as over piped.

    This is obviously putting a strain on the compressor at certain operating conditions, hence the E5 fault.

    What is the level difference of the indoor units?

  3. #3
    Join Date
    Jul 2007
    Location
    Finland
    Age
    55
    Posts
    20
    Rep Power
    0

    Re: E5 alarm on Daikin 3MXS52E -outdoor unit.

    Quote Originally Posted by frank View Post

    What is the level difference of the indoor units?
    Level difference is only 2m. (Residential house).
    Last edited by basti; 24-04-2008 at 07:37 PM.

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: E5 alarm on Daikin 3MXS52E -outdoor unit.

    The only thing I can say then is that operating any system outside of the manufacturers recommendations will lead to unexpected situations.

    Until the system has been modified to be within the limits, and then operating conditions compared, there is not a lot more to add.

    What you are really asking at the moment is " is there anything I can do to make it work as it would if it were installed correctly?"

  5. #5
    Join Date
    May 2008
    Location
    spain
    Age
    54
    Posts
    63
    Rep Power
    16

    Re: E5 alarm on Daikin 3MXS52E -outdoor unit.

    hello just confirming what Frank has said it is overcharged and has exceeded the manufacturers recommended pipe lengths.
    Try decreasing the pipelength by five meters and take out 100 grammes.

  6. #6
    Join Date
    May 2006
    Location
    aberdeen
    Posts
    124
    Rep Power
    18

    Re: E5 alarm on Daikin 3MXS52E -outdoor unit.

    Hi Basti,.
    Sounds like your compressor is having problems. Did you check your voltage to the compressor when running?.
    Your data looks like high currant for the frequency its at. Never a good idea to exceed the max pipe length.

  7. #7
    Join Date
    Jul 2007
    Location
    Finland
    Age
    55
    Posts
    20
    Rep Power
    0

    Re: E5 alarm on Daikin 3MXS52E -outdoor unit.

    Quote Originally Posted by stuartwking View Post
    Hi Basti,.
    Sounds like your compressor is having problems. Did you check your voltage to the compressor when running?.
    Your data looks like high currant for the frequency its at. Never a good idea to exceed the max pipe length.
    .
    They replace whole outdoor unit and it's have been working now about 2 weeks without any alarms.

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: E5 alarm on Daikin 3MXS52E -outdoor unit.

    Quote Originally Posted by basti View Post
    .
    They replace whole outdoor unit and it's have been working now about 2 weeks without any alarms.
    That is most dullness (and personally humiliating) option for any service technician.

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Daikin not working... many problems
    By stankovicv in forum Air Conditioning
    Replies: 26
    Last Post: 11-12-2010, 09:01 AM
  3. Dunham Bush Chiller Alarm
    By Regulator in forum Air Conditioning
    Replies: 11
    Last Post: 08-12-2010, 01:42 AM
  4. Daikin, Why do we bother?
    By gwilliamson in forum Air Conditioning
    Replies: 21
    Last Post: 02-02-2010, 09:38 AM
  5. Daikin Comp and inverter
    By WCC73 in forum Air Conditioning
    Replies: 5
    Last Post: 08-11-2008, 08:44 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •