    Suction valve icing



    I have a question similar to QQQ. After starting 4-compressor station I saw an ice on suction valves of compressors. Is it an attribute of liquid flow (insufficient superheat) to the compressor or a normal situation?
    Suction temperature -34 deg C.
    Condensation temperature +35 deg C.
    Is it necessary to adjust TEV?



  2. #2
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    In order to accurately evaluate the system, we need the following:

    Low side:

    evap air in temp
    evap air out temp
    SST (saturated suction temp)
    suction line temp near evap coil
    suction line temp near compressor

    High side:

    cond air in temp
    cond air out temp
    SCT (saturated condensing temp)
    liquid line temp at outdoor unit
    liquid line temp at metering device inlet

  3. #3
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25
    After starting 4-compressor station I saw an ice on suction valves of compressors. Is it an attribute of liquid flow (insufficient superheat) to the compressor or a normal situation?
    The observations that Gary requires are important for a thorough understanding, but if you are doing a startup on a parallel compressor rack and see ice on the suction valves, and not previous or upstream of the suction valves, I would think you have a problem that requires immediate addressing. The first thing that comes to mind is turn the machine off, and sit quietly with wonder and fear. Achieving understanding when everything is turned off buys you time to rethink how much you understand and how accurately you recall what you just witnessed.

    That only applies if you mean the suction valves of the compressors. If you see ice on Evaporator Pressure regulating valves, then you can relax somewhat.

    From your question, I am picturing that you saw ice form only on the suction valves of all the compressors. Perhaps we could improve upon your original question?

  4. #4
    Join Date
    Sep 2002
    Location
    Moscow
    Age
    45
    Posts
    9
    Rep Power
    0
    There is an ice on compressors suction valves, suction ball valves (because these are non-insulated), non-insulated areas of suction pipes.

    As regards values mentioned by Gary - there are difficult to measure - we don't have thermometrs, measuring temperature on suction line near compressor.

    By the way - is it nesessary to have suction line thermometers?

  5. #5
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24
    Hi Maxim,
    You should be carrying a thermometer as a standard service tools. What you are working on is a refrigeration system, with heat carrying fluids that operate on a temperature pressure relationship.
    Ice is normally on low temp suctions. Your refrigerant leaves the evaporator superheated by about 8 deg C,the refrigerant is further heated by ambidnt temperature, but to leave the refrigerant at above 0 deg C the suction would require heating by a further 23 to 25 deg C, unless you have no , or very poor insulation this should not happen.
    Determine the temperature at the compressor inlet, if it is close to or matches the refrigerant saturation temperature you have liquid carry-over, if not ice is normal for a low temperature application.
    Regards. Andy

  6. #6
    Join Date
    Sep 2002
    Location
    Moscow
    Age
    45
    Posts
    9
    Rep Power
    0
    Thanks a lot

  7. #7
    Join Date
    Oct 2004
    Location
    U.K.-London
    Posts
    144
    Rep Power
    20

    Re: Suction valve icing

    Quote Originally Posted by Gary
    In order to accurately evaluate the system, we need the following:

    Low side:

    evap air in temp
    evap air out temp
    SST (saturated suction temp)
    suction line temp near evap coil
    suction line temp near compressor

    High side:

    cond air in temp
    cond air out temp
    SCT (saturated condensing temp)
    liquid line temp at outdoor unit
    liquid line temp at metering device inlet
    Hi Gary

    As a matter of interest, how do you go about analyzing the data that you ask for.
    I am busy studying an HNC in Refrigeration/Aircon and am quite interested in learning more.
    Thanks
    Never underestimate anybody, you never know when they will make you look like an idiot!

  8. #8
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Suction valve icing

    In general, TD's indicate load, dT's indicate airflow, subcooling and superheat indicate refrigerant, and approaches indicate heat transfer. You'll be amazed at how much these numbers can tell you. It's like you can see inside the system.

  9. #9
    Join Date
    Oct 2004
    Location
    U.K.-London
    Posts
    144
    Rep Power
    20

    Re: Suction valve icing

    Quote Originally Posted by Marc O'Brien
    To put it another way, TD's tell you about the relationship between load and heat flow and then dT's tell you about the relationship between heat flow and mass flow. Subcool and superheat can be used to give a parallax or cross reference with which to qualify the seen balances, the nature of their deviation, between load, heat flow and mass flow.
    It all sounds very interesting. I'm sure we'll be covering this within the HNC I am doing now. If we don't then I will seriously consider one of your day courses Marc.
    I dont suppose there is a place on the web that covers this subject??
    Never underestimate anybody, you never know when they will make you look like an idiot!

Similar Threads

  1. Need a correctly sized valve
    By Abe in forum Commercial
    Replies: 2
    Last Post: 26-10-2005, 08:42 PM
  2. why icing on the suction valve
    By ong in forum Fundamentals
    Replies: 14
    Last Post: 12-06-2005, 10:03 PM
  3. Relief Valve on Suction
    By Latte in forum Commercial
    Replies: 19
    Last Post: 20-01-2004, 11:57 PM
  4. Replies: 5
    Last Post: 16-10-2002, 12:38 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •