Thread: Dixell Xc 911m
    wolf-zemun's Avatar
    wolf-zemun Guest
    Dixell Xc 911m
    Is Anybody Works With Dixell Xc 911m? I Need Help About Connecting Probe Input. If Anybody Have Electric Shema....but Not From Dixell, I Have It. Thanks!
    11,024
    Re: Dixell Xc 911m
    Hello and welcome to the forum.
    What is the problem you are having with connecting the probes?
    The wiring schematic clearly shows the connections.
    wolf-zemun's Avatar
    wolf-zemun Guest
    Re: Dixell Xc 911m
    Yes, but when I conncet they don't show right value and occure alarm A01F. When I switch polarity then occure alarm Er0H.
    Split Croatia
    57
    6,151
    36
    Re: Dixell Xc 911m
    Quote Originally Posted by wolf-zemun View Post
    Check your probe and configuration:
    5.3.2 Condensing probe configuration
    Pbc: Probe selection. Cur = 4 ÷ 20 mA probe; ntc = NTC probe.
    PA04: Adjustment of read out corresponding to 4mA (present only if Pbc=Cur). input
    signal, given by the suction probe (0 ÷30 bar or 0÷435 PSI or 0 ÷3000 KPA)
    Warning: set a value correspondent to absolute pressure. If the transducer measures
    relative pressure increase the range by 1 bar.
    E.I. PP30 relative pressure transducer, range: 0÷30bar. PA04=1; PA20=31.
    PA20: Adjustment of read out corresponding to 20mA input signal, given by the suction probe
    (0 ÷ 40.0 bar or 0÷580 PSI or 0 ÷ 4000 KPA) SEE THE WARNING IN PA04.
    CAL: Condensing probe calibration (-1.00÷1.00bar; -10.0÷10.0 °C or -20÷20°F/PSI or
    -100÷100KPA)
    Probe is NTC and polarity shouldn't be a issue.
  1. Dixell Controller
    By 4Qman in forum Electrical
    Last Post: 18-12-2007, 12:39 AM
  2. Dixell Clone
    By Peter_1 in forum Electrical
    Last Post: 20-01-2006, 07:54 AM
  3. Dixell controllers
    By eggs in forum Technical Discussions
    Last Post: 17-08-2005, 10:59 PM