please settle this debate
me and my friend were having a debate.
my statement:
during start up, the high side pressure in the system does not exceed its normal operating high side pressure.
you can find my explanation to him here.
his statement:
during start up, the high side pressure gets extremely high, up to twice as much; and then comes back down to normal operating pressure. he couldn't really provide me any sort of evidence for his argument, and i couldn't think of any myself. if you can, let me know.
please vote in the poll, and any comments on either side are much appreciated.
thanks for your time.
Re: please settle this debate
Quote:
Originally posted by dmitriyaz
me and my friend were having a debate.
my statement:
during start up, the high side pressure in the system does not exceed its normal operating high side pressure.
you can find my explanation to him here.
his statement:
during start up, the high side pressure gets extremely high, up to twice as much; and then comes back down to normal operating pressure. he couldn't really provide me any sort of evidence for his argument, and i couldn't think of any myself. if you can, let me know.
please vote in the poll, and any comments on either side are much appreciated.
thanks for your time.
Theirs only one good way to prove this to a stubborn friend. If you have a car with a working A/C system, hook up a set of gauges, one on the high side and one on the low side. Turn your car on, and turn the ac on... roll down the windows, find the throttle linkage to the throttle body/carburator and rev the engine to 3000+ rpms and let your friend watch the pressures rise/fall.
Re: Re: please settle this debate
Quote:
Originally posted by abcdefg1675
Theirs only one good way to prove this to a stubborn friend. If you have a car with a working A/C system, hook up a set of gauges, one on the high side and one on the low side. Turn your car on, and turn the ac on... roll down the windows, find the throttle linkage to the throttle body/carburator and rev the engine to 3000+ rpms and let your friend watch the pressures rise/fall.
:confused:
Who said anything about a car a/c system?They differ from the system he is talking about.
Try reading a bit next time. ;)
Just for the record I am his friend.The point I was trying to make was that there is a larger load on the system upon startup.And you really feel it if your condenser cant handle much more than average operating conditions.He is actually the stubborn one here. ;)
I will have to take a couple movies of the low and high side gauges upon startup for him I suppose.
When I told him that the pressures "get extremely high" I actually told him that they skyrocketed on one system I had.But he thought I meant for all systems.Our real argument was the increased load on startup.
Re: please settle this debate
Quote:
Originally posted by dmitriyaz
me and my friend were having a debate.
my statement:
during start up, the high side pressure in the system does not exceed its normal operating high side pressure.
you can find my explanation to him here.
his statement:
during start up, the high side pressure gets extremely high, up to twice as much; and then comes back down to normal operating pressure. he couldn't really provide me any sort of evidence for his argument, and i couldn't think of any myself. if you can, let me know.
please vote in the poll, and any comments on either side are much appreciated.
thanks for your time.
Re: please settle this debate
If the problem is really a high evaporator load and higer than normal room air temps, yes, the suction pressure will increase and some time drastically. Ways to control the excessive statr up suction pressure are use of a MP or pressure limiting expansion valve. An alternate method is to use a compressor suction pressure regulator or CPR valve (crankcase pressure regulator).
As for the restricted liquid line, if this is the case, you will tend to run high suction superheat and low suction pressure since you can not feed enough liquid to the coil. The compressor would be a PD (positive displacment) type and all it knows is to pump so many CFM, irreguardless of the load or liquid feed. If you do not feed sufficient liquid for the load, the load will evaporate all of the liquid available and the compressor sucks it out. If the line of expansion device is severely restricted, the incoming mass flow will be less than the CFM the compressor is pumping and the suction pressure drops.
I have designed low temp glycol chillers (two 700 HP screw units with flooded evaporators) which had to start up against a high temp load and pull down without operator attention. The last one had to start with 120 dF process liquid. Due to the total system volume and piping to pull down, these machines operated for close to 2 hours at elevated evaporator pressures before reaching the design pressure/temperature. The control was achieved by amp limiting the compressor, high discharge pressure load limiting, load ramp up control and a modulating suction pressure valve, to hold the high pressure off the compressor until it was within operating limits.
Ken
Re: please settle this debate
The head press will float up and down based on ambient temp and load. With ambient remaining constant and cond rejecting more heat head will go up. This is a normal condition.
Prof Sporlan is right if head press is abnormally high something is amiss.
I have seen non condensables in the system give the indications that were described above.
Re: please settle this debate
Fit high and low side gauges to a system , start the compressor, suddenly the refrigerant standing pressure changes , it gets lower on the low side and higher on the high. A good reason for the head to keep climbing and then drop to a steady level would be the activation of a condenser fan /pump / waterspray,
Re: please settle this debate
this is going to be short and sweet. The head pressure will be very high because the evap temp is high the evap pressure is high so the head pressure will be very high use a evap press reg or crankcase pressure regulator to avoid this . this is a very common siuation it happens every time a system starts up.
wesmax
Re: please settle this debate
Second comment. You can put all the formulas to paper you want the fact is undisputable the higher the suction the higher the head .
wesmax
Re: please settle this debate
pressure will be higher than working pressure... in my humble opinon
Re: please settle this debate
there is no better teacher than experence with hands on work.
wesmax
Re: please settle this debate
Hi All ,
Now heres a thought for you.Which is starting first - The condensor fan motor , OR the compressor.Simaltaneous start will give you slight rise before settling , Compressor on start delay with Condensor fan start on make of cooling call = cooling of standing refrigerant in condensor - pre compressor start for delay period usually 3- 5 minutes , very handy for our hot clmates like here in oz.
Re: please settle this debate
you may start the condensor fan first but we start the compressor first here in the winter to get enough heat in the condensor to move the gas around.
wesmax
Re: please settle this debate
higher suction at start up = higher head pressure.
Re: please settle this debate
you are rite sometimes depends on the condensor temp here in alberta in the winter the outdoor temp is -30 so air over the cond is -30 so head is not up. You realy do not give enough info in the question.
wesmax
Re: please settle this debate
Quote:
Originally Posted by
mr cool
higher suction at start up = higher head pressure.
This is pretty much it, when a unit starts it's going to be at it's highest suction pressure, which means the head pressure will be highest.
I was working on a upright freezer yesterday. Ambient was 39C, but it was hotter than that due to all the other condensing units.
After defrosting the coil (so the evap coil was warm), I couldn't get the damn thing running again. It kept on tripping out for some reason, while all the other freezers at -18 were cycling fine.
So I had to increase HP cut out from 2600Kpa to 2800kpa just to get it started.
edit: Nothing changed on the system, it was cycling fine, not tripping out the 2600kPa HP before I defrosted it.
Re: please settle this debate
I cannot vote . But High side pressure rise up and gradually drops down. Its a common phenomenon in the compressors. You can say this is an instantaneous rise due to back pressure in the condenser. If you start the compressor with throttled suction valve then you may notice high pressure side never exceed the set values. That's why when condition is bad suction is throttle and slowly open at start up. In new systems this part is looked after by the programs and related solenoid valves
Re: please settle this debate
Most systems that i work on have some sort of capacity control, be it converters/inverters on VRV/F's or unloading valves, slide mechanisms etc. on chillers, I am not suggesting that the design condensing temperature is achieved instantaneously but head pressure control is very precise in most modern systems.
Of the two answers I agree with you.