    CIAT Water chiller



    came across an odd one last week with a 200kw chiller that had been faulting with ice build up on the shell and tube evaporator.

    The unit had a sol valve prior to the tev but the LP switch was wired through a timer (solid state).

    If the system went into low pressure then the LP switch energised a timer which eventually energised a fault contactor to stop the machine. has any one come across this?

    As the comp continued to run in low pressure it pulled a vacuum before the contactor made and stopped the machine With a high vacuum on one side of the sol valve and high liquid pressure on the other the electro coil was not able to energise the sol valve and the machine just ran in a vacuum after it was called.

    to solve the problem I had to fit a new Ranco LP, scrap the timer and do a few other mods.

    Why fit a timer in the LP?



  2. #2
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24
    Hi Frank,
    the only time I ever seen that was on scroll compressors on AHU type a/c the idea being that the suction dropped until the head was built up on cold days, and the expansion valves started working.
    Regards, Andy

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51
    Hi Andy

    This thing has an 8 cylinder Copeland semi - nice piece of kit - and the condenser has a damper actuator (which is worked off the liquid line) just prior to the fan inlet so head presure is taken care of.

    I had to replace the water flow switch which was siezed and causing all the problems but when testing all the safety's this LP really amazed me.

    When I left the "modified" machine it was working OK

    Frank
    Last edited by frank; 18-04-2003 at 08:34 AM.

  4. #4
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24
    Hi Frank,
    I am inclined to beleive the L.P short out timer was a quick fix for something that happened in the past. The L.P cutout is a essential safety for a chiller, if the flow fail sticks in flow condition, this is what will save your chiller from freezing.
    I would have done exactly what you did.
    Kind Regards. Andy

  5. #5
    Join Date
    Dec 2001
    Location
    Cleveland
    Posts
    41
    Rep Power
    0
    Alright Frank
    what I have seen which is stranger is a oil failure switch used for low pressure safety control on chillers to prevent freeze up where the heater element in the oil failure switch cuts out the chiller if the lp pressure dips for too long strange but does work [cheap solution] one mark might have thought up eh!!! LOL.
    Regards Dave Goodings

  6. #6
    Join Date
    Aug 2005
    Location
    USA
    Age
    59
    Posts
    25
    Rep Power
    0

    Re: CIAT Water chiller

    Hello Frank,

    This is pretty common to have a timer on the LP switch for winter starting. However it should only be able to energise on start up only after that the timer should be out of circuit until the next start up.

  7. #7
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: CIAT Water chiller

    Nice website Cuge you have
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  8. #8
    Join Date
    Mar 2005
    Location
    u.a.e
    Age
    68
    Posts
    169
    Rep Power
    20

    Re: CIAT Water chiller

    Frank
    I had seen some machines with two L.P switches, one for the pump down and one for the system safety cut out, If that was not an original part then may be some one had expericened neusense trips and he added a timer in the circuit for to avoid it. The system will cut out after some time and not immediatly as
    at the time when L.P cuts out.

Similar Threads

  1. Water Chiller Control
    By David PS in forum Air Conditioning
    Replies: 4
    Last Post: 29-08-2006, 11:14 PM
  2. Mcquay PES Flooded Water Cooled Screw Chiller
    By Brian in forum Technical Speculations
    Replies: 4
    Last Post: 05-07-2006, 09:43 PM
  3. water chiller
    By andrewuk in forum Technical Speculations
    Replies: 9
    Last Post: 17-10-2005, 09:28 PM
  4. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM
  5. water chiller
    By dwallan in forum Air Conditioning
    Replies: 3
    Last Post: 12-12-2001, 03:17 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •