Re: Is POE bad for R407C ?
On same site:
Lubricants
RS-45 is suitable for use with mineral, alkylbenzene & polyol ester lubricants. R134a, R407C & R410A should not be used with MO & AB oils.
http://www.refsols.com/RS-45_OEM.html
http://refrigerants.dupont.com/Suva/...suva407c.html#
Re: Is POE bad for R407C ?
Thanks for quick reply. Now I understood.
So, is R434A a good choice, rather than R407 when retrotifing from R22 ?
Re: Is POE bad for R407C ?
Quote:
Originally Posted by
Acrisoft
Thanks for quick reply. Now I understood.
So, is R434A a good choice, rather than R407 when retrotifing from R22 ?
For retrofitting, best choice, for air conditioning purpose, is still R407.
But, there is available some drop-ins. I personally don't have any experience with drop-ins.
Search this forum for drop-ins. There are some good posts about that subject.
http://www.refrigeration-engineer.co...php/t-661.html
http://www.refrigeration-engineer.co...hlight=drop-in
Re: Is POE bad for R407C ?
I work in ultra low. We use AB oil with 407C/ or 407 D. We use HPLC Grade Pentane as a sweeping agent to keep the Oil and Refrigerant from mixing.
Re: Is POE bad for R407C ?
Quote:
Originally Posted by
jcook1982
I work in ultra low. We use AB oil with 407C/ or 407 D. We use HPLC Grade Pentane as a sweeping agent to keep the Oil and Refrigerant from mixing.
Main reason for "refrigerant oil compatibility" is ability of refrigerant to mix with oil and carry oil back to compressor where it belongs.
So use of something to keep oil and refrigerant from mixing is stupid.
In your case, HPLC Grade Pentane is used to swept oil and carry oil back in compressor instead of R407 (because of his bad miscibility with AB oil).
Re: Is POE bad for R407C ?
Quote:
Originally Posted by
nike123
Main reason for "refrigerant oil compatibility" is ability of refrigerant to mix with oil and carry oil back to compressor where it belongs.
So use of something to keep oil and refrigerant from mixing is stupid.
In your case, HPLC Grade Pentane is used to swept oil and carry oil back in compressor instead of R407 (because of his bad miscibility with AB oil).
Why would you want oil to get into your evaporator? Keeping oil out of refrigerant will keep your evaporator from becoming oil logged or you cap tubes from getting clogged with wax in the oils. The sweeping agent keeps the oil flowing in a circuit dedicated to oil going back the compressor bringing a high level of sustainability to your compressor. :cool:
Re: Is POE bad for R407C ?
all depends on the context my. No need to get all demeaning about it NIke
Re: Is POE bad for R407C ?
Quote:
Originally Posted by
nike123
Main reason for "refrigerant oil compatibility" is ability of refrigerant to mix with oil and carry oil back to compressor where it belongs.
So use of something to keep oil and refrigerant from mixing is stupid.
In your case, HPLC Grade Pentane is used to swept oil and carry oil back in compressor instead of R407 (because of his bad miscibility with AB oil).
NIKE123,
Would HPLC Grade Pentane work with any type refrigerant and oils to help oil to come back to compressor?
Re: Is POE bad for R407C ?
Quote:
Originally Posted by
nike123
Dupont says here "[IMG]file:///C:/DOCUME%7E1/JCOOK%7E1.SEE/LOCALS%7E1/Temp/moz-screenshot.png[/IMG][IMG]file:///C:/DOCUME%7E1/JCOOK%7E1.SEE/LOCALS%7E1/Temp/moz-screenshot-1.png[/IMG]Q: What type lubricant should be
used with R-407C?
A: A high-quality POE (polyol ester) lubricant is
recommended. Always consult the compressor
or system OEM.":rolleyes:
Re: Is POE bad for R407C ?
Quote:
Originally Posted by
michaelm
NIKE123,
Would HPLC Grade Pentane work with any type refrigerant and oils to help oil to come back to compressor?
It's Always important to refer back to what the Manufacturer of the product recommends. Go back to the compressor or system manufacturer to get the data!!:)
Re: Is POE bad for R407C ?
Quote:
Originally Posted by
nike123
We have been using R407D in our systems since the early 90's with no problems. R407 D is 70% R134A and 30% R410A. R407C is 52% R134A and 48% R410A. The oil we use is AB very similar to Zerol 150.
We have had no problems with this mix RSL web site has no basis for these statements besides the fact that Dupont says what is recommended. Dupont also says that you should refer to compressor manufacturer or system manufacturer specifications on oil...:o