Thread: Back to basics
-
28-07-2003, 11:49 PM #1
Back to basics
Hi There
This may be a bit basic for some of you out there but any info would be much appreciated!
If you have a standard setup with evaporator & Ex equalised tev what different symptoms are there from a blocked tev or a system thats very short of gas.
Thanks
Signed
New to this gameLast edited by charliewhite; 28-07-2003 at 11:59 PM.
-
29-07-2003, 02:28 AM #2
Naming a problem and figuring out the symptoms is backwards. The system tells you its symptoms, and you figure out the problem.
-
29-07-2003, 07:47 AM #3
Thanks for the reply
Here are the symptoms.
When the compressor starts up the head pressure initially rises but then like the suction pressure it drops till it trips out on low pressure.There is no hissing at the tev & no evidence of a leak.The sight glass tells me nothing( only thing I can say is that there are no bubbles, but could that be because its very low on gas )
Thanks
-
29-07-2003, 11:14 AM #4
Thanks Marc
I'll give it a go
Thanks
-
29-07-2003, 02:47 PM #5Originally posted by charliewhite
( only thing I can say is that there are no bubbles, but could that be because its very low on gas )
I interpret this as, "The sightglass is either full or empty (of liquid)". Of course the TEV not being noisy would tend to indicate a full head of liquid in the liquid line, but considering charliewhite's self proclaimed lack of experience, one would speculate whether he is familiar with the volume or nature of the noise that we refer to in regard to TEV operation. Particularly in consideration that he is not sure whether the sightglass is entirely empty or full (of liquid).
Last edited by herefishy; 30-07-2003 at 01:01 AM.
-
29-07-2003, 07:51 PM #6
what firm are you working for charlie?
-
30-07-2003, 12:44 AM #7
The pressure, and therefore the temperature, drops at the point of restriction. So the question is, following the liquid line from the condenser, at what point does it get cold?
-
01-08-2003, 05:59 PM #8
Usually the system that is very short of refrigerant will have a lot of flash gas feeding the valve and the evaporator will freeze up on the first rows of pipes.Low suction pressure,high superheat.
On a block TEV the liquid line is full,the valve present a ice build up in is body due to the blockcage.
Similar Threads
-
Back Pressure Valve
By guapo in forum Industrial CompressorsReplies: 2Last Post: 18-03-2006, 04:38 PM -
Flood Back After 2 years..
By Mahmoud in forum FundamentalsReplies: 10Last Post: 27-09-2005, 11:06 AM -
Compressor back pressure rating
By Cary in forum FundamentalsReplies: 9Last Post: 05-12-2004, 08:42 AM -
Can anybody back my theory up?
By Coolie in forum Trouble ShootingReplies: 5Last Post: 22-10-2004, 11:56 PM -
Low back pressure compressor application
By Abe in forum Technical DiscussionsReplies: 5Last Post: 31-07-2001, 11:43 PM