hi all, is it just me or r u all finding that tk sb111tci have very low td on the host unit even when all remote zones are off, has any one got any ideas??
td is -2.4 on host ambiant of 38 deg c all remotes off
refrigerant full charge, clean cond coil, sensor calibration correct, compressor efficientcy test pass, tx sreen clear, nill hot gas leakage, all seems to check out, havent done tx superheat as believe that should be last thing. is there any thing else i have missed first??
-
10-01-2008, 04:39 PM #2
Re: early tk multi temp, sb111 tci
What happens to the td if you put 2nd zone in heat?
-
11-01-2008, 03:21 AM #3
Re: early tk multi temp, sb111 tci
Dont touch the super heat, this is rarely by 99% of the time never the problem.
Have you checked the basics like,Compressor capacity test? poor capacity cause low td
How close is the zone divider bulkhead to the host unit. if it is close with in a few feet the unit will short cycle and cause low TD.
If this is not the issue, What are yyour system pressures while other zones in null or not in use.
Does the TD improve when other zones are on?
Have you performed a LLS ttest for all zones, and HGS test for all zones? valave and check valves that leak by cause low td along with abnormally hi frosted suction lines.
A-Z
Similar Threads
-
MP66 & Compressor Overheating
By Intermez in forum Technical DiscussionsReplies: 111Last Post: 13-04-2010, 08:58 PM -
Multi temp installations
By nova in forum TransportReplies: 6Last Post: 13-09-2008, 09:38 PM -
Compressor loading, cooling, and range of operation.
By Air duster in forum FundamentalsReplies: 10Last Post: 02-04-2008, 08:39 AM -
cold room temp & the product temp
By smpsmp45 in forum NH3Replies: 9Last Post: 21-09-2007, 11:46 PM