    Compressor wiring issues.....



    Firstly as this is my first post i'd like to say hello!

    I have a bit of a problem or possably just a miss understanding.
    I'm currently in the process of designing my first compressor control panel and have come across some conflicting information. The compressor is made by Frascold and i will be wiring it star delta. As i'm relativly new to the refrigeration thing so i got in touch with Frascold to obtain some info. They sent me through full details with wiring diagrams. This is where the confusion began.
    There star delta wiring diagram had 1 fuse protecting the circuit rated at 1.3 x LRA. Now my LRA is 106A which means the fuses and cable would have to be rated at 137.8A. Is this correct? Also they have no motor protection after the main contactor????
    I am sligtly confused and i need of advice i have scoured the internet for info but have drawn a blank. Thanks in advance.



  2. #2
    Join Date
    Aug 2007
    Location
    Adelaide Australia
    Age
    70
    Posts
    562
    Rep Power
    24

    Re: Compressor wiring issues.....

    Hi Alistair
    I would definitely put an overload in. If you have a fuse of 1.3 x LRA by the time the fuse blows if something goes wrong the motor is stuffed. Also your fuses need to be motor start fuses or better still put in a motor circuit breaker.
    On the motor you should have FLA which is Full Load Amps and this is the max amps the motor can draw without doing damage to the windings.
    Set your overload at about 5% less then FLA. This in effect gives you about a 10 - 15% safety margin as most motors have about a 5 - 10% safety margin.
    Hope this helps.
    Paul

  3. #3
    Join Date
    May 2007
    Location
    Northants
    Posts
    290
    Rep Power
    17

    Re: Compressor wiring issues.....

    Hi

    I believe you wire to the RLA (run load Amps), FLA (full load amps) or max running load amps, not to locked rotary amps.
    It should also be fused and a overload fitted to and set at the FLA or RLA. LRA is for the service personell to be able to not that something has seized stationary, but the fuses and thermal overloads should protect the compressor and more importantly the cable for maximum normal running current.

    Hope that makes sense

    CB

  4. #4
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    394
    Rep Power
    18

    Re: Compressor wiring issues.....

    A lot of good advice for you there Alistair.

    So size your wires on FLC + your safety margins i.e. cable length and route. Set your overload at FLC until you have commissioned and then set all adjustable circuit protection at around + 10%/ 15% above actual LC assuming the actual doesnt exceed the RLC.

    The primary circuit protection should be set if possible to the FLC.

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Compressor wiring issues.....

    I think as stated above btu just to repeat...

    Fuses/MCB are there to protect the cables not the item of equipment.

    The motor should be protected by an overload device of some sort.

    Also, a warm welcome to the forum.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Alistairjbown's Avatar
    Alistairjbown Guest

    Re: Compressor wiring issues.....

    Thanks for the response guys. What you've said makes sense and is how i've wired star delta motors in the past. Which is a good thing because if i'd just took for granted the wiring diagrams i would of been in a right mess. If i can find the link to these drawings on the net i'll post it. Can't understand why they've got them so wrong.
    Anyway, thanks again and keep up the good work, this is a cracking site and i will be definatly posting again.

  7. #7
    Join Date
    Jan 2006
    Location
    UK
    Posts
    53
    Rep Power
    19

    Re: Compressor wiring issues.....

    Are you sure that this is a star/delta compressor? If it's an old Frascold unit it may wll be a star/delta but for the last few years, Frascold have only supplied part wind machines.

  8. #8
    Alistairjbown's Avatar
    Alistairjbown Guest

    Re: Compressor wiring issues.....

    The unit was manufactured in 1999.
    On the plate on the side of the unit it gives values for star/delta and delta only. I'm unfamiliar with how the part wind wiring would be shown on an infomation plate. Thanks for the heads up though.

  9. #9
    Join Date
    Jun 2007
    Location
    Cyprus
    Age
    73
    Posts
    252
    Rep Power
    17

    Re: Compressor wiring issues.....

    What HP is the compressor ? We could probably give you a fair guideline on cable sizing by knowing this.

  10. #10
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Compressor wiring issues.....

    We have Frascold (or Carrier) in star/delta running for more then 12 years now.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  11. #11
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Compressor wiring issues.....

    Quote Originally Posted by TRASH101 View Post
    So size your wires on FLC + your safety margins i.e. cable length and route. Set your overload at FLC until you have commissioned and then set all adjustable circuit protection at around + 10%/ 15% above actual LC assuming the actual doesnt exceed the RLC.
    Why change it afterwards. If you set FLC, then the motor is properly protected .
    If you commissioned this compressor in winter and set it back to the actual running amps in winter conditions, then you will become in trouble in summer or in other situations pulling temporarily more current.
    I always set it on FLA and nobody can say that this is fault. I then have some margin when it becomes hot or the motor pulls more AMPS after a defrost or a startup after a longer shutdown.
    It will still run with condensers partially clogged.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  12. #12
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    394
    Rep Power
    18

    Re: Compressor wiring issues.....

    Quote Originally Posted by Peter_1 View Post
    Why change it afterwards. If you set FLC, then the motor is properly protected .

    It is possible that 3 phase compressors (motors) can drop a phase (say on a contactor connection) and not exceed the flc sufficiently to trip local protection quick enough to prevent motor damage. This is of course comparative to the exact circumstances of operation and equipment selection. I would not say you are at fault by any means but I have saved compressors, pumps & fans from failing control gear.

  13. #13
    Join Date
    May 2006
    Location
    United Kingdom
    Age
    52
    Posts
    34
    Rep Power
    0

    Re: Compressor wiring issues.....

    LRA is normaly LOCKED ROTOR AMPS which is current drawn with motor being seized or stalled. I noramly pull the main contactor in with a normaly open contact on the star to lessen the arcing on the smaller star contactor.

  14. #14
    Join Date
    Oct 2007
    Location
    Colombo
    Age
    72
    Posts
    15
    Rep Power
    0

    Re: Compressor wiring issues.....

    I usually set it to FLA to protect my compressors.
    If You set it to LRA it trips at critical condition.

  15. #15
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: Compressor wiring issues.....

    Hello mate you need to put mcb or fuses to protect the line cables, just under its full rated load, and wire in a kriwan int69 control module for thermal overloads in your control circuit . also put in a electronic by pass valve from high side to low side , so when compressor starts it can equalise the pressure to ease on starting , other wise under heavey loads it won't get away and sit there humming . good luck

  16. #16
    Join Date
    Dec 2007
    Location
    malaysia
    Posts
    159
    Rep Power
    17

    Re: Compressor wiring issues.....

    yes, i use FLA to size the motor protection circuit.

    since our practices here for S/D is 2 ~ 4 times starting current, we use that to select the motor protector.

    next, i observe the implication of kA rating for the motor protection.

    yes, i use O/L too!

    i'll use a MCCB in this case for extra protection/s.

    i'll be careful on cable/wire sizing so that it will not becomes the 'fuse' for the motor circuit.

    probably, 5% voltage drop from end to end.

    yes, the cable type and its mounting method cannot be ignored, too. IEC has a lot to gather on this ...

    yes, XLPE/SWA/PVC would be good if outdoor use.
    don't forget about earthing and neutral ...

    equal potential is important ...

    mmmm ... still thinking what to say

  17. #17
    Join Date
    Dec 2007
    Location
    Volos, Greece
    Posts
    46
    Rep Power
    0

    Re: Compressor wiring issues.....

    I thing the best is to put a Circuit braker ThermoMagnetic Like telemecanique GV3 series
    and this can replace also the fuses and over load protection.

    After you need an overload protection to star-delta after the relays.

    Use the thermistor of motor and install a voltage monitor controll .

  18. #18
    Join Date
    Oct 2007
    Location
    india
    Age
    50
    Posts
    16
    Rep Power
    0

    Re: Compressor wiring issues.....

    thnks for kind information about compressors wiring

  19. #19
    Join Date
    Oct 2007
    Location
    india
    Age
    50
    Posts
    16
    Rep Power
    0

    Re: Compressor wiring issues.....

    why compressors get stucked during full load amps conditions?

  20. #20
    Join Date
    Oct 2007
    Location
    india
    Age
    50
    Posts
    16
    Rep Power
    0

    Re: Compressor wiring issues.....

    Why rotary compressors does not perform efficiently at high ambient conditions?

  21. #21
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Compressor wiring issues.....

    Quote Originally Posted by mehtag View Post
    why compressors get stucked during full load amps conditions?
    Please, elaborate this question!

  22. #22
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Compressor wiring issues.....

    Quote Originally Posted by mehtag View Post
    Why rotary compressors does not perform efficiently at high ambient conditions?
    In order to get any meaningful answer, you have to put this question in some context.

  23. #23
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: Compressor wiring issues.....

    Evening all,

    Like a lot of engineers i have never taken much notice about compressor internal wiring. Usually you just replace like for like and therefore wire the same.
    With the compressor windings, obviously direct online does what it says on the tin, but what about part wound and star delta. Can anyone give me a basic run down on the electrics or point me in the direction of a good web link that shows how it works

  24. #24
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Compressor wiring issues.....

    Hi Latte, have a look here...

    http://www.lmphotonics.com/m_start.htm

    Also, look around that site for additional information.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  25. #25
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: Compressor wiring issues.....

    Thanks for the link Brian, Nice piece of bedtime reading. Did try to add a rep point but ive got to spread it around a bit first

  26. #26
    Join Date
    Oct 2006
    Location
    Bucks, U.K.
    Age
    71
    Posts
    604
    Rep Power
    18

    Re: Compressor wiring issues.....

    Hi Guys,
    Although this thread is almost a year old and has been resurrected, it might be worth mentioning Soft Start units here.

    The technology has moved on such that soft starters are now much more versatile, clever and cost effective.

    If you are going to be building a S/D board from scratch, for a large compressor, adding up the cost of x3 contactors, overload, timer, phase rotation/loss/under over voltage module as a minimum, you are probably at least up to 2/3 of the cost of a soft start.

    When you then add the cost of labour to physically wire the unit up and all the ancillaries if you're doing a half decent job, you will certainly come out on top with the soft start.

    The added benefits of the soft start include less mechanical stresses on the compressor whilst starting, much closer overload protection, I2T thermal computation of winding status and protection, phase loss, ability to use motor winding protection thermistors, power monitoring, running times etc.

    Much easier wiring!.

    Alternatively, go the whole hog and use a VSD.

  27. #27
    sharafeddin's Avatar
    sharafeddin Guest

    Re: Compressor wiring issues.....

    what is the normal operation of start delta connection

  28. #28
    Join Date
    Feb 2008
    Location
    Surrey
    Age
    67
    Posts
    17
    Rep Power
    0

    Re: Compressor wiring issues.....

    In star delta operation the 3 windings of a 3 phase motor would be first connected in a star arrangement with the 3 phases going onto the ends of the windings and the other ends connected together to form the star.
    This reduces the voltage across the windings by root 3 of the phase to phase voltage so starting current is reduced. After it starts to run up to speed the connection quickly change to the delta arrangement which puts a phase on each end of the windings so you have full voltage across the windings. This is all done with 3 contactors and a timer.
    Something like that anyway

  29. #29
    Join Date
    Jul 2008
    Location
    UK
    Age
    60
    Posts
    94
    Rep Power
    16

    Re: Compressor wiring issues.....

    Try this link, some useful info. http://courses.ee.sun.ac.za/Elektrie...Star-Delta.pdf
    Note that the overload is in the main contactor leg. Current measured on a phase at either delta or main is at 58%, therefore overload setting must take this into account. An overload set at 100A would actually relate to 172A approx.

Similar Threads

  1. Carrier 30GX control issues
    By whoopy-do in forum Trouble Shooting
    Replies: 6
    Last Post: 03-11-2007, 12:05 AM
  2. Blast freezer related issues ~~
    By spiderman in forum Fundamentals
    Replies: 5
    Last Post: 24-05-2007, 07:59 AM
  3. Ref Net issues
    By A/C student in forum Air Conditioning
    Replies: 12
    Last Post: 20-08-2006, 02:06 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •