Hi I am new to RE but not new to industrial refrigeration have just came across this thread regarding changing refrigerants . Be careful.iCE MAN is correct regarding chemical reactions.
A few years ago I was asked to check a NH3 plant that giving problems.
The Plant’s basic function was to supply refrigeration to eight 14 plate plate freezers.
A leak had occurred on one of the flexible hoses to one of the plates. An inexperience service man had been called in to trace the leak and repair. After apparently replacing a faulty hose he decided to pressure test and used R22????.
On deciding the system was again sealed he returned to plate unit to service after a short vac out.
I attended the plant the next day on being told there was a liquid feed problem. Not being aware of the previous work we arranged to have the strainers checked on the liquid feed lines assuming the problem was oil but what we found confounded me originally because the filter unit was blocked up by what appeared to be a wax.:confused:
To cut along story short the compound was Ammonium Fluoride. (NH4F).
Chemical analysis eventually deduced the following.
R22 +R717 => Ammonium Cyanide + Ammonium Chloride + Ammonium Fluoride
CHFIF2 + 5NH3 _=> NH4CN + NH4CI + 2NH4F
In the presence of iron the above becomes
R22 +R717+Iron => Ammonium Ferro cyanide + Ammonium Chloride + Ammonium Fluoride + Hydrogen
6CHFIF2 + 28NH3 +Fe =>(NH4)4Fe(CN)6 + 6 NH4CI + 12NH4F + H2
I understand a similar reaction any of the HFC refrigerants will have an adverse reaction with ammonia. Don't go there.
Remember the source of the Iron is the components of your plant and piping systems.