    Exclamation Fire Alarm Shutdown



    Hello all,

    I am undertaking a site survey for a new client (offices) who has Mitsubishi ceiling cassettes supplied via MCB's back at the dis.board.........all perfectly normal there...or so I thought.

    I recognised that having spent the last 7 years in retail, there appeared to be no fire alarm shutdown relay/interface fitted between the supply and the fan coils to isolate in the event of fire????

    This is an old install (both a/c systems and electrical install) so electrically speaking the 16th edition regs etc weren't in place at the time I would imagine, so maybe shutdown relays weren't compulsory then?

    Are fire alarm shutdown relays compulsory now, and in this instance would it need to be retro fitted
    to comply?

    If so under what Regulation??

    Hope business is treating you all kind!!

    All the best.

    J.



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Fire Alarm Shutdown

    My understanding is that recirculating systems does legally not require fire alarm interface.

    Insurance companies might still insist on them...but that's another matter.

  3. #3
    Join Date
    Dec 2006
    Location
    London & Surrounding Counties
    Posts
    122
    Rep Power
    18

    Red face Re: Fire Alarm Shutdown

    Quote Originally Posted by The Viking View Post
    My understanding is that recirculating systems does legally not require fire alarm interface.

    Insurance companies might still insist on them...but that's another matter.
    That's interesting to hear Viking!!

    I'm a CORGI ventillation scheme member, and am looking to contact them first thing, however I'm trying to make a start on the report now, so figured I could get a head start lol.

    Thanks for the quick reply mate!

  4. #4
    Join Date
    Dec 2006
    Location
    London & Surrounding Counties
    Posts
    122
    Rep Power
    18

    Re: Fire Alarm Shutdown

    Can anybody else confirm the above??

  5. #5
    Join Date
    Oct 2007
    Location
    w.mids
    Age
    49
    Posts
    110
    Rep Power
    17

    Re: Fire Alarm Shutdown

    Quote Originally Posted by Daikin=Overated View Post

    This is an old install (both a/c systems and electrical install) so electrically speaking the 16th edition regs etc weren't in place at the time I would imagine, so maybe shutdown relays weren't compulsory then?

    The 16th was out when i was training as an electrician 17 years ago, how old is this install ? Are you actually saying that every cassette installed now has to be linked to the fire alarm? I didn't know that i thought it was for supply and extract although hardly anyone does, i didn't know it was a wiring reg either.
    Put the screwdriver down and step away from the expansion valve !!!! OK Gary i won't touch it unless instructed.

  6. #6
    Join Date
    Dec 2006
    Location
    London & Surrounding Counties
    Posts
    122
    Rep Power
    18

    Re: Fire Alarm Shutdown

    Quote Originally Posted by get the gauges View Post
    The 16th was out when i was training as an electrician 17 years ago, how old is this install ? Are you actually saying that every cassette installed now has to be linked to the fire alarm? I didn't know that i thought it was for supply and extract although hardly anyone does, i didn't know it was a wiring reg either.
    Heya.
    i was just giving an example of a regulation by mentioning the 16th edition. I'm not suggesting that this is essential on each installation neither, it's common place on pretty much every commercial new install i've worked on lately, and so i'm slightly confused myself.

    I think as the viking said it's probably just that some insurers stipulate this and others don't?

    It's not a wiring reg.........I didn't word that particuarly well, it's most probably a ventillation regulation if anything or may even come in under fire alarm regs?
    That's why I mentioned contacting CORGI ventillation this morning to see if they could conclude this.

    Cheers.
    J.

  7. #7
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Fire Alarm Shutdown

    Here's an excerpt from the Building Regs Document B (Fire Safety in non domestic buildings).

    It doesn't mention the requirement for a fire alarm interlock with ventilation or A/C systems.

    I think that most fire alarm interlocks on control panels are written into the spec by the Consultant, but I may be wrong . It is something that we do in our panels as a matter of course but I don't know why
    Attached Files Attached Files

  8. #8
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    543
    Rep Power
    18

    Re: Fire Alarm Shutdown

    it would depend on what solar system planet zorb is located in.

    In the galaxy on the western side of the vast Atlantic way, the solar systems typically require shut down on systems that move 2000 CFM or more of air. Other western solar systems even require shut down if any size system serves an egress corridor.

    Ceiling cassettes are not typically located in corridors, so the jedi law would be shut down those 18 kW or greater capacity which would tend to exceed the humble capacity of the minisplits
    Take the V out of HVAC and you are left with a HAC job

  9. #9
    Join Date
    Dec 2006
    Location
    London & Surrounding Counties
    Posts
    122
    Rep Power
    18

    Talking Re: Fire Alarm Shutdown

    Quote Originally Posted by Abby Normal View Post
    it would depend on what solar system planet zorb is located in.

    In the galaxy on the western side of the vast Atlantic way, the solar systems typically require shut down on systems that move 2000 CFM or more of air. Other western solar systems even require shut down if any size system serves an egress corridor.

    Ceiling cassettes are not typically located in corridors, so the jedi law would be shut down those 18 kW or greater capacity which would tend to exceed the humble capacity of the minisplits
    --------------------------------------------------------------
    Some of what your on please Abby Normal!
    You killed that thread. Niceone.

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Dunham Bush Chiller Alarm
    By Regulator in forum Air Conditioning
    Replies: 11
    Last Post: 08-12-2010, 01:42 AM
  3. fire shutdown
    By mwizard in forum Air Conditioning
    Replies: 5
    Last Post: 20-02-2007, 08:50 PM
  4. Cost effective Freezer/Cooler Fire Detection
    By Marvin in forum New Technologies
    Replies: 6
    Last Post: 14-12-2004, 09:20 PM
  5. Dont call me, call the fire brigade!!!
    By 750 Valve in forum Chit Chat & Service Stories
    Replies: 8
    Last Post: 27-02-2004, 10:34 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •