    Question Back to basics



    Hi There

    This may be a bit basic for some of you out there but any info would be much appreciated!

    If you have a standard setup with evaporator & Ex equalised tev what different symptoms are there from a blocked tev or a system thats very short of gas.

    Thanks

    Signed

    New to this game
    Last edited by charliewhite; 28-07-2003 at 11:59 PM.



  2. #2
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    Naming a problem and figuring out the symptoms is backwards. The system tells you its symptoms, and you figure out the problem.

  3. #3
    charliewhite's Avatar
    charliewhite Guest
    Thanks for the reply

    Here are the symptoms.

    When the compressor starts up the head pressure initially rises but then like the suction pressure it drops till it trips out on low pressure.There is no hissing at the tev & no evidence of a leak.The sight glass tells me nothing( only thing I can say is that there are no bubbles, but could that be because its very low on gas )

    Thanks

  4. #4
    charliewhite's Avatar
    charliewhite Guest
    Thanks Marc

    I'll give it a go

    Thanks

  5. #5
    Join Date
    Jan 2002
    Location
    Austin, Texas
    Posts
    716
    Rep Power
    23
    Originally posted by charliewhite
    ( only thing I can say is that there are no bubbles, but could that be because its very low on gas )

    I interpret this as, "The sightglass is either full or empty (of liquid)". Of course the TEV not being noisy would tend to indicate a full head of liquid in the liquid line, but considering charliewhite's self proclaimed lack of experience, one would speculate whether he is familiar with the volume or nature of the noise that we refer to in regard to TEV operation. Particularly in consideration that he is not sure whether the sightglass is entirely empty or full (of liquid).

    Last edited by herefishy; 30-07-2003 at 01:01 AM.

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51
    what firm are you working for charlie?

  7. #7
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    The pressure, and therefore the temperature, drops at the point of restriction. So the question is, following the liquid line from the condenser, at what point does it get cold?

  8. #8
    Gonzalo's Avatar
    Gonzalo Guest
    Usually the system that is very short of refrigerant will have a lot of flash gas feeding the valve and the evaporator will freeze up on the first rows of pipes.Low suction pressure,high superheat.

    On a block TEV the liquid line is full,the valve present a ice build up in is body due to the blockcage.

Similar Threads

  1. Back Pressure Valve
    By guapo in forum Industrial Compressors
    Replies: 2
    Last Post: 18-03-2006, 04:38 PM
  2. Flood Back After 2 years..
    By Mahmoud in forum Fundamentals
    Replies: 10
    Last Post: 27-09-2005, 11:06 AM
  3. Compressor back pressure rating
    By Cary in forum Fundamentals
    Replies: 9
    Last Post: 05-12-2004, 08:42 AM
  4. Can anybody back my theory up?
    By Coolie in forum Trouble Shooting
    Replies: 5
    Last Post: 22-10-2004, 11:56 PM
  5. Low back pressure compressor application
    By Abe in forum Technical Discussions
    Replies: 5
    Last Post: 31-07-2001, 11:43 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •