When setting up switches is there is there a method for working out the settings including differential. At present I normally set up H.P. at 300 LP at 10. should this alter depending on the gas.
Regards to the wise ones.
Bernard
Bernard
HP/LP Settings should be different depending on gas.
Take R12/R409(FX56) Head pressure should be about 120psi therefore when the system was pressure/strength tested is was probably put upto 150psi max. A HP switch set at 350 would be useless because the system whould blow well before then. Also if these gases were used in a low temp application (Unlikely i know) but the system would stop because the suction pressure would be if anything in a vac.
R404 Head pressure should be about 240psi running so an HP at 350psi would be higher than i would put it (Prob 325 at most)
R22 runs about 190-200 so 350psi also well excessive.
Let us know what kind of equipment and gases you are woking on and i am sure someone will post the OFFICIAL HP Guidelines.
Raymond
Raymond
Thankyou for your reply:
The one I am most concerned about is R407c.But what you say makes sence there must be a guide or % to set these switches above the hp running pressure.
Thankyou
Bernard
Sorry Bernard,
Got me on that one, never used the stuff yet & my HRP sliderule doesnt show it. If anyone has a list of HP switch settings or wants to put one together i would like to see it
regards
Raymond
One way of deciding on the settings is to work out the condensing temperature at maximum design ambient then add a small overshoot allowance.
The differential should be quite wide to reduce compressor cycling; remember everytime the compressor starts it pumps a bit of oil out, if it doesn't run for long enough then the oil doesn't return.
End result - dry compressor - bang :eek:
If there is a continual head pressure problem then it should be investigated and rectified.
Hello Brian,
Maximum design ambient, now there is a subject that could take up a lot of space within the forum.
Anyone out there know the head pressures of R407 & R410 & what the HPCO's should be.
Raymond
hi raymond,
there is no such thing,
what you said before is right for the uk.
over here, R22 works around 250 and more in the summer.
so the settings will be different.
I guess the setting depend on the working conditions.
chemi
The nearest thing to chapter and verse in the UK is BS EN 378, Part 2.
Look at section 5, tables 1 & 2. It give a methodology for determining the maximum allowable pressure (Ps) for the refrigerant of your choice.
This standard is harmonised to the PED and would, I suspect, qualify as Standard Engineering Practice for equipment below Category 1. (Outside the scope of the PED.
Pressure limiting devices are set at < 0.9 Ps if you have a relief valve or <1 Ps without.
Differential is not defined.
You can obtain a copy from BSI or main public libraries should have sets. BSI should give you a list of Libraries that carry complete sets (usually on Microfilm).
Hope this helps.
________
Mercury Monarch picture
For me it's simple: HP is there to protect the compressor. So max allowabale pressure found on the nameplate and subtract 1 bar safety for it, which will be mostly 24 bar. Dff mostly not settable.
LP: Cut in at somewhat lower then normal operating pressures en diff set so that machine stops before atmospheric pressure.
Otherwise, the 1 st day it becomes warm - like last days- all the same calls:'Hey, my compressor is going on-off real fast"
The problem becomes even bigger especially with a resettable HP. If it's a freezer, you can't be fast enough then to repair.
Absolute maximum setting of 90% mwp, but should be set with safety of plant as priority. Head pressures will vary dependent on ambient temp as well as gas type.
BS EN378 I believe defines maximum working pressure at different saturation points for the gas in use. I believe it is at a temp of 32 degrees on the low side, and for the high side, 55 degrees for an air cooled condenser and 43 degrees in the case of water cooled condensers. Saying that we usually check manufacturers data and go from there.
As Peter says we usually set LP so that it will cut just above atmospheric pressure, for instance if the system has to be pumped down etc as well as to protect the compressor.
James
Hi all,
Just a quick list of approxomate pressures in response to Bernards original post. Obviously these are approx & ambients could change.If i have worked these out wrong can someone let me know
Raymond
Gas Type, HP, LP@0coil, LP@-10 Coil, LP@-30 Coil.
R12, 118, 30, 17, 1" vac.
R134, 125, 28, 14 , 1" vac/
R22, 190, 58, 36, 9.,
R502, 215, 67, 36, 14.
FX10, 220, 68, 44 , 13,
FX56 125, 27, 15 , 1" vac,
R404 230 , 72 , 48, 14,
R407 220, 50, 32 , 13,
R410 320 , 100, 68, 24,
R507 240, 76 , 48 , 16,
those hp settings will have you going back resetting units all summer
cheers
richard
This is the information in BS EN 378
Hi All,
I meant to say these are approx RUNNING Pressures if the system is OK, Condenser Clean Ect. THESE ARE NOT settings for hp/lp switches
Raymond
I am thinking of a refrigeration system, here. One condition that I would pay attention to is to make sure the high pressure control is set at least 25 psig below the pressure relief valve of the system, for what I would hope is an obvious reason. :) I would guess that a 407C system would have a 425 psig relief valve on it, so I would set it no higher than 400 psig and no lower than 375 psig which is about 135 Deg F bubble point. Anything lower and you run the risk of tripping out during transient high load conditions such as after defrost on a hot day.
As far as the low pressure control setting goes, I am assuming you are talking about a pump down situation. If that is the case, you would use one setting for low temperature and a different setting for medium temperature.
Forgetting about pressures, I would set a low pressure control for a -20 deg F evaporator no higher than 10 deg F below the design evaporator temperature and no lower than 5 deg F below the design temperature. With 407C 2 psig would be a good setting which corresponds to a dew point of -30 deg F.
For medium temperature, +20 deg F application I would set the cutout at 25 to 28 psig (7 to 10 deg F). No point in pumping down a compressor lower than necessary.
Differential settings are best done per the application. Again, for pumpdown situations, you want to mitigate the short cycles. If you pump deeper than necessary, you will probably desire a higher cut-in pressure (or larger differential) than if you pump down the practical minimum amount. I would convert the air temperature into an evaporator pressure and make sure I don't have the cut-in pressure below my warmest acceptable air temperature. Let's say, maybe 40 deg F (65 psig) for medium temperature and 10 deg F (27 psig) for a freezer.
Nice Post Dan - we all should look at temperatures more than pressures as this is what we are trying to achieve - temperature control. :o
By the way - I must say that your photo does not look anything like the picture in my mind of you after reading your posts for so long. (A bit of a compliment ;) )
Frank
R407c -- Suction should be around 3 bar and discharge around 15 bar.Quote:
Originally Posted by rdocwra
NOt sure about R410, but I know it's a lot higher
Exactly so. Determine the proper temperature at which to trip the control, then get out the P/T chart and find the corresponding pressure for whatever refrigerant you are using.Quote:
Originally Posted by frank
I generally recommend tripping a HP control at about 135-140F/57-60C. Look at your P/T chart to find what pressure that corresponds to for any refrigerant.
Refrigeration is about temperatures, not pressures. When you learn to think in terms of temperatures, you can work with any refrigerant. A new refrigerant only requires a new P/T chart.
Back when only a few refrigerants were in common use, I told people to paint over the pressure scales on their gauges, so they would be forced to use the temperature scales. Temperature is what really matters.
Translate all of these pressures into temperatures, and you will find that all systems run at roughly the same temperatures, regardless of refrigerant. You can memorize a few temperatures or a very long list of pressures. Temperatures make the job much easier.Quote:
Back when only a few refrigerants were in common use, I told people to paint over the pressure scales on their gauges, so they would be forced to use the temperature scales. Temperature is what really matters.[/QUOTE]
temperature alone is as irrelevant as pressure in isolation. it seems slightly patronising - to me at least- when some say
' forget the pressure tell me the temperature'
it's nonsense you cannot diagnose by temperature alone..
if i said the suction pipe is 12 deg's c what's wrong?
could you tell me??????
i rather doubt it..
no you would give me a list of alternatives much the same if i said 'the pressures 34psig whats the matter?'
rant over back to the wine..;-))
cheers
richard
I totally agree. There is no temperature or pressure that, by itself, tells me anything important about the system. It is temperature differences that tell us everything we need to know. TD's, dT's, subcooling, superheat, approaches. All of these involve subtracting one temperature from another temperature. Working with pressures adds an unnecessary layer of confusion, since we must then convert them to temperatures.Quote:
Originally Posted by rbartlett
So, instead of saying, "Forget the pressure, tell me the temperature", let's say, "Forget the pressures, tell me the temperatures".
And if you want me to figure out everything that's wrong with the system, then tell me ALL of the temperatures. Unless you really want to go back next week to find the other problem(s) that you missed the first time around.
well said Rbartlets I know if I work only in temprature or pressure then you are not able to understand what a system is doing.
if the liquid line was hot you would quickley check the condensor for dirt or faulty fans and you would be able to fix the problem 99% of the time, not to bad
if the liquid was cold then without gauges you know nothing except it aint working and you need a lucky guess
I am drinking a rather nice rioja at mo
Perhaps I'm not stating this clearly enough, so let's rephrase this one more time:
Forget the pressures, tell me the saturation temperatures which those pressures correspond to on a P/T chart.
Whether you realize it or not, you are defining hot/cold liquid line in context to ambient temperature. Your definition of "hot" or "cold" depends on how hot or cold the ambient is. You are considering two temperatures, not one.Quote:
Originally Posted by Peter Mitchell
If someone told you their liquid line temp was 110F/43C, would you say they had an airflow problem? What if that liquid line were surrounded by 110F/43C ambient air?
BTW, condenser delta-T (air out temp minus air in temp) is a much more accurate indicator of condenser airflow problems.
I disagree RichardQuote:
If you had your gauges connected and you read a pressure then you would still have to do a temp/pressure conversion to get the overall picture. Don't forget that we are trying to control temps. How do you determine superheat? - temp/ pressure relationship. How do you determine sub-cool? - temp/pressure relationship.
It's no good approaching an R22 system on an A/|C application and saying " I'm looking for a back pressure of 55psig" you need to now what temps you are getting on the system.
Temps alone don't give the overall picture but they do give a better insight of how thesystem is working against how it should against just looking at the pressures.
If you had a system on A/C on R22 with a gauge pressure of 55psig - what does that mean? Unless you do a press/temp relationship comparison then it doesn't mean anything.
Point made?
hot or cold is not a refrence to ambient but is a refrence to body temprature when you touch somthing it will feel hot to you and hot to me if all thing are equall
The wine is really kicking in
If you were realy wanting to push the boat out there is infact no such thing as cold just not as hot
err point not made at all
i said you cannot work from temperature alone, you agree then tell me you disagree whilst going on about temp/pressure..
what is your point exactly??
cheers
richard
Sorry, guys. I've been editing while you were posting, so read it all again... LOL
It's mid afternoon here, so I haven't started on the liebfraumilch yet. I'll catch up later. :)
Originally Posted by Gary
well don't hang around you've got a lot of catching up to do *hic*
cheers
richard
Richard
Just trying to make the point that you should not just look at pressues - everything is related (temp/pressure). Obviously my Leibfraumilch has kicked in :D
my piont is that if you only use say temprature then you will be able to fix some problems but not all
If you had a system that had air in it then just looking at the temprature you would not be able to find this problem you might think it needed more gas
If the system had air in it, then the difference between the saturated condensing temperature and the ambient temperature would be excessive.Quote:
If you know all of the temperatures, including the saturation temperatures, then you can find all of the problems.
Would you not get the simmilar readings if the unit was grossly over charged. I aggree with your statment but stick on gauges and the high discharge pressure with less than ambient tempratures at discharge of condencer
Maybe all you need is to get two readings whether pressure or temprature as thay are directly related
superheat can be measured by temp in versus temp out or pressure out versus temprature out how fancy would the gauges have to be for pressure in versus pressure out?
Too much wine I think
In order to do this you would need to know what 'high discharge pressure' means for every refrigerant on the market.Quote:
OR
You could know what 'high saturated condensing temperature' means. Then you can work with any refrigerant for which you have a P/T chart.
Your choices are: Memorize a long list of pressures, or memorize a single temperature.
BTW, it is not possible for the condenser leaving air temperature to be less than ambient (condenser entering air) temperature.
nice story but irrelevant
we are talking about diagnostics by temperature in relation to refrigerants not the cooling characteristics -or otherwise- of water
cheers
richard
It isn't the pressure of the (OFN, water, refrigerant, whatever) flowing inside of the coil that cools the air flowing outside of the coil, it is the temperature of the (OFN, water, refrigerant, whatever) flowing inside of the coil that cools the air flowing outside of the coil.Quote:
It's about temperature, not pressure.
and this is a PRESSURE enthalpy diagram
cheers
richard
Thinking I may start on that bottle early tonight... LOL
I said it already in other posts, I rarely use a thermometer and I know my job and can repair quick and good most problems.
The battery for my temperature meter was out when I needed it some time ago, well.. it took me months before I needed it again and I realised I still had no new battery for it.
Why translate pressures always in temperatures and why for christ sake you have to do this to set a pressure switch? On the gauges of a pressure switch are only pressures indicated, no temperatures at all, so why translate it again to pressures? I don't see it. It all has to do how you learned it. I think I skileld myself with pressure gauges while Gary did it with a thermometer. The new generation is doing it with a laptop or a handheld unit.
Is my method therefore not as good as Gary's TECH method? I doubt it.
I set pressure switches to the max allowable pressure the manufacturer gives me, mostly 26 bar for the HP versus LP just above atmospheric pressure (not for a scroll of course) What is wrong with that? It never gave me problems and no one could ever convince me that this is wrong.
A high pressure switch is a safety device to protect the compressor going above the max allowable design pressure, given by the manufacturer. So I only do what they recommend me without translating it to temperatures which i find is real b..s.
It's like other posters said (Frank I think): you need both, pressures and temperatures.
sorry I did not mean the air temprature through the coil but the liquid temprature leaving the coil going to the system