Hi everybody
I am looking for a Cataloque for Refrigerated air Dryer Donaldson Ultrafilter model SD0375 AP .
Thanks a lot
-
19-02-2008, 02:06 PM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 56
- Posts
- 6,172
- Blog Entries
- 6
- Rep Power
- 35
Re: Cataloque for Refrigerated air Dryer
I am sure that you could find here what you want.
http://tinyurl.com/yqwt3w
-
20-02-2008, 01:39 PM #3
Re: Cataloque for Refrigerated air Dryer
Hi Kaskiris
Do you have a problem with this dryer. If so I would more than happy to help, I work on lots of these things from 30cfm to 1000cfm.
Regards
PP
-
21-02-2008, 11:28 AM #4
Re: Cataloque for Refrigerated air Dryer
Thanks for your reply
The problem with the dyer is freezing and no air pass through the dryer.
-
21-02-2008, 12:39 PM #5
Re: Cataloque for Refrigerated air Dryer
Hi Kaskiris
What refrigerant is the dryer on & what is the suction pressure. some manufacturers use differant methods of keeping the evaporator pressure constant therefore keeping the temp constant.
Has it got a fan hp switch to cut the condenser fan in & out and does it have an hot gas by pass valve, aev or an epr fitted.
Is the refrigerant charge correct.
let me know & I will come back to you.
Regards
PP
-
21-02-2008, 01:57 PM #6
Re: Cataloque for Refrigerated air Dryer
Hi
The type of refrigerant is R134a- 0.95Kg. The fan works normally. Stops and start by high pressure switch ( The dyer has no high presure service valve. The evaporator pressure is kept constant by hot gas by pass valve. I didnt check the refrigerant charge. The low pressure is 2,1 bar.
Please note that the dryer is controlled by electronic microprossesor.
Thanks
-
21-02-2008, 10:21 PM #7
Re: Cataloque for Refrigerated air Dryer
Hi
The dryer should operate 24/7, however does the microprocessor switch the dryer on/off or just indicate temp ( red green & blue indicators ).
the fan appears to function correctly & suction pressure not to far out.
Put the drier on by pass ie no air flow through drier, this how the drier should be set up & adjust suction pressure to 35psi, wind the hot gas valve 1/4 of a turn at a time & wait 5 mins for the pressure to settle if the dryer is set up on load & the air demand drops off the suction pressure will drop causing it to freeze. Also check auto drain is working correctly & not holding water in the line.
Let me know how you get on.
PP
-
04-03-2008, 12:21 PM #8
Re: Cataloque for Refrigerated air Dryer
Dear p p
The microprocessor switch the dryer on/off and also contol the drain valve. I am sure that the proplem is the microprocessor controller.
Thank you for your help.
-
28-04-2008, 04:47 PM #9
Similar Threads
-
Building a Freeze dryer
By kennedyb4 in forum FundamentalsReplies: 15Last Post: 25-07-2009, 06:24 PM -
Removing sweat on Filter Dryer dangers?
By mooka in forum DomesticReplies: 16Last Post: 09-10-2007, 05:09 PM -
Scroll compressor with TXV no Receiver no filter Dryer
By FCS in forum FundamentalsReplies: 7Last Post: 19-06-2007, 10:51 PM -
UltraTroc Air Dryer Failure
By Robearbam in forum Trouble ShootingReplies: 3Last Post: 19-04-2005, 11:50 AM -
oil pressure problems on air dryer
By edge in forum Trouble ShootingReplies: 1Last Post: 16-07-2002, 02:10 PM