Results 1 to 16 of 16
Thread: Choosing a unit?
03-01-2008, 05:46 PM #1
Choosing a unit?
Hi Guys Happy new year first of all
A friend of mine has just had a conservatory built which is 18 square meters. He has asked me for a price for a wall mounted split unit. He doesn't want really cheap kit but thn again he doesn't want to pay the earth for it.
I worked out that he would need 5-6kw based on 330w per meter squared. I rang Daikin and got a quote of £850 for their FTXS60, i then rang Fujitsu and got a quote for a Fujitsu plasma 5.2 Kw and got a quote for £740.
Can anyone recommend a good system that i could get for around the £600 mark?
Marc
04-01-2008, 07:13 AM #2
Re: Choosing a unit?
hi marc
you said 18 square meter from did you get the formula every square meter needs 650 btu per sq meter thats mean 11200 btu plus heat load everyperson needs 660 btu sitting 1000 btu working every watt of lighting 3.4 btu than you can convert 1 kw=3411btu
sharp is a good ac and problem free
good luck
04-01-2008, 08:56 AM #3
I would put a 7 kw in so you can get enough heat out of it in the winter.
04-01-2008, 10:26 PM #4
but what make would you suggest?
Marc
04-01-2008, 11:09 PM #5
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
05-01-2008, 09:14 AM #6
hitachi dc inverter, put afew of these in. very good imho
rob
price wise v good aswell
05-01-2008, 04:05 PM #7
I would say fujitsu as well. Up there with daikin for quality, but they run slightly cheaper. They may be more expensive than other brands, but they tend to last alot longer (in my personal experience anyway).
06-01-2008, 12:56 PM #8
Mitsubishi Heavy SRK63ZE is a good unit. rated at 6.3 kw and comes in cheaper than both Daikin & Fujitsu.
17-02-2008, 12:56 PM #9
Cheers for all the replies
Marc
17-02-2008, 03:28 PM #10
toshiba inverter have one in my house. installed loads very rare any probs and cheap to get hold of
20-02-2008, 02:43 PM #11
how do you size up for a split system
20-02-2008, 05:35 PM #12
Hi simond - and welcome to the forum. I see that you are an apprentice - is that in refrigeration?
To size up for a split system (assuming that it's for air conditioning) and you want it for a cooling application, you have to calculate the total heat gain into the space to be cooled. This can include:
Fabric gains
Ventilation gains
Infiltration gains
Lighting gains
Occupancy gains
Equipment gains
Your location in the world can affect these calcs. The time of day that you intend to use the equipment can also affect the size of system you need, i.e. if you want it to cool your conservatory during the day or if you only want it to cool an office in the middle of the night for a night worker.
If you want a split system primarily for heating then you have to calculate the total heat losses to the space you want to heat.
It's quite a complex task, which is why I suppose, most 'engineers' guess
20-02-2008, 07:55 PM #13
Frank, Are you OK, you didnt mention a Daikin
Although the original post did say a reasonably priced unit
Fatboy
20-02-2008, 10:38 PM #14
25-02-2008, 09:59 PM #15
LG art cool......
06-03-2008, 10:56 PM #16
Btw he ended up getting the same as i have in my conservatory a Daikin wall mount FTXS60BVMB, just thought i'd let you all know.
Marc
Thermo King OptiSet
By REEFER-TEK in forum TransportReplies: 4Last Post: 06-12-2007, 07:23 PM -
TK basic micro-p features and functions
By REEFER-TEK in forum TransportReplies: 0Last Post: 05-12-2007, 06:25 PM -
Off-line Mitsi VRF leaks!
By sinewave in forum Air ConditioningReplies: 8Last Post: 05-06-2007, 11:18 PM