Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi animon.2008
All them too much. Maybe one of one i can send you the manual. Which one you need??
See you
Reefer Mechanic.
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
reefermechanic
Hi Alain,
I think your unit is not refrigerated container unit. I cant help you. sorry..
see you
reefer mechanic
Sorry, you're right ... my bad English made me post in the bad place.
See you.
Alain
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Help me please!What do theemergencycodesE6 and E7inthe refrigeratorKerstner202E?How to remove them?
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hey now this is the problem which i have a challenge can someone advice for this
m on the ship and i have a dikin reefer setpoint -25 is not getting in range and all the things seems ok
which are as below:-
supply=-24.6,return=-19.0,suction pressure=-.39 bar,discharge pressure=13.5 bar
EV=10
SMV=100
SG=44.7
DC=-91.2
EO=-25.3
EI=-28.3
AMBIENT=35
C.T=8.1AMP
SO i know you are reefer geeks so hoping for your good response.....take care
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hey guys can anyone maby help me out with a panasonic unit model number cu-140c53xp? unit runs for a while and then completely shuts down ...im still learning about ref...
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hi all ... i dont no if anybody can help but i hope so...i have an carrier thinline with controller microlink 3 and i want to change the battery data(BR 2330) anybody knows if it was like microlink 2i or it is necessary to weld ,the old was just plugged in, I can not see on these new because it comes filled with glue and I did not want to venture without knowing if it is really necessary welding it or not...
glad for your attention
hope anybody can help.
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
Ruiripper
hi all ... i dont no if anybody can help but i hope so...i have an carrier thinline with controller microlink 3 and i want to change the battery data(BR 2330) anybody knows if it was like microlink 2i or it is necessary to weld ,the old was just plugged in, I can not see on these new because it comes filled with glue and I did not want to venture without knowing if it is really necessary welding it or not...
glad for your attention
hope anybody can help.
Hi Ruirippe
yes you right , ,the old was just plugged in. But new batteries are different. You need to solder. But i didn't replace any new type. You should careful the plus and minus connections. Good luck.
see you
reefer mechanic
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hello. happy new year!!!.
I need views on the alarm13 : I/O expansion communication fault on .
unit type carrier, scroll compressor.
how to off or by pass the I/O expansion communication.
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hello!
I have a problem with SRAM cards. I wanted to upgrade to 5354 in a reefer, but I tried with several cards and now everyone shows me the display "bad card".
I've formatted the card and put the softwar again, but I still have the same problem. I tried to change the battery of the cards but not solved. Can you help?
I apologize for my poor English
Thanks!
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
KapitanPeskanov
Hello!
I have a problem with SRAM cards. I wanted to upgrade to 5354 in a reefer, but I tried with several cards and now everyone shows me the display "bad card".
I've formatted the card and put the softwar again, but I still have the same problem. I tried to change the battery of the cards but not solved. Can you help?
I apologize for my poor English
Thanks!
Hi Peskanov,
I m sorry but i think you have to buy new PCMCI card.
good luck
reefer mechanic.
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
..................................
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
.................................
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
reefermechanic
Hi khelian,check your mail boxsee you..reefer mechanic
Hi sir i solved my problem grounded SSV ireplace new thanks sir cher up hehehe
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
mr. reefer mechanic what can i do my compressor have icing on suction section when the temperature is -16 the suction section wil be heavy frosted so i will stop operation of the unit :'(
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
kheilan
mr. reefer mechanic what can i do my compressor have icing on suction section when the temperature is -16 the suction section wil be heavy frosted so i will stop operation of the unit :'(
hi kheilan
,
what s the unit model number??
see you
reefermechanic
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Peskanov
Are you using aftermarket cards? You have to reprogram the card or charge the battery. Keep it in the omnidrive and recharge the card. Then format and reload the software.
This happens to me once in a while with the non carrier cards.
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
I have a question. LXE10E -A15B. Unit cools fine but will not heat or defrost. Suction pressure is -50kpa in defrost. Both HSV and DSV operating normally(Can feel hot on both side of valve and coil energizes)
PTI alarms J241 and J321. ANY IDEAS ?
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Same one we touched on ?
Quote:
Originally Posted by
bruisermac
will not heat or defrost
(Can feel hot on both side of valve and coil energizes)
Curious, where does this "feel hot" end ?
I mean if it's not making it to to evap, gota 'end' somewhere.
Edit; Another thought, any chance it might be slightly under charged ?
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
bruisermac
I have a question. LXE10E -A15B. Unit cools fine but will not heat or defrost. Suction pressure is -50kpa in defrost. Both HSV and DSV operating normally(Can feel hot on both side of valve and coil energizes)
PTI alarms J241 and J321. ANY IDEAS ?
Hi bruisermac
pls check your PM.
see you,
Reefer mechanic.
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
pls i have a question .i have probleme in the starcool unit.section presser 0.5b and desh presser 6.4 b all valve are ok .set point -20 ret -13 sup -16 the probleme is the frequncy of the copressor is very low 33 HZ .tubing pressure section is full of frost.
i am sorry for my english.
thanks
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi reefermechanic maybe you can help me to find service manuals for SB II trailer, how to access the super guarded access of SB III SR+ a manuals for this as well, also i need to also a thermo king trucks and trailers parts catalogue. Here is my email rebartolay@yahoo.com. Thanks
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
terminal
pls i have a question .i have probleme in the starcool unit.section presser 0.5b and desh presser 6.4 b all valve are ok .set point -20 ret -13 sup -16 the probleme is the frequncy of the copressor is very low 33 HZ .tubing pressure section is full of frost.
i am sorry for my english.
thanks
You seem to have a defective suction temp sensor (reading is probably too high), so controller keeps on trying to open the EEV on higher percentage than needed to pull down.
Try to compare the readings of the evaporator temp sensor and suction temp sensor. :) They should not be too far from each other.
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
thank you gentlemen for your help. I checked all sensor are good.i've found the problem in copresseur performance.
best regard
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
check evaporator fan if it is running or any ice clogging before and after evaporator airway. if ok then check expansion valve.
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hi, i have small problem with carrier 69nt40-541-301. i found the unit was not running and no display.supply voltage were checked and found all ok.checked all connectors found all ok. i replaced the controller ML3. then unit ran. but the cooling is not that efficient. it only cool down to -1.8C to -1.3 sup, ret from 1.2 to 0.8C. SP is -2.0C. On the display cd01 smv opening is already 100%. it was cooling good before the old controller fail. i already bypassed the smv line with a hose from port before the smv to suction service valve(thinking that the smv not really opening) but still not cooling good. the new controller (ML3 uncofgrd,recip p/n 12-55008)has built in operational software (cd18) 5147. but unconfigured (cd20 is blank).dont have configuration software onboard right now.
how much must be the current or voltage (forgot how smv is controlled :D) when the contrller is commaNDING IT TO OPEN 100 %(because i measured V nothing, or even negative small value with smv disconnected)? iwant to correct first the software installed before jumping to conclusion that the EV is the problem.it is possible that the problem is cause by this unconfigured controller?
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
KapitanPeskanov
Hello!
I have a problem with SRAM cards. I wanted to upgrade to 5354 in a reefer, but I tried with several cards and now everyone shows me the display "bad card".
I've formatted the card and put the softwar again, but I still have the same problem. I tried to change the battery of the cards but not solved. Can you help?
I apologize for my poor English
Thanks!
Have you tried recharging the card in the Omni reader and reloading software.
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
alfredegz2003
hi, i have small problem with carrier 69nt40-541-301. i found the unit was not running and no display.supply voltage were checked and found all ok.checked all connectors found all ok. i replaced the controller ML3. then unit ran. but the cooling is not that efficient. it only cool down to -1.8C to -1.3 sup, ret from 1.2 to 0.8C. SP is -2.0C. On the display cd01 smv opening is already 100%. it was cooling good before the old controller fail. i already bypassed the smv line with a hose from port before the smv to suction service valve(thinking that the smv not really opening) but still not cooling good. the new controller (ML3 uncofgrd,recip p/n 12-55008)has built in operational software (cd18) 5147. but unconfigured (cd20 is blank).dont have configuration software onboard right now.
how much must be the current or voltage (forgot how smv is controlled :D) when the contrller is commaNDING IT TO OPEN 100 %(because i measured V nothing, or even negative small value with smv disconnected)? iwant to correct first the software installed before jumping to conclusion that the EV is the problem.it is possible that the problem is cause by this unconfigured controller?
You are right that you should first make sure model config is properly set. From what you said that SP is -2.0C and supply temp(controlling sensor) is -1.8C then stepper valve should already be partially closed.
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi Alfredegz,
check ur pm:)
see you
reefer mechanic
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi guys
I'm having an issue loading the Star Cool version 0350 software onto the CIM 6 units. I'm using a laptop to do the upload as i am currently stil waiting for my logman that i ordered 2months ago.
When ive connected to the reefer with starview through the laptop i go to the software upload option. Once selected unit shuts down and the upload window starts to test the connection and says satus ok after a few seconds. But the upload progress bar stays at 0% and when i go into details it shows that 2 block errors have occured.
Can anyone shed some light on what these block errors could be or what i'm doing wrong. I have never updated a star cool reefer with a laptop so if anyone can maybe provide me with a step by step on the process.
Also i would like to know if daiken, thermoking and carrier(all mentioned reefers are marine reefers) can be updated with a laptop and if so what sofware do i need and where to getit. I already have the updates available, but with no logman i'm a little stuck....
Thanks in advance
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi Guys,
I have changed comp. in an LXE10E Daikin. Sight glass was foggy so i changed that and drier.Recharged with virgin R134a. Unit ran for about 1 min or 2 then went into deep vacuum. I trouble shoot alarm 109 per latest bulletin. I have changed eev body, lsv coil and body. How to trouble shoot SMV without magnet. Any and all help appreciated.
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
Reefer709
Hi Guys,
I have changed comp. in an LXE10E Daikin. Sight glass was foggy so i changed that and drier.Recharged with virgin R134a. Unit ran for about 1 min or 2 then went into deep vacuum. I trouble shoot alarm 109 per latest bulletin. I have changed eev body, lsv coil and body. How to trouble shoot SMV without magnet. Any and all help appreciated.
Hi Reefer709
Do you sure EEV is ok? Pls take out the bobin of EEv from body. Then run the reefer. You have to check on select menu LPT. Waiting your reply.
Best regards.
reefer mechanic
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
There also may be a problem with either one of your evap inlet and outlet sensors that can be checked in the menu check your ambient sensor as well
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
There also may be a problem with either one of your evap inlet and outlet sensors that can be checked in the menu check your ambient sensor as well. Make sure that when you put the EEV coil onto the body that you seal it with silicone as moisture gets into the body and freezes up causing vacuums
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Good Day Mr. Reefer technician,
I'm trainee electrical officer in MAERSK line. Just started my 2nd sailing in MAY2012. I dont have much experiance on troubleshooting of REEFERS. I've handled DAIKIN,STARCOOL,CARRIER,TK.Will need your guidance for troubleshooting. I'm already started to reading through all manuals. But still require your guidance. I hope you will.
Thanking you.
Rohit.
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hi there Guys, I have a problem with an NT20-531-301. The unit throws up an AL14, it is running and at temp and has been for 2 days. we have checked all the IP circuits and all wiring. the evap motors are all working and the controller is reading current.I have tried to swap the incoming phases over and the other phase contactor pulls in and the alarm remains active. The incoming power is ok .
WE have also checked Cd41 and the right hand digit is a 4.The manual tells me it is either a motor or sensor. The manual doesnt tell me what sensor. I have reconfigured the controller and loaded the latest software, still no joy. We have swapped the controller and also tried a new expansion module and the alarm is still active. We have checked the terminals on the compressor and they are all ok. the current draw on the compressor is within limits. I have talked wirth a couple of people and they seem to think that the compressor could be the problem. I really need to be sure before recommending this .
Any help that anyone can give would be very much appreciated
Thanks in advance
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
................................
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
E/E Rohit
Good Day Mr. Reefer technician,
I'm trainee electrical officer in MAERSK line. Just started my 2nd sailing in MAY2012. I dont have much experiance on troubleshooting of REEFERS. I've handled DAIKIN,STARCOOL,CARRIER,TK.Will need your guidance for troubleshooting. I'm already started to reading through all manuals. But still require your guidance. I hope you will.
Thanking you.
Rohit.
Hi Rohit,
Thanks for your good wishes. I try help you for your request. But reefer container jobs is not easy. I was working since 10 years in this job. I still learning a lot of things when working. My suggestion would be to develop the most important scholar, cooling and electricity.
good luck
see you
reefermechanic.
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi all reefer,
First, sorry for my poor English.
I have a problem with Carrier 551-506 (scroll compressor). It got P10-1 Fail when Pretrip, about 3-4 units got same this problem. I've check refrigerant OK, all valves are operating normally. When unit's in cooling mode (not in Pretrip), it run until about -10C to -12C, automatically actived deforst by system. Normally, a 40' unit take about 3-4 hours for a Pretrip, but it took over 6-9 hous then got P10-1 Fail. Also i've SW (5354), config (551-506) are OK. I was confused this problem, so anyone can help me for solving it pls.
Thanks & Bgds,
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
ReeferC
Hi all reefer,
First, sorry for my poor English.
I have a problem with Carrier 551-506 (scroll compressor). It got P10-1 Fail when Pretrip, about 3-4 units got same this problem. I've check refrigerant OK, all valves are operating normally. When unit's in cooling mode (not in Pretrip), it run until about -10C to -12C, automatically actived deforst by system. Normally, a 40' unit take about 3-4 hours for a Pretrip, but it took over 6-9 hous then got P10-1 Fail. Also i've SW (5354), config (551-506) are OK. I was confused this problem, so anyone can help me for solving it pls.
Thanks & Bgds,
Hi reeferC
welcome on board:))
Have you try work the normal operation to the reefer? You have to set the set temperatureto -18.0 C and pls note when return temperature to the -18.0 C. I no know have you check to the inside of reefer container. If there is damage on buffer plate and evaporator fan blades reefer unit doesn't cool. Check them pls.
good luck
reefer mechanic
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
ReeferC
Hi all reefer,
First, sorry for my poor English.
I have a problem with Carrier 551-506 (scroll compressor). It got P10-1 Fail when Pretrip, about 3-4 units got same this problem. I've check refrigerant OK, all valves are operating normally. When unit's in cooling mode (not in Pretrip), it run until about -10C to -12C, automatically actived deforst by system. Normally, a 40' unit take about 3-4 hours for a Pretrip, but it took over 6-9 hous then got P10-1 Fail. Also i've SW (5354), config (551-506) are OK. I was confused this problem, so anyone can help me for solving it pls.
Thanks & Bgds,
and also you have to check air flow of condenser coil. If need clean the condenser coil.
see you
reefer mechanic.