    Run 4 cassettes off one controller



    Hi Guys,

    Just installing 4 mitsubitshi cassettes and need to hard wire all to one controller.
    Never worked on Mitsi's before so any tips or is it just daisy chain the units.

    Thanks.



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Run 4 cassettes off one controller

    You don't say which type of controller but this may help

  3. #3
    Join Date
    Sep 2007
    Location
    England
    Posts
    53
    Rep Power
    17

    Re: Run 4 cassettes off one controller

    Hi pal

    From your controller wire to unit one (master 0) then follow on 0-1,1-2,2-3,3-4.

    So you will have two wires inside the unit. For example you'll have wire one coming into power/signel unit one then have wire two going out of unit one conetted and going to unit two and so on.

    Make sure you set your controller to master mode.

    Hope it helps

  4. #4
    Join Date
    Dec 2005
    Location
    Cheshire
    Age
    39
    Posts
    264
    Rep Power
    21

    Re: Run 4 cassettes off one controller

    Last time I did 4 it was: Daisy chain from the master and then set dip switches on the 3 slave outdoors, SW1 I think??? Master=0 (factory)

  5. #5
    Join Date
    Jul 2005
    Location
    Ireland
    Age
    56
    Posts
    164
    Rep Power
    19

    Re: Run 4 cassettes off one controller

    Hi Aza

    Again I havn;t done this in a long time . But the guys are correct normal daisy chain in on the remote control terminals. Then set up the dip sw's on the outdoors. there is one bank of switch's on the outdoor PCB with 6 sw's, ignore switch one and two and use the remaining
    Sw's in a binary configuration to set the outdoor addresses. Im sure the info will be in the install manuals.

    But from memory

    UNIT 1 SW1 DO NOT TOUCH
    UNIT 2 SW1 DIP SWITCH 3 ON
    UNIT 3 SW1 DIP SWITCH 4 ON
    UNIT 4 SWI DIP SWITCH 3 AND 4 ON

    Power all units on then they should auto address after that.

    Hope this helps

    T

Similar Threads

  1. Daikin Hard wired controller
    By marc5180 in forum Air Conditioning
    Replies: 16
    Last Post: 10-11-2007, 06:43 PM
  2. H0 on Mitsubishi Controller
    By Freecool in forum Air Conditioning
    Replies: 2
    Last Post: 29-09-2007, 07:24 PM
  3. Help with new electronic refrigerator controller !
    By EngiGal in forum New Technologies
    Replies: 17
    Last Post: 08-04-2006, 07:39 PM
  4. Controller wiring
    By Mickvee in forum Air Conditioning
    Replies: 2
    Last Post: 30-12-2005, 02:04 AM
  5. Fan Controller
    By Abe in forum Trouble Shooting
    Replies: 4
    Last Post: 12-01-2002, 02:21 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •