Thread: Fault codes
08-02-2008, 09:32 PM #1
Fault codes
Can anyone supply a list of fault codes that includes P5 & P6 on Hitachi Air Con units.
Many thanks Nigel
08-02-2008, 09:48 PM #2
Re: Fault codes
Nigel,
If you send me a pm with a fax number i can fax you a list but i have never seen p5 or p6 on hitachi
code 05 is normally a transmission fault with a problem with the power poss incorrect phase problems
code 06 is a voltage problem on the outdoor unit
Hitachi Technical is on 01628 585393
Fatboy
10-02-2008, 11:08 PM #3
Re: Fault codes
Nigel, I suspect your unit is a RAS- HVRNE or HRNE.
P6 is a protection code (frost protection),suggesting shortage of refrigerant, blockage etc.
P5 is also a protection code (high discharge temperature) which also suggests shortage of refrigerant or a blockage etc.
Is there a similar adjacent unit? possibly crossed comms cable.
Also if there are adjacent systems and a common H-Link comms is used then the blue dip switches on the relevent I/U O/Us need to be set the same (this is the cycle address or system address).
Good luck
11-02-2008, 01:02 AM #4
Re: Fault codes
Is this what your after:
hitatci%20Alarm%20code[1].pdf
11-02-2008, 03:16 AM #5
Re: Fault codes
carrier fault codes
By richelli in forum Trouble ShootingReplies: 5Last Post: 18-06-2010, 07:35 AM -
carrier chiller fault codes
By al in forum Air ConditioningReplies: 7Last Post: 20-07-2009, 10:10 PM -
Daikin fault codes
By Markie in forum Air ConditioningReplies: 16Last Post: 13-01-2009, 01:58 AM -
standardisation of fault codes?
By kelvin kline in forum Air ConditioningReplies: 1Last Post: 10-10-2007, 12:30 AM -
MHI, Sanyo & Fuijitsu Complete Fault Codes
By aeb200 in forum Air ConditioningReplies: 1Last Post: 16-11-2005, 01:11 PM