Results 1 to 8 of 8
Thread: start single phase capacitor
15-04-2008, 12:45 PM #1
hi
i have fan motor (230 V) without label how i can select capacitor for it.
15-04-2008, 02:22 PM #2
Re: start single phase capacitor
What does it do, CF motor, ducted evap motor etc?
Was this motor just laying around, or is it in a system with a capacitor already in there?
Depending on size and duty, most fan motors have 5uF to 20uF
Got any testing equipment and spare capacitors?
Normally small motors are 5uf or less (so 5uf would be fine), small ducted motors are 10-15uf, and the large 4amp twin shafts are 20uF. But most of the larger units have stuff stamped on rather than a sticker. How many wires does it have going to it?
Capacitors don't have to be exact, they are rated at +-10% from the factory anyway. But without a clue of it's size or what it does, no one can help you better.
edit: Also fans don't have a start relay, so they generally don't have start capacitors, they have a split capacitor setup.Last edited by paul_h; 15-04-2008 at 02:30 PM.
23-04-2008, 06:55 PM #3
Plug the motor to mains, start it by hand and mesure the current (amp's). Get another motor with the same AMP's, and get the capacytor value.
24-04-2008, 08:57 AM #4
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
07-07-2010, 08:40 PM #5
There should be a uf rateing on the motor data plate, or ring the manufacture
12-07-2010, 06:17 PM #6
hi, kinz there book called kotza, if you look page 347 ,you found how to size capacitor for motor .it is rating current x 14.+-10%. correct me if i am wrong.
13-07-2010, 07:04 AM #7
Basically motor capacitors perform two functions. The first function is to start the motor and the second function is to run the motor. Some motors only require a run capacitor others require both a start and a run capacitor.
You'll have to tell us the wattage or horsepower rating of the motor for us to better answer your question. Any other information regarding the motor's former use would be helpful such as ;was it used in a fan, was it used to drive a compressor, etc.?
In these two instances a fan only needs a run capacitor because the starting torque requirements are low whereas a compressor motor usually starts against a load and needs a start capacitor to increase the starting torque.
13-07-2010, 07:25 AM #8
In general terms capacitors for most motors can be calculated using the formula below.
(2650 x Amps) divided by the Voltage
= Micro Farads.
Do consider the type of motor it is, capacitors are used for different reasons, dependant on the starting characteristics of the motor
marstair beer cellar unit
By airconadam in forum Air ConditioningReplies: 9Last Post: 11-04-2008, 10:40 PM -
Hermetic analyzer " ANNIE" how do they work
By kengineering in forum Tools and CalculatorsReplies: 11Last Post: 02-03-2008, 06:10 PM -
SR2 50 models electric SBY diagonostics made simple
By absolute-zero in forum TransportReplies: 5Last Post: 04-01-2008, 05:11 PM -
Variable speed drives for single phase motors
By PRESS in forum Air ConditioningReplies: 10Last Post: 10-12-2007, 07:23 PM -
Capacitor Start Motor
By bryan2392 in forum ElectricalReplies: 7Last Post: 27-01-2006, 07:17 PM