    Arrow CTC high discharge



    I have seen Carrier Ultras with high pressure fault many times through the years, and the cause is low ***** level. Never really understood why the processor sets this fault. Anyone care to explain?



  2. #2
    Join Date
    Dec 2007
    Location
    Tampa, Florida U.S.A
    Age
    51
    Posts
    590
    Rep Power
    17

    Re: CTC high discharge

    Quote Originally Posted by DaButcher View Post
    I have seen Carrier Ultras with high pressure fault many times through the years, and the cause is low ***** level. Never really understood why the processor sets this fault. Anyone care to explain?
    Sorry cant help myself, but i know the answer to this as well.

    The suction pressure transducer on the suction line reads the suction pressure, soon as the summit controller sees a, vacuum HG pressure reading for more than 30 seconds, it will energize the rear compressor unloader in efforts to see suction pressure come up, then it will enrgize the front, if still remains in vacuum, the the unit will display high pressure and turn into a shutdown conditon.

    TK has a couple units that do a similiar same thing that confuses most, for an example the code 109 in multi-temp SR units states high head pressure, from the transducer, if you ever noticed when a system is out of refrigerant or near out of refrigerant this code will generate. but the description of the code confuses most.

    Code 89 ETV electronic throttle valve problem similiar thing, techs auto matically go to the ETV expecting to find a problem, only to find the micro never saw a reaction to suction pressure changes when testing the ETV, mostly because the unit was low or out of refrigerant.

    Code 10 on SR truck units with open drive scrolls same thing, the high pressure cutout, low pressure cut out and higfh compressor tem cut out are all wired in series, and feeds signal to the coil side of the run relay. If any one of those switches opens it throws code 10, and if cleared by driver and the switch remains open, the remainder code will be 35.

    This one stumped me for about an hour one day before i wisened up and lookedt a schematic.

    Regards A-Z

  3. #3
    Join Date
    Feb 2005
    Location
    Hong Kong
    Posts
    190
    Rep Power
    20

    Re: CTC high discharge

    Great stuff a-z, keep this up and you will make " moderator' grade yet or better still, Webram may offer you a partnership ? co-directorship ?etc YUK YUK

    best regards
    T-P
    Remember what Augustus once said:
    "festina lente" - make haste, slowly!

  4. #4
    Join Date
    Dec 2007
    Location
    Tampa, Florida U.S.A
    Age
    51
    Posts
    590
    Rep Power
    17

    Re: CTC high discharge

    Quote Originally Posted by thermo prince View Post
    Great stuff a-z, keep this up and you will make " moderator' grade yet or better still, Webram may offer you a partnership ? co-directorship ?etc YUK YUK

    best regards
    T-P
    T-P

    "Thanks buddy" Glad to help whenever I can.

    I dont think they will be considering making me modertor or co-partener considering my "tedious" track record,,, anytime soon. YUK YUK.

    If the offer does ever come across, I think I may require RE moderator training before I could consider it.


    Regards A-Z

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: CTC high discharge

    Quote Originally Posted by absolute-zero View Post
    I dont think they will be considering making me modertor or co-partener considering my "tedious" track record,,, anytime soon. YUK YUK.

    Regards A-Z
    Still at it then
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Dec 2007
    Location
    Tampa, Florida U.S.A
    Age
    51
    Posts
    590
    Rep Power
    17

    Re: CTC high discharge

    Quote Originally Posted by Brian_UK View Post
    Still at it then
    Nah I dont sweat the small stuff.

    Regards A-Z

  7. #7
    Join Date
    Jan 2008
    Location
    Texas
    Age
    65
    Posts
    132
    Rep Power
    17

    Re: CTC high discharge

    Quote Originally Posted by absolute-zero View Post
    Code 89 ETV electronic throttle valve problem similiar thing, techs auto matically go to the ETV expecting to find a problem, only to find the micro never saw a reaction to suction pressure changes when testing the ETV, mostly because the unit was low or out of refrigerant.

    Code 10 on SR truck units with open drive scrolls same thing, the high pressure cutout, low pressure cut out and higfh compressor tem cut out are all wired in series, and feeds signal to the coil side of the run relay. If any one of those switches opens it throws code 10, and if cleared by driver and the switch remains open, the remainder code will be 35.
    Regards A-Z
    Ya, after the first experience with code 89, I assume it is low ***** level.

    I don't service many truck units, code 10 on SB units is low battery volts sometimes.

  8. #8
    Join Date
    Dec 2007
    Location
    Tampa, Florida U.S.A
    Age
    51
    Posts
    590
    Rep Power
    17

    Re: CTC high discharge

    Quote Originally Posted by DaButcher View Post
    Ya, after the first experience with code 89, I assume it is low ***** level.

    I don't service many truck units, code 10 on SB units is low battery volts sometimes.
    I have not found that to be common here, but in those rare occasions the code 10 was accompanied by a alrm code 61 or 35.

    regards a-z

  9. #9
    Join Date
    Jan 2008
    Location
    Canada
    Posts
    579
    Rep Power
    17

    Re: CTC high discharge

    Another one that often catches rookies on the CTC's is the oil pressure alarm that is generated by a faulty alternator. If this alarm shows on start up, check for power on the D pos. or "orange wire" before the unit starts.
    By the way, Absolute zero I am glad to meet you! Everyone should check out your site. Are you an outcast too?

  10. #10
    Join Date
    Dec 2007
    Location
    Tampa, Florida U.S.A
    Age
    51
    Posts
    590
    Rep Power
    17

    Re: CTC high discharge

    Quote Originally Posted by abbsnowman View Post
    Another one that often catches rookies on the CTC's is the oil pressure alarm that is generated by a faulty alternator. If this alarm shows on start up, check for power on the D pos. or "orange wire" before the unit starts.
    By the way, Absolute zero I am glad to meet you! Everyone should check out your site. Are you an outcast too?
    Greetings abbsnowman,
    Good to meet you too. I have several post and threads here on that tech-tip you posted. Its a good one, and does catch lots of techs by the short hairs.

    Site????What Site????? Outcast??? I dont know what your talking about.

    But seriously I do like to hang out here so please dont spam or make any mention of advertising of the sort.



    Best Regards A-Z

  11. #11
    Join Date
    Feb 2008
    Location
    Norway
    Age
    57
    Posts
    446
    Rep Power
    17

    Re: CTC high discharge

    Quote Originally Posted by DaButcher View Post
    I have seen Carrier Ultras with high pressure fault many times through the years, and the cause is low ***** level. Never really understood why the processor sets this fault. Anyone care to explain?
    I have no experience with Ultras, but on Maximas is the HP and LP switch conected in series. It gives an HP alarm whenever one of them tripps.

  12. #12
    Join Date
    Dec 2007
    Location
    Tampa, Florida U.S.A
    Age
    51
    Posts
    590
    Rep Power
    17

    Re: CTC high discharge

    Quote Originally Posted by SteinarN View Post
    I have no experience with Ultras, but on Maximas is the HP and LP switch conected in series. It gives an HP alarm whenever one of them tripps.
    I have not had the pleasures of ever seeing or servicing a maxima,,,, Am i missing much??????

    A-Z

  13. #13
    Join Date
    Feb 2008
    Location
    switzerland
    Posts
    10
    Rep Power
    0

    Re: CTC high discharge

    SteinarN is absolute right.
    maxlp.JPG

  14. #14
    Join Date
    Dec 2007
    Location
    Tampa, Florida U.S.A
    Age
    51
    Posts
    590
    Rep Power
    17

    Re: CTC high discharge

    Quote Originally Posted by swissreefer View Post
    SteinarN is absolute right.
    maxlp.JPG
    Not debating if wrong or right, just curiouse of the other differnces in service relation, between maxima and Ultra models..

    A-Z

  15. #15
    Join Date
    Feb 2008
    Location
    Norway
    Age
    57
    Posts
    446
    Rep Power
    17

    Re: CTC high discharge

    Quote Originally Posted by absolute-zero View Post
    I have not had the pleasures of ever seeing or servicing a maxima,,,, Am i missing much??????

    A-Z
    Nope.

    Well, its an ok unit, at least the monotemp version. The multitemp version has more flaws and an unbelievable unreliable 1 phase 230V generator. The zone 2 and 3 has only electric heating. Its ok for defrost, but here in cold Norway its inadequate to heating in cold ambient. Especially when you consider that the unit must be running in high speed to generate voltage by the electic motor (which acts as an asyncroneous generator in high speed to supply voltage to the heating elements in zone 2 and 3) and the heat lockout function at zone 1 at termostat setting below -12 degres C. When the driver has frozen goods in zone one and fresh in lets say zone 2, then the unit go crazy in high speed trying to heat zone 2 while at same time high speed cool only at zone 1! Before you know it it's -35 degres C in zone 1. Easy to maintain +8 in zone 2 then. Espesially when its -20 degres C outside!

    However they realized the idiotic function of heat lockout and came up with a new software which was configurable to disable that function 2 years ago.


    And it's intendend to trailers, not semis.
    Last edited by SteinarN; 21-02-2008 at 10:56 PM. Reason: minor typo

  16. #16
    Join Date
    Dec 2007
    Location
    Tampa, Florida U.S.A
    Age
    51
    Posts
    590
    Rep Power
    17

    Re: CTC high discharge

    Quote Originally Posted by SteinarN View Post
    Nope.

    Well, its an ok unit, at least the monotemp version. The multitemp version has more flaws and an unbelievable unreliable 1 phase 230V generator. The zone 2 and 3 has only electric heating. Its ok for defrost, but here in cold Norway its inadequate to heating in cold ambient. Especially when you consider that the unit must be running in high speed to generate voltage by the electic motor (which acts as an asyncroneous generator in high speed to supply voltage to the heating elements in zone 2 and 3) and the heat lockout function at zone 1 at termostat setting below -12 degres C. When the driver has frozen goods in zone one and fresh in lets say zone 2, then the unit go crazy in high speed trying to heat zone 2 while at same time high speed cool only at zone 1! Before you know it it's -35 degres C in zone 1. Easy to maintain +8 in zone 2 then. Espesially when its -20 degres C outside!

    However they realized the idiotic function of heat lockout and came up with a new software which was configurable to disable that function 2 years ago.


    And it's intendend to trailers, not semis.
    It sounds allot like the CTC genesis TM 900-TM1000 in comparison

    Thanks A-Z

  17. #17
    Join Date
    Feb 2008
    Location
    Norway
    Age
    57
    Posts
    446
    Rep Power
    17

    Re: CTC high discharge

    Quote Originally Posted by absolute-zero View Post
    It sounds allot like the CTC genesis TM 900-TM1000 in comparison

    Thanks A-Z
    Probably the same unit then. An older version of Maxima multitemp was named TM 800 i think.

Similar Threads

  1. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  2. High discharge temperature
    By raviperumal in forum Trouble Shooting
    Replies: 14
    Last Post: 10-02-2008, 08:41 AM
  3. TK basic micro-p features and functions
    By REEFER-TEK in forum Transport
    Replies: 0
    Last Post: 05-12-2007, 06:25 PM
  4. cooling &freezing comp.
    By afeef in forum Industrial Compressors
    Replies: 25
    Last Post: 15-12-2006, 09:29 PM
  5. GSHP discharge temp high
    By Lc_shi in forum Trouble Shooting
    Replies: 6
    Last Post: 20-01-2005, 08:37 AM