Anyone knows how to enter the test operation mode on a Daikin CVP (Convenipack) or Zeas?
I have tried to press the testbutton on the outdoorunit for 5 sek but no success.
:confused:
:confused:
Have you followed the instructions within the installation or service manual?
Does your system include a booster unit?
Here you go. https://manualzz.com/doc/901740/daik...service-manual
See page 71
I've checked both the service manual and installation manual. Maybe I have the wrong ones? The things I found about self test was with a controller. But I don't have one. I was more thinking how to start the test with the buttons on the outdoor unit.
I have some trouble with the cvp. It gives a warning of protection device. Sometimes. I have measured all three compressors and they are fine. I have changed both pressure sensors and thermistors. No success.
Yes it has one booster.
Page 71.
Section 5.6
Item 2.
Turn RUN switch to ON