    Hermetic compressor tripping



    Hi

    I have a hermetically sealed compressor, which is used on a machine which runs for 25-40mins to freeze, that is it's cycle and job.
    When it is running system pressures are good and it does it's job
    BUT!!!

    Problem the compressor runs on R404a and has two cappillary tubes feeding two plates which it freezes.
    The compressor is tripping after about 20 mins into it's cycle, i have changed the drier, cappillaries and vacuumed the system and recharged with fresh refrigerant to the manufacturers weight.
    The compressor still trips, i've check the compressor capacitor and relay them seem OK
    I've put high pressure OFN into the discharge pipe and i don't get anything come out the suction, so i assume the valves are OK, I have run the compressor totally disconnected and the amps read are still higher than the manufacturers name plate, i'm reading 6.4, name plate reads fla 4.5 and i'm assuming this is why the thermal overload trips.

    Don't know what else to do apart from change the compressor???

    Any ideas

    CB



  2. #2
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: Hermetic compressor tripping

    So this compressor is CSIR?
    Does the start relay disengage properly?
    Can you get the compressors rated winding resistance from the manufacturer and compare to the actual?

  3. #3
    Join Date
    May 2007
    Location
    Northants
    Posts
    290
    Rep Power
    17

    Re: Hermetic compressor tripping

    Thanks paul

    I have started the compressor manually and the amps are still high, thats how i know it's not the starting gear. I shall have to try and get the ratings.

    CB

  4. #4
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Hermetic compressor tripping

    Check the voltage at the compressor while it is running. Loose or burnt connections or contacts anywhere in the circuit can cause a voltage drop, which increases the amperage.

    If the voltage is ok, the relay may be stuck in the closed (start) position. You may want to try a new relay before replacing the compressor.

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Hermetic compressor tripping

    What are the running amps when the compressor is connected ?

    Some motors can tend to high amperage when there is no load on them.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Hermetic compressor tripping

    Can you give the brand and type of the compressor?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  7. #7
    Join Date
    May 2007
    Location
    Northants
    Posts
    290
    Rep Power
    17

    Re: Hermetic compressor tripping

    Hi all

    What are the running amps when the compressor is connected ?

    Some motors can tend to high amperage when there is no load on them.
    The amps are the same mate, as said before the rating plate shows 100v 50hz 4.5amps
    115v 60hz 4.5amps

    i'm running 110volt 50hz at between 5.3-6.7amps connected or disconnected.

    The compressor is a Tecumseh AEZ2451Z

    Thanks for the help

    CB

  8. #8
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: Hermetic compressor tripping

    When you ay you started it manually, do you mean with an annie?
    Or how else did you start it manually without using the possibly defective relay on the compressor?

  9. #9
    Join Date
    May 2007
    Location
    Northants
    Posts
    290
    Rep Power
    17

    Re: Hermetic compressor tripping

    hi Paul

    No i just short the start winding in series with the start capacitor, from the run winding terminal.
    Word of warning though BE CAREFUL!!!!..

    CB

  10. #10
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Hermetic compressor tripping

    Did you mean Tecumseh AEZ2514Z. There is no AEZ2541Z in Tecumseh documentation.
    Compare these data to your case, and if amperage you read and that in table are different more than 10% change the compressor.
    Attached Files Attached Files

  11. #11
    Join Date
    May 2007
    Location
    Northants
    Posts
    290
    Rep Power
    17

    Re: Hermetic compressor tripping

    Thanks Gary

    Quote Originally Posted by Gary View Post
    Check the voltage at the compressor while it is running. Loose or burnt connections or contacts anywhere in the circuit can cause a voltage drop, which increases the amperage.
    At what drop in voltage will it start to cause a problem??, And i suppose it is best to meter it at the compressor terminals (end of the line)

    Cheers Nike

    That looks handy software, can it be downloaded??

    CB

  12. #12
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Hermetic compressor tripping

    Quote Originally Posted by chillyblue View Post
    Thanks Gary


    At what drop in voltage will it start to cause a problem??, And i suppose it is best to meter it at the compressor terminals (end of the line)
    You're welcome. Did you find the problem?

    Generally, more than 10% drop in voltage is unacceptable... and yes it should be checked at the end of the line.

    It is good practice, when replacing any power consuming (load) device, to check voltage at the device with that device operating.

    When a load device burns out, it often burns contacts in switching devices due to the excess amperage passing through them in the burnout. Replacing the load device without resolving this can lead to another burnout.
    Last edited by Gary; 11-12-2007 at 09:08 PM.

  13. #13
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Hermetic compressor tripping

    Quote Originally Posted by chillyblue View Post

    That looks handy software, can it be downloaded??

    CB
    Snagit or the selection software?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  14. #14
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Hermetic compressor tripping

    Quote Originally Posted by chillyblue View Post

    Cheers Nike

    That looks handy software, can it be downloaded??

    CB
    No, but you could request it on www.tecumseh-europe.fr by completing request form on Contact tab and they wil send it to you by mail.

Similar Threads

  1. Dorin Semi hermetic Compressor
    By Samarjit Sen in forum Industrial Compressors
    Replies: 5
    Last Post: 02-07-2007, 04:06 PM
  2. do we need a hermetic or semi hermetic comp.?
    By duraid in forum Fundamentals
    Replies: 14
    Last Post: 17-04-2007, 05:52 PM
  3. Oil changing on hermetic compressors.
    By alexdouglas1969 in forum Fundamentals
    Replies: 8
    Last Post: 12-04-2007, 04:22 AM
  4. Hermetic reciprocating versus hermetic scroll
    By Cofreth in forum Technical Discussions
    Replies: 26
    Last Post: 19-11-2005, 06:29 PM
  5. Hermetic analyzer
    By Mickvee in forum Tools and Calculators
    Replies: 2
    Last Post: 16-04-2005, 10:20 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •