12-12-2007, 07:16 PM #1
Fujitsu AUY 30 Failing to Heat
Hi All
Problems with a newly installed AUY 30 Fujitsu Cassette 240v Heat pump
After the installation and commissioning of the system we found that the off coil temp in heating mode was about +21 it didn't want to go any higher.
The suction pressure was around 110 psig liquid line around the same.
Please could anyone help as the store manger is rather cold today.
-
12-12-2007, 07:55 PM #2
Re: Fujitsu AUY 30 Failing to Heat
bbbbuurrrrr.....ithe unit turned on? is it in heat mode?is the compressor running? is the compressor driving the right way?
rgrds phil
-
12-12-2007, 09:03 PM #3
Re: Fujitsu AUY 30 Failing to Heat
Hi Phil
Yes its doing all of that.
-
12-12-2007, 09:06 PM #4
Re: Fujitsu AUY 30 Failing to Heat
Hi Phil
Do you think I would have asked for help before checking the obvious!
-
12-12-2007, 09:07 PM #5
Re: Fujitsu AUY 30 Failing to Heat
Has the reversing valve changed over correctly, have you tried it with a magnet?
What is it like in cooling mode?
Are the service valves fully open?Brian - Newton Abbot, Devon, UK
Retired March 2015
-
12-12-2007, 09:12 PM #6
Re: Fujitsu AUY 30 Failing to Heat
HI Brian
The service valves are fully open
Its trying to heat but ends up going on defrost before it reaches its target temperature.
-
12-12-2007, 09:16 PM #7
Re: Fujitsu AUY 30 Failing to Heat
Could there be a problem with the coil/air temperature sensors ? Either faulty or displaced from their holders.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
12-12-2007, 09:21 PM #8
Re: Fujitsu AUY 30 Failing to Heat
Hi Brian
Its definetly food for thought. Will try tommorrow.
Thanks
-
12-12-2007, 10:58 PM #9
Re: Fujitsu AUY 30 Failing to Heat
Is it just a single system or were there more installed at the same time? - crossed pipes / wiring maybe, we've all done it before.
You also mentioned that the suction and liquid pressures were the same - compressor running but not pumping? Was there any movement on the gauges when you started the compressor?
Andy
-
13-12-2007, 10:22 AM #10
Re: Fujitsu AUY 30 Failing to Heat
You wouldn't be able to even get the suction or liquid pressures.
I don't think these have a schrader on the condenser, (which would be the evaporator in heat mode), so on heat you couldn't get the suction anyway.
The suction service valve on heat mode would be showing the discharge pressure.
What's the full model code?
What does it do on cooling?
Is the condenser actually icing up and going on defrost legitimately, or is the condeser clear of frost and ice and it going on defrost for no reason?
edit: Use test mode to get it to run on cooling if it's a low ambient, - if it's the wall controller with an orange start button and flip down lid, hold down mode and fan button to get test mode.Last edited by paul_h; 13-12-2007 at 10:26 AM.
-
13-12-2007, 08:17 PM #11
Re: Fujitsu AUY 30 Failing to Heat
Hi All
Sorted the problem
I removed the precharge supplied with the unit and re commissioned with fresh R410A refrigerant.
Running pressures and amps all okay
Working fine
-
13-12-2007, 09:17 PM #12
Re: Fujitsu AUY 30 Failing to Heat
Good to hear.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
13-12-2007, 10:45 PM #13
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Fujitsu AUY 30 Failing to Heat
Last edited by nike123; 13-12-2007 at 11:52 PM. Reason: correction of sentence
-
13-12-2007, 10:48 PM #14
Re: Fujitsu AUY 30 Failing to Heat
Hi pal
If your ever stuck again try www.airconsquad.co.uk
There pretty good on fujitsu tech work.
Cheers
Danny
-
13-12-2007, 11:17 PM #15
Re: Fujitsu AUY 30 Failing to Heat
-
13-12-2007, 11:29 PM #16
Re: Fujitsu AUY 30 Failing to Heat
Viking what sort of pressures are you applying during a pressure test?
Incidently what sort of pressure would you apply for a 407a system guys?
Cheers grizzly
-
13-12-2007, 11:46 PM #17
Re: Fujitsu AUY 30 Failing to Heat
Now you got me....
I don't do installs any more.
I will ask some of the guys tomorrow.....
(Sorry)
-
14-12-2007, 12:05 AM #18
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Fujitsu AUY 30 Failing to Heat
After every instalation, I check with soap solution every connection and valve cap, and I don't see any reason to pressure test unit after that. It is common knowledge that every 3way and 2way valve on split systems leaks when they are frequently used, and because of that, all off them have valve cap. After every manipulation of valves, it is ( at least, for me) obligatory to test valve cap with soap solution.
-
14-12-2007, 12:22 AM #19
Re: Fujitsu AUY 30 Failing to Heat
Hi brian
I have spoke to webram a while back,its ok because weve put a link on our website of RE.
Cheers
Danny
-
14-12-2007, 12:24 AM #20
-
14-12-2007, 12:45 AM #21
Re: Fujitsu AUY 30 Failing to Heat
Nike,
First of all, good engineering practices dictates that all installations are pressure tested......
Secondly, I believe that you misunderstood the issue.
These "problem" valves are leaking internally(when shut), from the pipe work in to the condensor, you will never find that with soapy water on the outside.
-
14-12-2007, 08:06 AM #22
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
14-12-2007, 11:45 PM #23
Re: Fujitsu AUY 30 Failing to Heat
We've had leaking valves on Fujitsu units efore now!
I think the OFN mixed with the Refrigerant is a likely cause too!
-
15-12-2007, 12:23 AM #24
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Fujitsu AUY 30 Failing to Heat
When you installing compact split systems with flexible (annealed) coper pipes you don't need to pressure test it (because there is no brazing involved).
It is sufficient to vacuum it below 400 microns, then isolate vacuum pump, and if vacuum after 10-15 minutes stays below 400 microns you could be pretty sure that there is no leak.
Than, after you let refrigerant into pipes and indoor unit, you simply test flare connections with soap solution after you put unit to heating mode.
This is my method!Last edited by nike123; 15-12-2007 at 10:04 AM.
-
15-12-2007, 12:51 AM #25
Re: Fujitsu AUY 30 Failing to Heat
No comment.
-
15-12-2007, 02:25 AM #26
Re: Fujitsu AUY 30 Failing to Heat
Just be wary of the leaking valves, or you'll vac out the condensing unit. I've seen it happen about a dozen times. When removing the service valve flare cap, see if theres any pressure behind it. Let the pressure out then refit the cap loosely and see if there's any bubbles around it before installation to see if the valve holds.
Last edited by paul_h; 15-12-2007 at 02:28 AM.
-
15-12-2007, 05:44 AM #27
Re: Fujitsu AUY 30 Failing to Heat
Hi All
The Australian Fujitsu web site shows the minimum pipe length to be 5m. If the units are located closer together there may be a heat or cool problem with operating pressures.
As I plan to install a ducted Fujitsu next week where the pipe length may be less than 5m, I'm keen on knowing how to proceed. Remove refrigerant or have ugly loops of refrigerant pipes.
My theory on flare fittings is that a good vacuum could be achieved as the fittings will forced together, but then leak refrigerant when pressure is applied as pressure will obviously push the copper flare away from the brass fitting.
Anyone agree or is my theory wrong!
Gary
-
15-12-2007, 07:30 AM #28
Re: Fujitsu AUY 30 Failing to Heat
How can a ducted be less than 5m.
Don't tell me you are putting the o/u high up on the wall and the indoor right above the eaves?
It's pretty easy to get 5m pipe runs on a ducted, 2m up the wall, 4-6 metres accross the ceiling to the midlle and highest point of the ceiling.
The pipe length is more for heating, too short a pipe run and it will be overcharged, with gas noises heard from the indoor unit. It doesn't matter so much on cooling because of the suction accumultors and condenser fan control. It's hard to balance by removing refrigerant, you may end up with an undercharge in cooling, still get gas noises in heating, and it could void the warranty.
How can you end up with ugly extra coiled pipes when it's a ducted unit that goes through the ceiling anyway?
Flares leak because they are loose, rough or burred, so they'll leak under vacuum. But there's no point saying it has a vacuum so it doesn't leak, without a accurate vacuum gauge getting a 'vacuum' tells you nothing, you need to be able to measure it in microns, not your service gauges.Last edited by paul_h; 15-12-2007 at 07:33 AM.
-
15-12-2007, 10:22 AM #29
Re: Fujitsu AUY 30 Failing to Heat
Paul
Thankyou for your reply. The ducted unit will be in an office building with the condenser on the wall and the indoor about 2m on the other side. The current York ducted is to be replaced with a larger Fujitsu.
I agree, a digital vacuum meter should indicate a problem with a flare. The flare nut problem occurred many years past when digital vacuum meters were not common.
Gary
-
15-12-2007, 10:25 AM #30
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
15-12-2007, 10:39 AM #31
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
09-01-2008, 04:30 PM #32
Re: Fujitsu AUY 30 Failing to Heat
Late entry here but a few tips from someone who knows
If you are taking the flare nuts off the service valve don't be an oaf and just crank on the flare nut without supporting the body of the valve by countering the force you apply with another spanner on the cap of the service valve. Fuji's early R410A offerings did seem to be bit funny in this area but only if you were brutal and I have never had it occur myself. But the later ones if you look closely seem to have about twice as much brass in the body of the service valve as the earlier ones.
As far as pressure testing if you don't exceed the standing pressure inside the outdoor unit then there is no chance of blowing your OFN into the outdoor unit is there
-
09-01-2008, 04:39 PM #33
Re: Fujitsu AUY 30 Failing to Heat
That's only 1500kpa at best, while the joins have to be good enough to seal at 3500kpa on heating mode.
-
12-07-2008, 07:50 AM #34
Re: Fujitsu AUY 30 Failing to Heat
Similar Threads
-
Capacity control
By sparrow in forum TrainingReplies: 44Last Post: 18-01-2010, 07:49 PM -
Fujitsu heat recovery
By chillyblue in forum Air ConditioningReplies: 11Last Post: 13-07-2008, 11:10 AM -
frostles heat pump
By Lc_shi in forum New TechnologiesReplies: 27Last Post: 31-03-2008, 07:53 AM -
Daikin VRVII
By Cool100 in forum Air ConditioningReplies: 17Last Post: 14-10-2007, 10:26 AM -
heat exchanger for small chiller
By star882 in forum FundamentalsReplies: 4Last Post: 30-01-2007, 12:06 PM