    Re: 404a high pressure?

    SPECIFICATIONS
    • CFM 180/200
    • Voltage 115 AC
    • Hertz 50/60 cycle
    • Amps 0.6/0.55
    • Max. air pressure 0.48" H20
    • Noise level 52/55 dBa
    • Ball Bearings
    • Speed 2650/2950 RPM
    • 5 Blade
    • Fan blade diameter 5-5/8"
    • Size 6-3/4" x 6" x 2"




  2. #2
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: 404a high pressure?

    Dare we assume that the refrigerant enters the top of the coil and exits the bottom?

  3. #3
    Join Date
    Aug 2007
    Location
    racine, wi
    Age
    68
    Posts
    135
    Rep Power
    17

    Re: 404a high pressure?

    Quote Originally Posted by Gary View Post
    Dare we assume that the refrigerant enters the top of the coil and exits the bottom?

    ummmm,, nope

    i checked it again this morning,, here are the readings,,,

    ambient 84f
    box temp 46f
    cond air in 73f
    cond air out 93f
    evap air in 53f
    evap air out 41f
    suction line at bulb 48f
    liquid line at receiver 100f
    45/280

    the superheat is still really high at 37f and the subcooling is close at 12f, so i backed out the txv 2 full turns ccw. after about 20 mins the new readings are,,,

    cond in 72f
    cond out 96f
    evap in 56f
    evap out 44f
    suction at bulb 49f
    liquid line at receiver 101f
    50/270
    superheat at 33f
    subcooling at 9f

    i wasnt aware that it made a difference where the refrigerant entered the coil. i dont recall ever learning that part. when i set it up,, i figured it was better to have the liquid enter the bottom and exit the top to help insure that only vapor would be returning to the compressor.

    anyhow,, its time to head up to sheboygan to visit my gf's family (fun fun).

  4. #4
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: 404a high pressure?

    Quote Originally Posted by flyboy3b View Post
    i wasnt aware that it made a difference where the refrigerant entered the coil. i dont recall ever learning that part. when i set it up,, i figured it was better to have the liquid enter the bottom and exit the top to help insure that only vapor would be returning to the compressor.
    It makes a BIG difference. Feeding the coil bottom up reduces heat transfer and traps oil in the evaporator. The oil coats the inside of the tubes, insulating them... and the compressor is deprived of lubrication.

    You need to reverse the lines. Technically, the refrigerant should enter the coil at the top of the leaving air side and exit the bottom on the entering air side (counterflow)... then the suction line should dip down (to trap oil)... then up to the top (to prevent liquid from returning to the compressor)... then down to the compressor.

    And while you have it apart, check the TXV inlet screen to see if it has collected any trash.
    Last edited by Gary; 23-12-2007 at 07:06 PM.

  5. #5
    Join Date
    Aug 2007
    Location
    racine, wi
    Age
    68
    Posts
    135
    Rep Power
    17

    Re: 404a high pressure?

    Quote Originally Posted by Gary View Post

    You need to reverse the lines. Technically, the refrigerant should enter the coil at the top of the leaving air side and exit the bottom on the entering air side (counterflow)...
    ill try to do that on tuesday morning. im not sure if ill be able to flip it around to get the orientation right. time will tell

  6. #6
    Join Date
    Aug 2007
    Location
    racine, wi
    Age
    68
    Posts
    135
    Rep Power
    17

    Re: 404a high pressure?

    ok,, i got it switched around. i was not able to get the counterflow right though. it enters the incoming side and exits the center. and let me tell you,, it was a real bugger getting in there to sweat those joints. ill be very happy if it doesnt leak.

    before i pumped it down,, i did find a small leak from an access fitting which i tightened. i believe that was part of the problem initially, but we will see.

    anyhow,,, i added some new 404a liquid and brought the pressures up to 50/250. at that point the liquid line at the receiver was 89f which gives me a subcooling of 15f. the txv was frosted and the unit sounded normal.

    condenser air in 70f
    cond air out 85f
    evap air in 59f
    evap air out 50f
    suc line at bulb 49f and dropping.

    it took me a couple hours to do the work,, and the box warmed up,, so ill check it later tonight and see how the superheat looks.

    the txv screen was clean

  7. #7
    Join Date
    Apr 2007
    Location
    EGYPT
    Age
    68
    Posts
    5
    Rep Power
    0

    Re: 404a high pressure?

    what prefer for lubrication 404a mineral or synthetic oil systems

  8. #8
    Join Date
    Aug 2007
    Location
    racine, wi
    Age
    68
    Posts
    135
    Rep Power
    17

    Re: 404a high pressure?

    Quote Originally Posted by m3ae2002 View Post
    what prefer for lubrication 404a mineral or synthetic oil systems
    honestly,, i couldnt tell you. this unit came with oil. i would check with the manufacturer of that particular compressor or go to dupont.com and look there.

  9. #9
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: 404a high pressure?

    The numbers aren't making any sense. If the coil is frozen then the suction line should also be frozen and the temperature of the air leaving the coil should be at or below freezing. Instead, the leaving air is 47F and the suction line is 49F.

    When you say the coil is frosted, exactly what part of the coil are you looking at?
    Last edited by Gary; 26-12-2007 at 05:34 PM.

  10. #10
    Join Date
    Aug 2007
    Location
    racine, wi
    Age
    68
    Posts
    135
    Rep Power
    17

    Re: 404a high pressure?

    Quote Originally Posted by Gary View Post
    When you say the coil is frosted, exactly what part of the coil are you looking at?
    i can see the center part of the coil through the fan while its running. in order to see the whole coil,, i have to remove the cover plate on the right side.

    ill try to get some more pics tomorrow morning

  11. #11
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: 404a high pressure?

    I'm thinking we need more pictures of the coil and TXV with the insulation and covers removed so we can see how it is all assembled. There is something very wrong here.

    Do you have any specs on that TXV?
    Last edited by Gary; 26-12-2007 at 05:41 PM.

  12. #12
    Join Date
    Aug 2007
    Location
    racine, wi
    Age
    68
    Posts
    135
    Rep Power
    17

    Re: 404a high pressure?

    Quote Originally Posted by Gary View Post
    I'm thinking we need more pictures of the coil and TXV with the insulation and covers removed so we can see how it is all assembled. There is something very wrong here.

    Do you have any specs on that TXV?

    here is the link for some new pics,,

    http://wavespub.com/evapcoil.html

    now dont laugh at my crappy cuts,,, i had to change this whole thing around after i installed it and its 2 1/2 inches thick. i plan on trimming it out after i get it running right.

    here is the link to the txv,,

    http://www.parker.com/cig/catalogs/C...ion5Parker.pdf

    the model # is C-A-SZ

    i have to run some errands so ill finish this post in an hour or two

  13. #13
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: 404a high pressure?

    Can you remove the sheet metal so that we can see the end of the coil?

    The "A" says this is not a 1/4 ton valve, it is a 1 ton valve.

    The "Z" means it is for a freezer, not a cooler.

    The correct valve would be C-AA-SW

    And here's the really bad news:

    Being oversized and having a low temp (freezer) bulb charge, it should be running wide open and flooding the compressor. Instead the coil is not getting enough refrigerant. Either the TXV is severely restricted or the coil is severely restricted.
    Last edited by Gary; 28-12-2007 at 06:35 PM.

  14. #14
    Join Date
    Aug 2007
    Location
    racine, wi
    Age
    68
    Posts
    135
    Rep Power
    17

    Re: 404a high pressure?

    where did you get that information???

    i read that pdf, and it looks like its a 1/4 to 1 ton txv. where did you look up the "z"?

  15. #15
    Join Date
    Aug 2007
    Location
    racine, wi
    Age
    68
    Posts
    135
    Rep Power
    17

    Re: 404a high pressure?

    nevermind,, i found it further down the page,, ill have to check my local suppliers to see if they have a txv thats applicable.

  16. #16
    Join Date
    Aug 2007
    Location
    racine, wi
    Age
    68
    Posts
    135
    Rep Power
    17

    Re: 404a high pressure?

    the new txv is coming in on monday,

    thanks again gary

  17. #17
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: 404a high pressure?

    When you get the new valve, do not adjust it unless the superheat is low. High superheat is to be expected until the return air temp is down to 40F or less.

  18. #18
    Join Date
    Aug 2007
    Location
    racine, wi
    Age
    68
    Posts
    135
    Rep Power
    17

    Re: 404a high pressure?

    gotcha,,,

    depending on what time ups shows up,, it may end up being tuesday before i can install it. dec 31st is a busy day for us

  19. #19
    Join Date
    Dec 2007
    Location
    lebanon
    Posts
    130
    Rep Power
    17

    Re: 404a high pressure?

    hi flyboy
    it seems that you wont giveup thats good
    is your box insulated well
    did you fit a door switch to stop fan when its open
    from your readings ithink that you need more capacity
    i use to deal with that kind of boxes and my readings were
    30 psi at the suction and275 dicharge using 404

  20. #20
    Join Date
    Aug 2007
    Location
    racine, wi
    Age
    68
    Posts
    135
    Rep Power
    17

    Re: 404a high pressure?

    Quote Originally Posted by tonyelian View Post
    hi flyboy
    it seems that you wont giveup thats good
    is your box insulated well
    did you fit a door switch to stop fan when its open
    from your readings ithink that you need more capacity
    i use to deal with that kind of boxes and my readings were
    30 psi at the suction and275 dicharge using 404

    the doors could seal a little better,, but its ok,, and the box is very well insulated for such a small unit. i should be able to cool 4 boxes this size with this condensing unit. if you read back in the thread,, you will see that its very small. but i appreciate the ideas. 30 psig on the suction side sounds kinda low. my target temp is low 40's.

    certainly getting the right txv in there will help. which , by the way,, never came in on monday. it should be in tomorrow and hopefully ill be able to install it right away.

    thanks,
    mike

  21. #21
    joshman1's Avatar
    joshman1 Guest

    Re: 404a high pressure?

    I think your system is not sized up properly, your condensing unit is struggling mate, good luck.

  22. #22
    Join Date
    Dec 2007
    Location
    lebanon
    Posts
    130
    Rep Power
    17

    Re: 404a high pressure?

    hi fly boy
    sorry i did not see your site before my reply
    so your comp e2145gk aspera is a lbp application&it gives you about2200btu at23 degree fah or -5 centigrade evaporation temp
    so i think your txv is over sized&here what i am thinking you can fit a cap-tube 2.32meter&0.044 inche int diameter why?
    you can remove the receiver so you can move your condensor back for more vent
    you can fit your thermostat with diff direct to evaporator pipe letting the fan blows cold air
    that thermostat will cycle the fan so your comp take a little break
    fit another room thermostat
    i hope that will help

  23. #23
    Join Date
    Aug 2007
    Location
    racine, wi
    Age
    68
    Posts
    135
    Rep Power
    17

    Re: 404a high pressure?

    Quote Originally Posted by tonyelian View Post
    so i think your txv is over sized&here what i am thinking you can fit a cap-tube 2.32meter&0.044 inche int diameter why?
    thanks for the advice,, however,, i just got the new txv in and i installed it this morning. ill know more tomorrow morning when i take some more readings. until then,,,,, this is what i got.

    ambient 68f
    box (wine) 52f
    liquid line at receiver 97f
    suction line at txv bulb 30f (although this reading was bouncing around pretty good. from 22f to52f)
    suction line at compressor 44f
    evap air in 51f
    evap air out 43f (and dropping)
    cond air in 67f
    cond air out 85f
    pressures at 45 and 285 psig

    subcooling 285 psig=113f-97f=16f
    superheat 30f-10f (45psig)=20f

    gary,, i forgot to get the picture of the evap coil,, ill try to get it in the morning. this cooler is still balancing out and i havent adjusted the txv. when i first fired it up,,, the suction pressure was at 65 psig. and it slowly dropped. the txv that i ordered was a C-A-SW, but the one they shipped was a C-A-RW. i couldnt find the "r" even listed on that pdf file,, but grainger assured me that it was the same application. (they didnt have the C-AA-SW)

    anyhow,, until tomorrow am,
    thanks again
    mike

  24. #24
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: 404a high pressure?

    Is it possible that some of the air is going around the coil instead of through the coil?

    The "A" orifice in the TXV is rated 1 ton nominal, but will control down to 1/4 ton. You are currently running closer to 1/8 ton. The "AA" orifice is rated 1/2 ton nominal, but will control down to 1/8 ton. That's why the TXV is hunting (temps/pressures bouncing). Any air that bypasses the coil will reduce the tonnage and add greatly to this effect.

    The TXV bulb should be mounted as close to the coil as possible, and should be heavily insulated (real insulation, not rags). Get a roll of closed cell foam insulation tape.
    Last edited by Gary; 03-01-2008 at 10:40 PM.

  25. #25
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: 404a high pressure?

    Hmmm... Is this a trouble shooting thread or a training thread.

  26. #26
    Join Date
    Aug 2007
    Location
    racine, wi
    Age
    68
    Posts
    135
    Rep Power
    17

    Re: 404a high pressure?

    Quote Originally Posted by nike123 View Post
    Did you guys/girls noticed, that this troubleshooting thread is longest in RE archive. First next to this has "only" 77 posts!

    its only that long because i am too dense to get it right the first time.


    Quote Originally Posted by Gary View Post
    Is it possible that some of the air is going around the coil instead of through the coil?
    sure,, its possible,, but how much air would have to bypass the coil before it became significant in such a small box. and even at that,, all the air going through the coil originated from the inside of the cooler, so eventually it will all get cold.

    now that were done with all these holidays,, ill have some time to go back inside and tighten the whole unit up. remember,, when i originally installed this thing,, it was a 134a cap tube system. so i had some cutting to do to get it where it is now. i just dont want to get too much time in finishing it until im sure its running right.

    Quote Originally Posted by Gary View Post
    Hmmm... Is this a trouble shooting thread or a training thread.
    i think i feel an invoice coming

  27. #27
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: 404a high pressure?

    Quote Originally Posted by flyboy3b View Post
    its only that long because i am too dense to get it right the first time.
    There's nothing like doing things over to drive the lesson home.


    Quote Originally Posted by flyboy3b View Post
    sure,, its possible,, but how much air would have to bypass the coil before it became significant in such a small box. and even at that,, all the air going through the coil originated from the inside of the cooler, so eventually it will all get cold.
    The more air goes through the coil, the higher the heat transfer, the higher the efficiency, and the less likely the TXV is to hunt.

    Quote Originally Posted by flyboy3b View Post
    now that were done with all these holidays,, ill have some time to go back inside and tighten the whole unit up. remember,, when i originally installed this thing,, it was a 134a cap tube system. so i had some cutting to do to get it where it is now. i just dont want to get too much time in finishing it until im sure its running right.
    Insulation, especially on the TXV bulb, is part of getting it running right.

  28. #28
    Join Date
    Aug 2007
    Location
    racine, wi
    Age
    68
    Posts
    135
    Rep Power
    17

    Re: 404a high pressure?

    and yet once again,,, more readings
    this morning 6am,,,
    ambient 76f
    box 47f
    suction at bulb 40f
    liquid at receiver 101f
    cond air in 73f
    cond air out 84f
    evap air in 52f
    evap air out 45f
    pressures at 55/290 psig
    subcooling of 14f and superheat of 21f

    i pulled the top apart and added some insulation and generally tightened things up and then i let it sit for a couple of hours. here are the readings i just took,,,

    suction line at bulb 30f
    liquid line at receiver 96f
    cond air in 67f
    cond air out 88f
    evap air in 45f
    evap air out 38f
    pressures at 45/285 psig
    subcooling of 16f and superheat of 20f
    the suction line was starting to frost back to the compressor and the temperature of the suction line at the compressor was 50f.

    here are some variables to take into consideration,,, when i take the evaporator air in temp,, it can vary by how far i push the probe in. and being thats its a wire probe (not solid) i cant be sure that its not touching something inside and affecting the temperature. the same thing is true with the condenser air in temp. moving the probe a few inches will make a difference of +-12f. so i try to take these temps the same way each time to keep them relative to each other. the other thing is,, i think thermostat may be shutting off too soon,, so i adjusted it down,, and moved the probe further into the return air duct. now it should run longer and give me some more stable readings.

    i did take some more pictures but it will be later today before i can post them. oh,, and i still need to tape the txv bulb.

  29. #29
    Join Date
    Aug 2007
    Location
    racine, wi
    Age
    68
    Posts
    135
    Rep Power
    17

    Re: 404a high pressure?

    heres the link for the new pics,, you cant really see much and remember,, when its back together,, the coil is tight against the left side of the box,, so no air is getting by.
    http://wavespub.com/evapcoil1.html

    for what its worth,, it seems to be doing much better today.

  30. #30
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: 404a high pressure?

    I think we can move the thermostat sensor inside the box, mounting it at the entrance to the return air duct... and we can take the evap air in readings there, also.

    The numbers are looking much better with the new TXV.

    There is good airflow through the evap... the weakest link seems to be the coil itself.

  31. #31
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: 404a high pressure?

    Is the TXV still hunting?

  32. #32
    Join Date
    Aug 2007
    Location
    racine, wi
    Age
    68
    Posts
    135
    Rep Power
    17

    Re: 404a high pressure?

    i havent looked at it since this morning,, but it seemed to be stabilizing. there was a steady (light) frost on the suction line and the evap air out was dropping nicely. i will hook up my datalogger and see just how often the thermostat is shutting it down.

  33. #33
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: 404a high pressure?

    Looking at the pic, that appears to be an upside down condenser coil... lol

    Actually, its a good thing that you have it upside down or the subcooling loop would trap oil.
    Last edited by Gary; 04-01-2008 at 10:02 PM.

  34. #34
    Join Date
    Dec 2007
    Location
    lebanon
    Posts
    130
    Rep Power
    17

    Re: 404a high pressure?

    hi fly boy
    it look like a condensor not evap you have fin spacing problem freezing up anyway waiting for your latest readings
    best regards for you&gary

  35. #35
    Join Date
    Aug 2007
    Location
    racine, wi
    Age
    68
    Posts
    135
    Rep Power
    17

    Re: 404a high pressure?

    actually,, its a radiator from a 65 rambler classic 550

  36. #36
    Join Date
    Aug 2007
    Location
    racine, wi
    Age
    68
    Posts
    135
    Rep Power
    17

    Re: 404a high pressure?

    its warm(45f) and rainy here in wisconsin and here are the latest readings...

    ambient 80f
    box 41f
    evap air in (from the intake) 38f
    evap air out 41f
    cond air in 74f
    cond air out 91f
    suction line at bulb 30f
    liquid line at receiver 105f
    pressures at 45 and 295 psig

    this leaves me with a superheat of 19f and subcooling of 10f. the txv was fairly stable but the pressure seems low to me so i turned the txv 1 full turn ccw. also,, the coil was starting to frost up. i shut it down for about 15 mins and restarted. after about 1/2 hour the pressures were at 50 and 300 psig and the superheat had dropped to 17f.

    after restarting,, the txv was hunting a little (suction line temps between 30f and 35f over a cycle of about 30 seconds, but that was starting to smooth out when i left it. i think im getting close here and i am pretty certain there are no leaks in the system.

    of course,, im waiting for gary's intuitive insight and profoundly sage advice before i lock this cooler down.

    thanks,
    mike

  37. #37
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: 404a high pressure?

    Quote Originally Posted by flyboy3b View Post
    evap air in (from the intake) 38f
    Judging from the previous evap delta-T's, the evap air in (at the coil) would be about 48F, so we can estimate that the return duct is gaining at least 10F (48 - 38 = 10F gain). That's a HUGE gain.

    You really need to do something about the return air duct. It needs to be leak-free and very heavily insulated. The temp at each end of that duct should be nearly identical.

    Possibly the heat gain is coming from the evaporator compartment itself, so the compartment should be leak-free and heavily insulated also.

    A lot of heat is getting in somewhere.
    Last edited by Gary; 06-01-2008 at 06:45 PM.

  38. #38
    Join Date
    Aug 2007
    Location
    racine, wi
    Age
    68
    Posts
    135
    Rep Power
    17

    Re: 404a high pressure?

    Quote Originally Posted by Gary View Post

    You really need to do something about the return air duct. It needs to be leak-free and very heavily insulated. The temp at each end of that duct should be nearly identical.
    i was thinking it might be better to just eliminate the return duct and enlarge the evaporator chamber. (basically just hang the coil in the cooler space,,, so to speak). that would eliminate any chance of other air leaking in. give me a couple days to think about some other options,, and to let the cooler settle down,, and ill repost the current results.
    one thing i notice,, when im taking the evap air out temp,,, is how fast that temperature rises when i open the door. there should be no negative or positive pressure difference inside the box, but it sure seems to draw outside air in fast when i open the door.

    anyhow,, till next time,
    thanks,
    mike

  39. #39
    Join Date
    Feb 2005
    Location
    Hong Kong
    Posts
    190
    Rep Power
    20

    Re: 404a high pressure?

    Hi Gary, before Nike 123 posted his interesting observation, I was just thinking to myself, the tremendous job you had done in guiding FlyBoy through this project thus far.

    However, the downside ... I fear it will impact your book sales !!

    Why? because you have (kindly) divulged most of your knacks and techniques over the course of this 77+ post thread. . Many of the newbies may have all they need ( if they are sharp on the uptake!)

    kind regards
    T-P
    Remember what Augustus once said:
    "festina lente" - make haste, slowly!

  40. #40
    Join Date
    Aug 2007
    Location
    racine, wi
    Age
    68
    Posts
    135
    Rep Power
    17

    Re: 404a high pressure?

    Quote Originally Posted by thermo prince View Post
    Hi Gary, before Nike 123 posted his interesting observation, I was just thinking to myself, the tremendous job you had done in guiding FlyBoy through this project thus far.

    However, the downside ... I fear it will impact your book sales !!
    and thats exactly the reason why i bought 3 of them.

    Quote Originally Posted by thermo prince View Post

    Why? because you have (kindly) divulged most of your knacks and techniques over the course of this 77+ post thread. . Many of the newbies may have all they need ( if they are sharp on the uptake!)

    kind regards
    T-P
    i cant speak for everyone,, but i, myself,, find that the smarter i get,, the dumber i feel. i already own a few troubleshooting manuals. it seems that everyone has a slightly different method. by learning these different methods i hope to consolidate these methods into something that works for me. i would reccommend to anyone who is new to the trades like myself (and possibly some of the veterans who never bothered to learn the theory) to read as much literature and training as possible to gain a better understanding of the whole process. there are so many variables to consider and so many times we see techs who merely swap out parts rather than diagnose.

    again,, many thanks to you gary for your time and patience,
    mike

  41. #41
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: 404a high pressure?

    Quote Originally Posted by thermo prince View Post
    Hi Gary, before Nike 123 posted his interesting observation, I was just thinking to myself, the tremendous job you had done in guiding FlyBoy through this project thus far.

    However, the downside ... I fear it will impact your book sales !!

    Why? because you have (kindly) divulged most of your knacks and techniques over the course of this 77+ post thread. . Many of the newbies may have all they need ( if they are sharp on the uptake!)

    kind regards
    T-P
    I would like to think that this thread has been helpful to many people, but it is in fact just a small taste of what's in my books.

  42. #42
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Exclamation Re: 404a high pressure?

    Just to point out, my previous observation has nothing to do with content of this thread. It is just observation that this is longest thread of this forum.

  43. #43
    Join Date
    Feb 2005
    Location
    Hong Kong
    Posts
    190
    Rep Power
    20

    Re: 404a high pressure?

    It's all good - a very pleasant and polite thread which made rivetting reading! Better than primetime TV here even !

    Sorry to jump into your posts if it's not entirely concluded yet but it appears to be getting close now.

    Good luck with rest of it FlyBoy.
    And Gary I must review your material soon to see if and which parts may be helpful in Transport HVACR training programmes. Of course the fundamentals are universal.
    Can you tell from sales records if any Transport people in USA have purchased yr books previously?

    best regards
    T-P
    Remember what Augustus once said:
    "festina lente" - make haste, slowly!

  44. #44
    Join Date
    Aug 2007
    Location
    racine, wi
    Age
    68
    Posts
    135
    Rep Power
    17

    Re: 404a high pressure?

    Quote Originally Posted by thermo prince View Post

    Sorry to jump into your posts if it's not entirely concluded yet but it appears to be getting close now.
    youre not intruding at all. isnt that what this forum is all about?

  45. #45
    Join Date
    Feb 2007
    Location
    solihull
    Posts
    53
    Rep Power
    18

    Re: 404a high pressure?

    IF I COULD I WOULD VOTE FOR GRAY USA PRESIDENT

    and i am gone buy a set off his books ,

  46. #46
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: 404a high pressure?

    Quote Originally Posted by knight rider View Post
    IF I COULD I WOULD VOTE FOR GRAY USA PRESIDENT
    Hmmm... on day one I would issue a presidential pardon to all non-violent drug offenders.

    On day two I would pardon all tax evaders.

    On day three I would be assassinated... LOL

  47. #47
    Join Date
    Aug 2007
    Location
    racine, wi
    Age
    68
    Posts
    135
    Rep Power
    17

    Re: 404a high pressure?

    Quote Originally Posted by Gary View Post
    Hmmm... on day one I would issue a presidential pardon to all non-violent drug offenders.
    its street language for homegrown pot

  48. #48
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: 404a high pressure?

    Quote Originally Posted by flyboy3b View Post
    its street language for homegrown pot
    I never use the stuff... and I rarely use alcohol. But if others want to use all of the above, I have no right to stop them. I have a simple philosophy: If you want to smack yourself in the head... it's your head.

    If you want to smack someone else's head, that's a different story. The legitimate basis of government is collective self defense.

  49. #49
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    394
    Rep Power
    18

    Re: 404a high pressure?

    A flawed philosophy I`m afraid

    someone may get smacked in the head and then blame you.

    someone might pretend to get smacked in the head and blame you.

    you might try and smack yourself in the head miss and hit the person beside you.

    But in essence a really sound philosophy

  50. #50
    Join Date
    Aug 2007
    Location
    racine, wi
    Age
    68
    Posts
    135
    Rep Power
    17

    Re: 404a high pressure?

    Quote Originally Posted by Gary View Post
    I have a simple philosophy: If you want to smack yourself in the head... it's your head.
    i am enjoying my new hobby of home distillation and it pleases me no end that i can make something that tastes better and is cleaner than what i can buy in the store. everything in moderation i guess. anyhow,, i have a different forum for home distillation so ill get back to things at hand...

    ambient 75f
    box 44f
    cond air in 75f
    cond air out 91f
    evap air in 53
    evap air out 41f
    suction at bulb 32f
    suction at compressor 53f
    liquid at receiver 104f
    pressures at 60/295 psig

    this leaves me with 11f superheat and 12f subcooling. the txv was wandering between 29f and 32f bulb temperature and seemed pretty normal. the unit may be a bit overcharged.

    at this point, i think, once i get the evaporator air in temperature down about 6 or 7 degrees i will need to increase the superheat a couple of turns which should lower the pressure a tad and bring the evaporator air out temp down 1 or 2 degrees. otherwise,, we are in the ballpark.

    gary,, once again,, i thank you for your time and patience. and of course to everyone else who shared thier ideas. i have started to read the manuals i got from you and im waiting for the next time i can try out the TECH system (which may be sooner than later, i had my manitowoc ice machine apart this morning and it was flashing an error code that the harvest cycle had exceeded 3 1/2 minutes 3 times) i reset the machine and watched it through 3 cycles with no problem).

    itll be a bit before i can tear that wine cooler apart to redo the air intake,, but ill keep you posted as to the results.

    to summarize,,, (and please correct me if im wrong)...

    the original question was "how do i know when i have the charge right in a medium temp home built system"

    the answer is,,,

    add refrigerant until the subcooling reaches around 15f.
    keep the superheat between 20f and 30f
    keep the delta t for the condenser to less than 30f
    keep the delta t for the evaporator less than 20f
    assuming that everything else seems normal, the charge is correct.

Page 3 of 5 FirstFirst 12345 LastLast

Similar Threads

  1. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  2. fun quiz
    By Brian23 in forum New to RE
    Replies: 6
    Last Post: 02-10-2007, 10:18 PM
  3. High Side Pressure is ...
    By SULTAN in forum Trouble Shooting
    Replies: 5
    Last Post: 14-08-2007, 12:53 PM
  4. Replies: 6
    Last Post: 18-11-2005, 04:30 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •