Thread: Daikin container software.
18-01-2008, 03:24 AM #1
One of the features in the Daikin software is the "current operating data" screen. Thought you guys might enjoy.
This is 'real time' info and you must be plugged into the unit via laptop RS232 port. (using the same download cable as TK, Carrier and Starcool.)
Full cool.
Full heat.
Defrost.
SET
S.P.............Temp Set Point
Hum SET......Humidity Set Point
SENSORS
SS.............Supply Air Sensor
RS.............Return Air Sensor
DCHS.........Compressor Discharge Sensor
EIS............Evap Inlet Pipe Sensor
EOS...........Evap Outlet pipe Sensor
SGS...........Suction Gas Sensor
AMBS.........Ambient Air Sensor
HPT...........High Pressure Transducer
LPT............Low pressure Transducer
PT..............Potential Transformer (input voltage)
CT1............Current Transformer 1
CT2............Current Transformer 2
DSS............Data Recorder Supply Air Sensor
DRS............Data Recorder Return Air Sensor
USDA1.........Cargo Sensor 1
USDA2.........Cargo Sensor 2
USDA3.........Cargo Sensor 3
CTS............Cargo Temp Sensor
HuM............Humidity Sensor
OUTPUTS
Ry1..............(unused)
Ry2 RSV........Reheat Solenoid Valve
Ry3 BSV........Bypass Solenoid valve
Ry4 DSV........Defrost Solenoid valve
Ry5 HSV........Hot Gas Solenoid valve
Ry6 ISV.........Injection Solenoid valve
Ry7 LSV.........Liquid Solenoid valve
Ry8 ESV.........Economizer Solenoid valve
Ry9 RM COMP..Notaclue
Ry10 RM DEF...Notaclue
Ry11 RM IR.....Notaclue
Ry12.............(unused)
Ry13 COMP....Compressor Motor
Ry14 EFH.......Evap Fan High
Ry15 EFL.......Evap Fan Low
Ry16 CF........Condensor Fan
Ry17............(unused)
Ry18 PCC1.....Phase Correction Contactor
Ry19 PCC2.....Phase Correction Contactor
SMV.............Suction Modulation Valve
EV...............Electronic Expansion ValveLast edited by Will; 19-01-2008 at 07:57 AM.
18-01-2008, 05:53 AM #2
Re: Daikin container software.
Nice Post Will,
I have that program and have used it when i was servicing containers a few years ago.
Dude I miss working on containers.
A-Z
19-01-2008, 07:53 AM #3
Added abbreviation nomenclature to bottom of first post.
19-01-2008, 10:10 AM #4
I am looking handbook for design of HVAC for clean room
19-01-2008, 07:47 PM #5
Greetings Alfredo,
Did you try looking here? http://www.refrigeration-engineer.co...splay.php?f=24
If you cant find post a new thread labeled what you are looking for.
Regards A-Z
19-01-2008, 10:51 PM #6
Service checker Daikin
By Cool100 in forum Air ConditioningReplies: 26Last Post: 22-03-2011, 12:53 PM -
Daikin not working... many problems
By stankovicv in forum Air ConditioningReplies: 26Last Post: 11-12-2010, 09:01 AM -
Daikin, Why do we bother?
By gwilliamson in forum Air ConditioningReplies: 21Last Post: 02-02-2010, 09:38 AM -
Daikin Service CHecker Type III
By Ben-Hur-Cool in forum Air ConditioningReplies: 27Last Post: 15-01-2010, 02:53 PM -
Daikin Comp and inverter
By WCC73 in forum Air ConditioningReplies: 5Last Post: 08-11-2008, 08:44 PM