    Scroll compressor



    When wiring a 3 phase scroll compressor it is critical to connect correctly. Is there a way to determine if the phases are connected correctly without having to start the compressor and listening to it.



  2. #2
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24
    I'm assuming that it's a hermetic.

    There is no way of telling from a static compressor unless you have the manufacturers wiring instructions and you already know the connected phase order.

    Most units will have a built in interlock that prevents incorrect phase rotation.

    So, you have to start the unit. There are a number of ways to find out.

    In descending order of 'correctness' they are:

    Method 1 - Obtain a phase rotation meter.
    They cost about 20 or 30 quid. Most suppliers will stock one. It's a set of three coloured leads on a small solid state box that you connect to the three phases. It usually comes with a set of LEDs that indicate the direction of rotation. You have a 50% chance of getting it right first time.
    You will need the manufacturer to tell you the correct rotation. When you have one of these you will probably use it once in a blue moon.

    Method - 2 If you have another unit of the same type, have a look at the connections and wire it the same.

    Method - 3 Run it for half a minute with your gauges and ammeter on, then reverse two phases and run it again. The one where the suction, discharge and current don't do much is the wrong way.


    Most people will opt for methods 2 or 3, usually the latter.

    With a centrifugal compressor, a sight glass is usually privided so that the end of the rotor can be seen. You spin the comp for a few seconds under power and watch the direction.

    Despite what the good books say, I'm afraid that it's mostly hit and miss.

    good luck

    Argus
    ________
    Niki Lauda
    Last edited by Argus; 07-02-2011 at 07:51 AM.

  3. #3
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27
    Argus

    It is hermetique
    Thanks for the info, very very helpful
    May your life be blessed!!!

    Im opting for method 3, compressor is a Bristol York ACU type
    It does have a sight glass

    Best regards

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51
    Hi Ayb

    I once went to investigate an IMI condensing unit that was reportedly not cooling. It was in a building in the centre of Nottingham that was opened about 15 months previously. The complaint was raised because the room it was serving had a number of electronic boxes fail due to high heat.

    When I got there the unit was running (IMI MCU+80) but no heat was coming out of the condenser fan. Put the gauges on and the amp clamp and saw running currents within tolerances but no difference in the pressures. Changed the phase rotation and the system started to cool! 15 months running the wrong way - can you believe that??

    I always use a phase rotation device before commissioning a new 3 phase unit - only cost a few quid but really save the guesswork.

    Frank

  5. #5
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24
    Thank you Aiyub, I appreciate the felicitations in these nasty times it goes a long way.

    Franks job reminds me of exactly the same thing I hadwith a Carrier 19 series centrifugal working R 11 many, many years ago in the Gulf.

    .....It's amazing what getting the direction right can do for the duty! This thing had been running for a year like that.

    Nobody would believe that I travelled 3 days for a 20 minute job!

    Argus
    ________
    GSX-R1100
    Last edited by Argus; 07-02-2011 at 07:51 AM.

  6. #6
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25
    Excellent advice, Argus. I might add that scrolls are less sensitive to reverse rotations as compared to screws. So just looking at the gauges during start is entirely adequate.

    I am amazed at Frank's example of a scroll running backwards for such a long time. IMI must have one fine lubrication system!

Similar Threads

  1. About Copeland ZB scroll compressor
    By ernestlin in forum Technical Speculations
    Replies: 18
    Last Post: 27-08-2009, 08:39 AM
  2. Dual Scroll Compressor
    By ernestlin in forum Technical Discussions
    Replies: 7
    Last Post: 27-06-2006, 04:14 AM
  3. 60Hz Copeland scroll compressor
    By Lc_shi in forum Fundamentals
    Replies: 5
    Last Post: 05-06-2006, 09:08 PM
  4. Scroll Compressor
    By dwallan in forum Commercial
    Replies: 1
    Last Post: 30-07-2001, 04:18 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •