06-04-2008, 06:14 PM #11
Re: test hp cut out
I agree with the others.
No1 Test the switch with N2 or a hand pump if you have one (real ball ache if your doing hp though).
2nd Test by dropping the cond fan or blocking air flow over cond.
and C Test by front seating the discharge service valve if fitted (extreme care to be taken).
taz.
There are three types of engineer, Those who can count and those who can't.