    Thumbs up Now What Pressure do I test to?



    For those of us that have to stop and think "now what was the formula" occasionally, refer to the data below!
    Grizzly
    Last edited by Grizzly; 25-04-2008 at 01:44 PM.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Now What Pressure do I test to?

    Good one, thanks for the reminder.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Now What Pressure do I test to?

    Quote Originally Posted by Grizzly View Post
    For those of us that have to stop and think "now what was the formula" occasionally, refer to the data below!
    Grizzly

    Hello Grizzly.
    I think that document is out of date now.
    It was the old British standard 4434 which has now been superseded by EN378. We now test to standing pressure @ 55degc X 1.3 for strength and X1.1 for leak testing.

    Cheers taz.

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Thumbs up Re: Now What Pressure do I test to?

    Good info, no matter of standards!
    Thanks Grizly and Taz!

  5. #5
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Thumbs up Re: Now What Pressure do I test to?

    Quote Originally Posted by taz24 View Post
    Hello Grizzly.
    I think that document is out of date now.
    It was the old British standard 4434 which has now been superseded by EN378. We now test to standing pressure @ 55degc X 1.3 for strength and X1.1 for leak testing.

    Cheers taz.
    Taz
    Can you give us a bit more info. what is an EN (EUROPEAN SOMETHING?) and does it supersead
    A BS. Standard?
    Cheers Grizzly

  6. #6
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Now What Pressure do I test to?

    Quote Originally Posted by Grizzly View Post
    Taz
    Can you give us a bit more info. what is an EN (EUROPEAN SOMETHING?) and does it supersead
    A BS. Standard?
    Cheers Grizzly

    Hello Grizzly the document you have is good the main difference I can see is were it states Max working pressure. that is now designated by the pressure of the refrigerant at 55degc.

    BS EN 378-2:2000 referers to

    Refrigerating systems, Refrigeration, Refrigerators, Heat pumps, Heat transfer, Safety, Environmental engineering, Operating conditions, Maintenance, Repair, Recycling, Health and safety requirements, Hazards.

    It replaces
    BS 4434:1995

    Cheers taz,
    Last edited by taz24; 21-01-2008 at 01:17 AM.

  7. #7
    Join Date
    Nov 2006
    Location
    UK
    Age
    63
    Posts
    392
    Rep Power
    18

    Re: Now What Pressure do I test to?

    However if the equipment manufacturer specifies a different pressure you should always test to that and in the eyes of the law you should be OK if you have followed their instructions, but if you exceed their instructions then you are liable even thou they do not meet EN378 standards.

    En378 is not a law just a standard so you do not have to comply with it but if you do not you may be in the C__P big time.

    Ian

  8. #8
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,261
    Rep Power
    31

    Re: Now What Pressure do I test to?

    Hi, all

    to find a leak we can see something here:

    http://www.acrib.org.uk/MPLUGB71936

    and here, but on different way....

    http://www.ior.org.uk/ior_/images/pd...%20testing.pdf

    ....but very little when to make hydraulic and when pneumatic pressure test...

    http://www.jlab.org/ehs/manual/EHSbook-389.html

    with weird explanation when pneumatic test is permitted...

    and F-gas regulation update is here:

    http://www.acrib.org.uk/web_images/d...%20LEAFLET.pdf


    Best regards, Josip
    Last edited by Josip; 21-01-2008 at 01:23 AM. Reason: add link

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  9. #9
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Now What Pressure do I test to?

    Quote Originally Posted by Josip View Post
    Hi, all

    to find a leak we can see something here:

    http://www.ior.org.uk/ior_/images/pd...%20testing.pdf

    Best regards, Josip
    This is very informative .
    A good document thanks ..


    taz.

  10. #10
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Now What Pressure do I test to?

    Quote Originally Posted by Pooh View Post
    En378 is not a law just a standard so you do not have to comply with it but if you do not you may be in the C__P big time.

    Ian
    NE 842/2006 is a law I think and there are also a description how to test.
    It may be perhaps not a law but if you have a case which end in court, then a judge will follow the law or standards.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  11. #11
    Join Date
    Nov 2006
    Location
    UK
    Age
    63
    Posts
    392
    Rep Power
    18

    Re: Now What Pressure do I test to?

    Peter
    that is what I meant, you can ignore the standards but at your own risk.

    Ian

  12. #12
    Join Date
    Feb 2001
    Location
    Doncaster, England
    Posts
    199
    Rep Power
    25

    Re: Now What Pressure do I test to?

    Hi Taz,

    We now test to standing pressure @ 55degc X 1.3 for strength and X1.1 for leak testing.
    If you read BS EN 378 the reference to 1.1 ps is the setting for the pressure relief device.

    Leak testing is carried out to less than or equal to 1ps (AP)
    Tony

  13. #13
    Join Date
    Aug 2006
    Location
    England
    Posts
    50
    Rep Power
    18

    Re: Now What Pressure do I test to?

    EN = European Norm
    EN:378 is a standard which lays down minimum requirements for refrigeration & air conditioning systems.
    You should distinguish which is the high side & low side of the system then which refrigerant is to be used. Determin the pressure of that refrigerant at 32C for the low side, 43C for the high side of a water cooled system & 55C for an air cooled system. Then multiply by 1.3 for the strength test, 1.1 for the leak test & 0.9 for the setting of the HP switch. Use OFN to perform the tests. Any PRV's must of course be removed during these tests, then refitted before pulling a vacuum of 200 microns (about .25 torr).
    Be careful on a heat pump as there is little to the low side. Be very careful as the pressure can be as high as 43 Bar for the high side on a system using R410a.
    figures quoted apply to latitudes for the UK

  14. #14
    Join Date
    Feb 2001
    Location
    Doncaster, England
    Posts
    199
    Rep Power
    25

    Question Re: Now What Pressure do I test to?

    Hi Pendlesteve,

    where do you get 1.1 times for leak test. BS EN 378 clearly states < or = 1 times?
    Tony

  15. #15
    Join Date
    Jan 2008
    Location
    Norfolk - England
    Posts
    95
    Rep Power
    17

    Re: Now What Pressure do I test to?

    Good Evening Gentlemen,

    A very good civalized debate indeed, very interesting comments.

    Your thoughts would be welcome on the following points.

    1. How do you 'get round' the issue of pressure testing components within a system which have a lower MWP, i.e evaporators etc. Typically a Searle cooler for instance has a MWP of 21 Bar. How do you pressure test the sytem in entirity should you operate on R404A? Do you disconnect the cooler? This then defeats the objective?

    2. Would somebody explain what the system MWP is? Does this relate to 55deg condensing? The H.P setpoint? or the PRV setting.

    Thanking in anticipation.

    Maybe this is considered differnet in other countries.

    Billy Ray (new to posting)

  16. #16
    Join Date
    Feb 2001
    Location
    Doncaster, England
    Posts
    199
    Rep Power
    25

    Re: Now What Pressure do I test to?

    Hi,

    1. How do you 'get round' the issue of pressure testing components within a system which have a lower MWP, i.e evaporators etc. Typically a Searle cooler for instance has a MWP of 21 Bar. How do you pressure test the sytem in entirity should you operate on R404A? Do you disconnect the cooler? This then defeats the objective?
    You work out the AP for the LP side (in UK) using 32°C saturation pressure for the refrigerant in the system then you work out the AP for the HP side (in UK) using 43°C saturation pressure for the refrigerant in the system the if it is a water cooled or evaporative condenser or 55°C if it is an air cooled condenser.

    So these are your pressures for leak testing if you can test LP and HP separately.

    For the strength test you use 1 to 1.3 times AP, but you would not exceed manufacturers test pressures.
    Tony

  17. #17
    Join Date
    Jan 2008
    Location
    Norfolk - England
    Posts
    95
    Rep Power
    17

    Re: Now What Pressure do I test to?

    Thanks Tony,

    thats understood pressure testing each 1/2 of the system.

    i assume from your reply that disconnecting the low side from the high side & pressure testing each section suffices to EN378.

    After you reconnect, will a pressure test of the whole system suffice at the lower pressure?

    Can you advise on the termniology of 'system MWP'

    or is this a mesconception?

    Billy Ray

  18. #18
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Thumbs up Re: Now What Pressure do I test to?

    Thanks guys.
    Lots of useful info and I am glad to see that all you trainers are not yet to busy to find time to advise. I suspect that you guys will be very busy once things are firmed up come summer!
    Those interested might like to comment on my post in the thread " Safety Valve Inspection and Replacement" It's all in a similar vein.
    Grizzly

  19. #19
    Join Date
    Feb 2001
    Location
    Doncaster, England
    Posts
    199
    Rep Power
    25

    Re: Now What Pressure do I test to?

    The MWP (system maximum working pressure) refered to as the AP (allowable pressure) will be set by the manufacturer normally.

    However if it is not, BS EN 378 allows you to work out the minimum AP by using 55C or 43C for HP and 32C for LP.

    When pressure testing, if it is possible to test LP and HP separately by closing off valves - if you cannot separate LP from HP, you are allowed to test the whole system at 32C. This would be for small systems.

    But of course for heat pump systems, you would have to test the whole system at 55C.
    Tony

  20. #20
    Join Date
    Jan 2008
    Location
    Norfolk - England
    Posts
    95
    Rep Power
    17

    Re: Now What Pressure do I test to?

    Thanks Tony, that helps.

    Another question if i may (as you seem to be 'the man' to answer).

    Consider a 10 H.P semi-hermetic condensing unit connected to a DX coil.

    This is not a single manufacturers piece of kit, more however a selection of components 'put together by a contractor.

    Therfore each component has differnet MWP's.


    Would therefore the correct terminology for 'system MWP' be either _

    1. PRV set point.

    2. H.P switch set point.

    Billy Ray

  21. #21
    Join Date
    Feb 2001
    Location
    Doncaster, England
    Posts
    199
    Rep Power
    25

    Re: Now What Pressure do I test to?

    Billy Ray,

    the system MWP would be the manufacturer's MWP of the weakest component in the system.

    BS EN 378 sets the PRV set point at 1.1 x that components MWP.

    Set the HP switch to cut out at 0.9 x MWP of weakest component on HP side of system.
    Tony

  22. #22
    Join Date
    Jan 2008
    Location
    Norfolk - England
    Posts
    95
    Rep Power
    17

    Re: Now What Pressure do I test to?

    Tony,

    Thankyou, understood.

    Billy Ray

Similar Threads

  1. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  2. fun quiz
    By Brian23 in forum New to RE
    Replies: 6
    Last Post: 02-10-2007, 10:18 PM
  3. Using Argon to pressure test?
    By mooka in forum Air Conditioning
    Replies: 6
    Last Post: 02-08-2007, 11:12 PM
  4. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38