    early tk multi temp, sb111 tci



    hi all, is it just me or r u all finding that tk sb111tci have very low td on the host unit even when all remote zones are off, has any one got any ideas??
    td is -2.4 on host ambiant of 38 deg c all remotes off
    refrigerant full charge, clean cond coil, sensor calibration correct, compressor efficientcy test pass, tx sreen clear, nill hot gas leakage, all seems to check out, havent done tx superheat as believe that should be last thing. is there any thing else i have missed first??



  2. #2
    Join Date
    Oct 2007
    Location
    USA
    Age
    48
    Posts
    9
    Rep Power
    0

    Re: early tk multi temp, sb111 tci

    What happens to the td if you put 2nd zone in heat?

  3. #3
    Join Date
    Dec 2007
    Location
    Tampa, Florida U.S.A
    Age
    51
    Posts
    590
    Rep Power
    17

    Re: early tk multi temp, sb111 tci

    Quote Originally Posted by daniel ox View Post
    hi all, is it just me or r u all finding that tk sb111tci have very low td on the host unit even when all remote zones are off, has any one got any ideas??
    td is -2.4 on host ambiant of 38 deg c all remotes off
    refrigerant full charge, clean cond coil, sensor calibration correct, compressor efficientcy test pass, tx sreen clear, nill hot gas leakage, all seems to check out, havent done tx superheat as believe that should be last thing. is there any thing else i have missed first??
    Dont touch the super heat, this is rarely by 99% of the time never the problem.

    Have you checked the basics like,Compressor capacity test? poor capacity cause low td

    How close is the zone divider bulkhead to the host unit. if it is close with in a few feet the unit will short cycle and cause low TD.

    If this is not the issue, What are yyour system pressures while other zones in null or not in use.

    Does the TD improve when other zones are on?

    Have you performed a LLS ttest for all zones, and HGS test for all zones? valave and check valves that leak by cause low td along with abnormally hi frosted suction lines.

    A-Z

Similar Threads

  1. MP66 & Compressor Overheating
    By Intermez in forum Technical Discussions
    Replies: 111
    Last Post: 13-04-2010, 08:58 PM
  2. Multi temp installations
    By nova in forum Transport
    Replies: 6
    Last Post: 13-09-2008, 09:38 PM
  3. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  4. cold room temp & the product temp
    By smpsmp45 in forum NH3
    Replies: 9
    Last Post: 21-09-2007, 11:46 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •