Results 1 to 12 of 12
Thread: carel ir33 controllers
14-12-2007, 11:45 PM #1
has anyone had bother with carel ir33 controllers on network systms coming up with etc fault but still having the correct times in the controller this is starting to get on my nerves as iam always having to reset the controllers
15-12-2007, 01:05 AM #2
Re: carel ir33 controllers
Fowlie.
Hi if as I suspect your are way ahead of me when dealing with these controllers. Please ignore the link attached below.
This will open on a search page.
under type select MANUAL
under range select IR33
chose your required pdf. from the list.
Incidently the search page covers a huge range of Carel Product.
http://www.carel.com/carelcom/web/en...icerca_doc.jsp
15-12-2007, 09:26 PM #3
cheers for that link grizzly only ever had the set up leaflet and you know how basic they can be.
15-12-2007, 11:01 PM #4
We have a lot of these controllers and as of yet no problems,I much prefer the RDM mk2 which is more user friendly.
Regards Bernard
16-12-2007, 12:29 AM #5
I have a Carel IR33 that wont read the correct temperatures, have looked in the manual thinking that it was set on deg F but it is not, I reckon it is reading about 30 deg C high if not more. We have not shortened the probe cables or anything like that but am at a bit of a loss with it. I have even tried a different controller and it still reads wrong everything points to the probes but they are definately Carel ones.
Anybody got any ideas?
Ian
16-12-2007, 12:38 AM #6
Is this a new unit install Pooh or an old one that has 'gone off' ?
If it reads wrong with a different controller then it would suggest that the probe itself is at fault.
Have you tried the 'faulty' controller on the other probes? If it shows your expected temps then that would also point at the probes being at fault.Brian - Newton Abbot, Devon, UK
16-12-2007, 12:47 AM #7
Pooh.
Follow the link below and open Technical Bullitin no 15.
It has a section on how to test probes of all sorts
There is also a section on how to test ouputs ect from controllers.
There is enough there to confirm where the problem lies.
http://www.invensyscontrolseurope.co...lBulletins.htm
16-12-2007, 01:04 PM #8
what a brilliant document every service engineer should have a copy in his van. Thanks for that mate.
Ian
16-12-2007, 10:44 PM #9
Just like to add that with some controlers you can set the display to read higher or lower to allow for long cable runs to the probes, but as you have tryed a different controller in prohably isnt this. Also some are selectable for NTC and PTC probes.
Hate the things, i usually spend five minutes trying to read the manual before realising i'm on the foriegn page Then when you do get it, its gone back to displaying the temperature
Jon
16-12-2007, 10:52 PM #10
17-12-2007, 12:34 AM #11
17-12-2007, 07:14 PM #12
Yeah, offset sounds about right. I'm not that good with these style of controlers as i only work on them a few times a year, hence the trouble with the destructions
Jon
Kiour controllers
By Andy AC in forum CommercialReplies: 20Last Post: 09-02-2010, 06:19 PM -
Daikin Controllers
By MadMax in forum Heat PumpsReplies: 12Last Post: 22-07-2008, 03:46 AM -
Mitsubishi Alpha Controllers
By frank in forum Air ConditioningReplies: 4Last Post: 21-07-2004, 08:44 PM -
Carel Controllers
By Latte in forum Computers & the InternetReplies: 2Last Post: 21-05-2004, 09:01 PM -
Liropa Controllers (Linde Fridges)
By Latte in forum Refrigeration BooksReplies: 1Last Post: 25-02-2003, 09:17 PM