    Tk Sr2 Code 26



    hey all

    i went to a tk toptech class a while ago and did not get this question answered you guys seem to be pretty smart


    sr2 at a 50 degree box will code 26 after 15 minutes if td drops below 5.0

    at a 10 box the td is even less before codes 26

    i have downloads of units with a 8.0 td at 70 box
    that code 26

    im told that the td is now variable for different box temps

    does anyone no the formula tk uses on the sr2

    i got that info from service eng.

    thanks tkjimmy



  2. #2
    Join Date
    Dec 2007
    Location
    Tampa, Florida U.S.A
    Age
    51
    Posts
    590
    Rep Power
    17

    Re: Tk Sr2 Code 26

    Quote Originally Posted by tkjimmy View Post
    hey all

    i went to a tk toptech class a while ago and did not get this question answered you guys seem to be pretty smart


    sr2 at a 50 degree box will code 26 after 15 minutes if td drops below 5.0

    at a 10 box the td is even less before codes 26

    i have downloads of units with a 8.0 td at 70 box
    that code 26

    im told that the td is now variable for different box temps

    does anyone no the formula tk uses on the sr2

    i got that info from service eng.

    thanks tkjimmy
    Good question,

    When the unit is in engineering labs being tested TDs are being calculated along with unit performance.

    There are many factors when considering what a normal td is, such as:

    Model of unit.
    Optional etv.
    Modulation.
    Air chute
    Optiset modulation temp bands, based off floor limit.
    Cargo not loaded correctly causing short cycle.

    If you are getting a code 26 which is low capacity, is it doing it in heat mode or cool mode?

    There is no simple algorythim to figure out what your asking.

    You need to send me that down load, so i can see what the S/W revision and compare all the TD data against the additional data offered in technican mode.

  3. #3
    Join Date
    Feb 2008
    Location
    delaware
    Age
    58
    Posts
    11
    Rep Power
    0

    Re: Tk Sr2 Code 26

    not sure how to send other than email

  4. #4
    Join Date
    Dec 2007
    Location
    Tampa, Florida U.S.A
    Age
    51
    Posts
    590
    Rep Power
    17

    Re: Tk Sr2 Code 26

    Quote Originally Posted by tkjimmy View Post
    not sure how to send other than email
    Check your email... and reply with download attachment.

    A-Z

  5. #5
    Join Date
    Dec 2007
    Location
    Tampa, Florida U.S.A
    Age
    51
    Posts
    590
    Rep Power
    17

    Re: Tk Sr2 Code 26

    From the download I am seeing quick temp pull downs, from 80 degrees f to Zero degrees quickly, This would indicate a couple things, loading while unit running at well sealed frozen dock, or short cycling, from bulk head or product improperly loaded.

    I am ruling out compressor capacity and or other refrigeration related components based on the unit quick temperature pulldown. with ambient temps exceeding 80 degrees F.

    Here are some items you should look at or possibly be concerned with as well make the customer aware of.

    • What is the trailer dimensions?
    • Do they use divider bulkheads? If so where is it set In reference to length of trailer.
    • Do these units have return air bulk heads?
    • What is the product they load?
    • Do they load product off the floor?
    • Do they load product too high?
    Those are all the listed items that can cause the codes your seeing, based off the download you gave me.

    A-Z

  6. #6
    Join Date
    Jan 2008
    Location
    melbourne
    Age
    49
    Posts
    11
    Rep Power
    0

    Re: Tk Sr2 Code 26

    tkjimmy,i would be thinking it has to be in your optiset programiing, i take it your talking in F not C so id expect a much greater td at those box temps, or your etv is not opening fully?? do you know the software revisions and what units are you having the dramas with?? SB or SL This all comes into it, let us know ok
    Quote Originally Posted by tkjimmy View Post
    hey all

    i went to a tk toptech class a while ago and did not get this question answered you guys seem to be pretty smart


    sr2 at a 50 degree box will code 26 after 15 minutes if td drops below 5.0

    at a 10 box the td is even less before codes 26

    i have downloads of units with a 8.0 td at 70 box
    that code 26

    im told that the td is now variable for different box temps

    does anyone no the formula tk uses on the sr2

    i got that info from service eng.

    thanks tkjimmy

  7. #7
    Join Date
    Dec 2007
    Location
    Tampa, Florida U.S.A
    Age
    51
    Posts
    590
    Rep Power
    17

    Re: Tk Sr2 Code 26

    Quote Originally Posted by daniel ox View Post
    tkjimmy,i would be thinking it has to be in your optiset programiing, i take it your talking in F not C so id expect a much greater td at those box temps, or your etv is not opening fully?? do you know the software revisions and what units are you having the dramas with?? SB or SL This all comes into it, let us know ok

    Daniel, I agree that optiset and ETV has an influence on TDs, but not in this case.

    If it were an optiset controlled TD, it would not produce an alarm code for capacity as this is the way the unit is expected to run.

    Based on the download I saw, I dont believe he has any capacity issues.. also unit its not equipped with optional ETV, so Fresh Set and etv problem are eliminated.

    The download clearly shows from the time the unit is started at 80 degrees f till it reaches -5 degrees f is around 30 minutes.

    Regards A-Z

Similar Threads

  1. lennox fault code
    By richelli in forum Trouble Shooting
    Replies: 0
    Last Post: 01-02-2008, 09:13 PM
  2. mitsubishi city multi fault code
    By robin r33 gtr in forum Air Conditioning
    Replies: 5
    Last Post: 05-11-2007, 10:23 PM
  3. HTML code fragment
    By Abe in forum Computers & the Internet
    Replies: 5
    Last Post: 22-03-2007, 05:07 PM
  4. Diplomat 6528 Fault Code
    By Targus in forum Domestic
    Replies: 3
    Last Post: 31-10-2006, 07:43 PM
  5. Fault Code Sheets...?
    By C_Henderson in forum Air Conditioning
    Replies: 2
    Last Post: 01-08-2006, 05:19 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •