    I am working on a small walk in freezer with R404a which has not fitted with sight glass. It was short of gas when I fitted the gauges on. What pressure should the unit be to get it to -20c? And what should be if it is a walk in fridge?
    Thanks.
    Oct 2006
    1,843
    Re: walk in freezer
    Quote Originally Posted by ail View Post
    Hi there
    Thanks.
    You will need to find out where the old refrigerant has gone first. Pull all the refrigerant out and then repair leak. On the thing somwhere will be a lable telling you how much refrigerant to weigh into it to correctly charge the system.
    You should never just add gas, but you knew that did'nt you?
    As for pressures just get your compariter out and see what the saturation pressure of r404a is at about -30degC.
    You will not be able to tell how much refrigerant there is in a system by pressures alone.
    Cheers taz.
    Feb 2008
    Las Vegas, NV
    67
    330
    Re: walk in freezer
    Hi there
    Thanks.
    What taz24 said plus, if its your plan, its not wise to just turn the temperature up and run as a cooler.
    There are other things to consider. The most important being, will the compressor handle the higher SP. Two other items that come to mind are the controls and the TD across the evap.
    Many LT404A units will also pump R134a for MH temps, but this would be a permanent change if you decided to run as a cooler.
    Feb 2008
    Las Vegas, NV
    67
    330
    Re: walk in freezer
    Quote Originally Posted by taz24 View Post
    Cheers taz.
    taz24,
    Help out this ole Southern guy across the pond. I assume a "compariter" is a P/T chart? I did fiqure out what a "phile" is.
    Aug 2005
    4
    Re: walk in freezer
    404a evap @ -6 for a coldroom temp of 1*C = 56psig
    for a freezer room @ -28*C Evap = 17psig
    38
    Re: walk in freezer
    Possibly on a capilary tube expansion, so no sight glass and hopefully no receiver. System charge on name plate.
    First, find the leak if you are sure it is short of gas, if capillary it will run lower suction pressure.
    More system info required.
    Saui Arabia
    12
    Re: walk in freezer
    if the room temp. is -20 oC, then the SST saturated suction temperature have to be -26 or -27 oC, temp difference for practical and ecnomical use is 6 to 7, so see pressure @ SST
    Re: walk in freezer
    Check out the OP date guys, and he hasn't come back either.
    38
    Re: walk in freezer
    OK Brian_UK
    thanks and bugger
  1. walk in freezer
    By tonto33 in forum Commercial
    Last Post: 05-10-2009, 09:12 PM
  2. Trolley freezer & blast freezer
    By smpsmp45 in forum NH3
    Last Post: 25-08-2007, 07:29 AM
  3. walk in freezer refrigeration sizing?
    By trammd in forum Technical Discussions
    Last Post: 02-11-2006, 11:56 AM
  4. It's snowing in my walk in freezer!
    By Matt in forum Commercial
    Last Post: 14-10-2006, 07:07 AM
  5. Walk in freezer with no LLS
    By eskimo joe in forum Fundamentals
    Last Post: 07-05-2002, 06:35 PM