    Fridge Quiz!



    During a recent service call to a six month old multi deck chiller I found the following evaporator arrangment. If from the following description you can picture these coils, then see if you can guess the symptoms the cabinet was suffering from.

    After the externally equalised TEV the evaporator feed tee's into the bottom of two sections of single pass evaporator coil. The return is connected to the top of the coil and from the coils tee's back into a common suction which has the TEV bulb attached. The coils are arranged in two equal sized sections one placed directly in front of the other so that the air on, passes through the first section then through the second.

    No faults were found with the condensing units.

    The cabinet is made up of two equal multiplexed sections and built into a restaurant as part of a £750,000 refit.



  2. #2
    Join Date
    Apr 2002
    Location
    Manchester UK city of rain
    Age
    51
    Posts
    37
    Rep Power
    0
    Marc,

    I have recommended that we repipe the evaporators so that the feed enters the rear evaporator at the top of the coil, leave’s at the bottom of the coil and onto the top of the front coil exiting at the bottom of this coil then returning to the condensing unit. This configuration would allow the TEV to operate correctly and prevent the refrigerant logging in the bottom passes of the coils.

    What do you think?

  3. #3
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25
    I am guessing that the front coil has a wider fin spacing and its intent is to dehumidify the air before it enters the second coil. Piping the coils the way you suggest would be the correct way to pipe them. If you have gas defrost, you may want to stick with the bottom feed, otherwise I agree with your solution.

  4. #4
    Join Date
    Apr 2002
    Location
    Manchester UK city of rain
    Age
    51
    Posts
    37
    Rep Power
    0
    Dan,

    The coils are identical and it only has ambient defrost, it just amazes me that even a small manufacturer can produce a cabinet like this. At the moment the TEV is closing right down, the lower passes of the coil are flooded with liquid and probably oil and the cabinet is only managing 13-14C , I have already had to change the condensate trays because they were too small. Also the air is allowed to pass by the coils at both ends and the condensers are recycling hot air and you have to be a contortionist to get gauges on to it.

    Thanks for confirming my thoughts on what to do, the only problem I have now is that I can't guarantee the customer that any modifications will gain the desired temperature of 3-5C. I have made that clear to them though and I don't think they will ask this manufacturer to make any more cabinets for them.

  5. #5
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25
    For beverage duty you will be able to make it work. Keep in mind, the customer bought a display case, not a refrigerator. I am surprised the manufacturer has not been contacted to make the repair. Regardless, Marc's observation and your solution both make sense.

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51
    Is the cabinet made by "Storer Refrigeration" ?

  7. #7
    Join Date
    Dec 2001
    Location
    nottingham
    Age
    62
    Posts
    96
    Rep Power
    23
    FRANK
    I can see why you think this may be a Storer cabinet, but they never manufactured a cabinet with that many flaws, they also always piped from the top of the first evap into the bottom of the next.
    see you later

    Jasper

  8. #8
    Join Date
    Apr 2002
    Location
    Manchester UK city of rain
    Age
    51
    Posts
    37
    Rep Power
    0
    Frank/Dan,

    The cabinet was custom made by Excel refrigeration for a shopfitting firm who asked me to look at it. The cabinet is required to run below 5C by the customer and normally holds sandwiches etc, although I can not be sure what specs were given to Excel. The shopfitting firm has told me that Excel are not being at all helpful as far as warranty repairs are concerned and have asked me to compile a report on the cabinet for them so that they can recover the repair costs.
    I'll take some pics with the digital camera before I make any alterations and post them on the site.

Similar Threads

  1. Replies: 1
    Last Post: 19-02-2006, 12:08 AM
  2. Help! fridge freezer probs
    By Glenreed in forum Trouble Shooting
    Replies: 2
    Last Post: 06-01-2006, 10:51 PM
  3. help- my bar fridge is wacko?!
    By ben in forum Trouble Shooting
    Replies: 3
    Last Post: 25-01-2002, 12:06 AM
  4. is my fridge working properly?
    By vincec in forum Trouble Shooting
    Replies: 1
    Last Post: 15-01-2002, 09:55 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •