23-03-2003, 02:41 PM #1
Suction valve icing
I have a question similar to QQQ. After starting 4-compressor station I saw an ice on suction valves of compressors. Is it an attribute of liquid flow (insufficient superheat) to the compressor or a normal situation?
Suction temperature -34 deg C.
Condensation temperature +35 deg C.
Is it necessary to adjust TEV?
-
23-03-2003, 02:59 PM #2
In order to accurately evaluate the system, we need the following:
Low side:
evap air in temp
evap air out temp
SST (saturated suction temp)
suction line temp near evap coil
suction line temp near compressor
High side:
cond air in temp
cond air out temp
SCT (saturated condensing temp)
liquid line temp at outdoor unit
liquid line temp at metering device inlet
-
25-03-2003, 02:06 AM #3After starting 4-compressor station I saw an ice on suction valves of compressors. Is it an attribute of liquid flow (insufficient superheat) to the compressor or a normal situation?
That only applies if you mean the suction valves of the compressors. If you see ice on Evaporator Pressure regulating valves, then you can relax somewhat.
From your question, I am picturing that you saw ice form only on the suction valves of all the compressors. Perhaps we could improve upon your original question?
-
25-03-2003, 06:20 PM #4
There is an ice on compressors suction valves, suction ball valves (because these are non-insulated), non-insulated areas of suction pipes.
As regards values mentioned by Gary - there are difficult to measure - we don't have thermometrs, measuring temperature on suction line near compressor.
By the way - is it nesessary to have suction line thermometers?
-
25-03-2003, 06:51 PM #5
Hi Maxim,
You should be carrying a thermometer as a standard service tools. What you are working on is a refrigeration system, with heat carrying fluids that operate on a temperature pressure relationship.
Ice is normally on low temp suctions. Your refrigerant leaves the evaporator superheated by about 8 deg C,the refrigerant is further heated by ambidnt temperature, but to leave the refrigerant at above 0 deg C the suction would require heating by a further 23 to 25 deg C, unless you have no , or very poor insulation this should not happen.
Determine the temperature at the compressor inlet, if it is close to or matches the refrigerant saturation temperature you have liquid carry-over, if not ice is normal for a low temperature application.
Regards. Andy
-
26-03-2003, 06:40 PM #6
Thanks a lot
-
21-10-2004, 05:28 PM #7
Re: Suction valve icing
Originally Posted by Gary
As a matter of interest, how do you go about analyzing the data that you ask for.
I am busy studying an HNC in Refrigeration/Aircon and am quite interested in learning more.
ThanksNever underestimate anybody, you never know when they will make you look like an idiot!
-
22-10-2004, 06:35 AM #8
Re: Suction valve icing
In general, TD's indicate load, dT's indicate airflow, subcooling and superheat indicate refrigerant, and approaches indicate heat transfer. You'll be amazed at how much these numbers can tell you. It's like you can see inside the system.
-
23-10-2004, 09:41 AM #9
Re: Suction valve icing
Originally Posted by Marc O'Brien
I dont suppose there is a place on the web that covers this subject??Never underestimate anybody, you never know when they will make you look like an idiot!
Similar Threads
-
Need a correctly sized valve
By Abe in forum CommercialReplies: 2Last Post: 26-10-2005, 08:42 PM -
why icing on the suction valve
By ong in forum FundamentalsReplies: 14Last Post: 12-06-2005, 10:03 PM -
Relief Valve on Suction
By Latte in forum CommercialReplies: 19Last Post: 20-01-2004, 11:57 PM -
TEV with MOP: how to keep valve body temp above bulb temp?
By DaBit in forum FundamentalsReplies: 5Last Post: 16-10-2002, 12:38 AM