plz i have probleme with dakin for f 803 END F109; I WANT TO KNOW THE GOOD SOLUTION FOR THIS PROBLEME;THINKS MY TETCHER
the problem is that one of the phase contactor coil is shorted to ground. if Fu1 pops when the contactor pulls in the coil is shorted. so you can change the faulty contactor or if an emergency rewire the 460V plug and swap 2 wires...this will change the phase and pull in the other contactor. F 803 is "protection devices have tripped 10 times" and will also probably have a E101 or E109 alarm. you can then clear any alarm by selecting the alarm and holding enter.
im a container reefer pro and can help just like reefermechanic!
good luck.
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi reefermechanic,
I am a fresh guy on this site but work for reefer container for many years
We got a problem on TK/MP3000A controller, we found the GMT time changed by unit on /off several times
( seems breaker of power supply tripped at terminal ) though we had reset the corrrect GMT time but problem still occured, We can't find anything wrong on this one year old controller of Magnum type.
Is there possible the RTC battery dead
or weak ? I had ask TK guy but can't get the answer till now. Do you have any idea about it ?
Tks,
William0707
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi PRO reefer Mechanic,
I know the password " A " for MP300 but reset only can be done by LOGAMN PC
We can reset to the correct GMT time but don't know what trouble lead to this change of GMT( but nobody do the setting, it reset by controller ). I have found 2 cases in two shipping line's datalog but can't expalin this trouble only by their datalog.
Any comment will be appreciate !
William0707
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Im too i search the catallogue ; informations for reefer tec
thanks monir_khatibi@hotmail.com
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
tanks my tetsher i have one probleme for daikin end i want solution for this probleme
f 803 END F1O9 END F 107
I WAIT YOU SOON
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi PRO Reefer Mechanic,
Unfortunately units were away from my terminal. The strange of GMT time
( time even record 2009-06-20 138:20:16- future time and abnormal hour ), we had checked the dehumidity sensor, gas sensor even replace to a new one to avoid high voltage then reset the GMT time, but it occured after power on/off for running 2 days. I guess it must be some short circuit or bug in the controller ? But it still passed the test by tester !
I know it's hard to find out without current unit on hand for test, but just can't find a way to explain this defect, any idea? please share, tks!
william0707
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
did you try to set the date with smartsponge and a laptop? or are you just using the logman?
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hallo
i bought the thermo king refrigerator container type hd-ha-ab951 2007 year. But i need manual.maybe you could help me!!!
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi Bruiser
Mp3000 controller should be uploaded the setting or software by LOGMANPC 4.9.0 , of course we did upload the GMT setting by laptop P.C.
We still get no idea about this defect, Any comment will be appreciated, tks!
william0707
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
maiks
Hallo
i bought the thermo king refrigerator container type hd-ha-ab951 2007 year. But i need manual.maybe you could help me!!!
Hi Maiks
you sure type is correct??I never seen to this model:)do you add a picture in here??Thanks..
nice to meet you
see you
reefer mechanic..
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
I need to repair a Thermo Guard Up-IV for Thermo King SB-III SR, where can I get this done? or even where can I buy used one for not a lot of money?
Thanks for any help you can provide.
Oscar
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hi guys i am new here so pls excuse me but i am intrested in buying a small 3 tonne hino truck with an older thermoking md-1 Fuelsaver the hours shown are 2202 hrs . do you guys know anything about the reliability and dependability of these tks and would you pls let me know what i got to look for as this is my first truck and i want it to last a while
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
reefermechanic
Hi All,
I m senior reefer technician.İf you have got any problem about reefer container units . i will be here....
All the best.
Dear mec
I have got many problems in different type of reefers can u give me your mobile number my is 00967733762011
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
RTE or Eriksson for the controller
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
...................................
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
I have a carrier Phoenix Advantage that I recently purchased. It's on a wreck that laid on it's side. It starts and runs good, blows cold, but the out of range light stays on and the numbers on the display keep counting down continuously, and I can't set temp. Any help would be greatly appreciated.
Thanks, Art
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
reefermechanic
Hi All,
I m senior reefer technician.İf you have got any problem about reefer container units . i will be here....
All the best.
I have a carrier Phoenix Advantage that I recently purchased. It's on a wreck that laid on it's side. It starts and runs good, blows cold, but the out of range light stays on and the numbers on the display keep counting down continuously, and I can't set temp. Any help would be greatly appreciated.
Thanks, Art
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hey art
you need trailer guys for that problem...this is the container reefer side of the industry...plus units dont usually run very well on their sides. may sound like alot of problems
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi PRO Reefer Mechanic,
I have problem with download data of daikin reefer machine, LXE-10D, have you send for me software DCCS new version. thank. email: pacificocean.info@gmail.com
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi reefermechanic,
I have some problem with download data of reefer machine carrier and daikin, can you send for me software? thank
pacificocean.info@gmail.com
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi all,
I am new in this business and i feel lost right now, can someone give me carrier and tk software and connection cable specification ???
Thank You !!!
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi senior mec
Need the manuals for Daikin (all models) and Thermoking (smart reefers) Service Manuals.
Regards
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hallo to all...
I'm new at this comunity and i'm so happy to have found you. I have a problem with a refeer container. Its an older one (1989) build by Graaff Germany, and it has Carrier Transicold machinery.
The problem is: it starts cooling fin until it reaches -3ºC. At that temp. it just turns off completely. Even the display turns off. It will eventually turn back on by it self after 15 min... How can i fix that..?
Do you have the instructions manual for that one?
Please help...
model nº.: 69NT40-394-9
Regards
Alex
-
1 Attachment(s)
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
OttiliPY
Hallo to all...
I'm new at this comunity and i'm so happy to have found you. I have a problem with a refeer container. Its an older one (1989) build by Graaff Germany, and it has Carrier Transicold machinery.
The problem is: it starts cooling fin until it reaches -3ºC. At that temp. it just turns off completely. Even the display turns off. It will eventually turn back on by it self after 15 min... How can i fix that..?
Do you have the instructions manual for that one?
Please help...
model nº.: 69NT40-394-9
Regards
Alex
Hi OttiliPY.
I donn t see like this model since a few years..Its very old but i think its working still:)
First you have to check to the "board,timing and current control".Usually somethings may burning on this card.I hope you will find problem..
Good luck
Reefer Mechanic.
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hey man isee u are so genirus in dis forum so iwant ducement about thermoking instalations and dats my email didou_wind@yahoo.fr
thank's man
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
didouwind
hey man isee u are so genirus in dis forum so iwant ducement about thermoking instalations and dats my email
didou_wind@yahoo.fr
thank's man
hi didouwind ,
what you wants??Manual??
see you
reefer mechanic
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
reefermechanic
Hi OttiliPY.
I donn t see like this model since a few years..Its very old but i think its working still:)
First you have to check to the "board,timing and current control".Usually somethings may burning on this card.I hope you will find problem..
Good luck
Reefer Mechanic.
Thanks a lot... I`ll check that out.
Still, i would need the installation manual, or the programming procedures. Yeah that thing is pretty old, but as you guessed, its still in a good shape. Despite this little problem...:)
Gracias dude...
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
reefermechanic
hi all,
i m senior reefer technician.İf you have got any problem about reefer container units . I will be here....
all the best.
tanks may tetsher i have probleme in refeer daikin al 803 the are to possibility for this alarm f107 or f 109 but t dont know the solution about this alarm plz thank you mester
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
tanks may tetsher i have probleme in refeer daikin al 803 the are to possibility for this alarm f107 or f 109 but t dont know the solution about this alarm plz thank you mester
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
I have probleme in daikin refeer al 803 plz what a wil doing plz mau prof
mu email/ hichamviolon@hotmail.com
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
reefermechanic
hi terminal,
first you have to check all control fuses..than you have to check eev(electronic expansion valve..
You have to check lpt (low pressure transducer) on select menü..if low pressure goes to down side quickly eev was failured.how can you check to eev?you have to take out eev coil body.if low pressure comes to up side eev coil problem when take out eev coil..
Good luck...
Reefer mechanic.
yes my prof some times i tchek the eev is good end when i make of in the reffer end make on it work normal end in rang but after 3hour or 2hour the some probleme unite stop al 803 .thenks
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
yes my prof some times i tchek the eev is good end when i make of in the reffer end make on it work normal end in rang but after 3hour or 2hour the some probleme unite stop al 803 .thenks
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Thankyou my teacher
for al803 i know that it is acause the 107 or 109 to 10 times.
All fuse are ok
servo motor running eev ok
what a did i make reefer off end on then he travel normal byt after time reefer out of rang end al e107 or e 109
plz help me because i have 3 reefers in terminal morocco
thanks
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hallo again...
After checking the electronic cards of my container, we got it running. Now there are some simple things i donto know.
On the control board are some switches wich i dont know what they do. I'm sure you can help.
What is the "HCS" switch for...? What does it do?
What does the "TDS" button...?
What is the "TSS"...?
What is "SDS"...?
All these switches are for something. Please explain them to me...
I'm blind here...:cool:
-
3 Attachment(s)
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
terminal
some times i tchek the eev is good end when i make of in the reffer end make on it work normal end in rang but after 3hour or 2hour the some probleme unite stop al 803.
Check for moisture/h2o in EEV between stem and valve body.
Important you get area in green arrow clean (blow off this part 'pic' #3)
See attachments below.
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
.................................
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
Will
Check for moisture/h2o in EEV between stem and valve body.
Important you get area in green arrow clean (blow off this part 'pic' #3)
See attachments below.
THANK YOU PROFESSOR AND FOR YOUR HELPEND Gentille
REALLY I NEED YOU FOR ADVICE OF REEFERS PROBLEMS .thank you
IF THAT possibl TO still be contacted my email :
troytroy@live.fr
THANKS
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi All,
I have problem with my laptop are can't connect communication when used for Carrier container unit/launch pad.
Detail model are acer TravelMate 6292.
Cause the port using usb port so i using serial adpter to joint cable communication with my laptop.
Is it cause that adapter so communication become interupt?or any other suggest
Any kind of response will be highly appreciated
Thank you
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
faruq
Hi All,
I have problem with my laptop are can't connect communication when used for Carrier container unit/launch pad.
Detail model are acer TravelMate 6292.
Cause the port using usb port so i using serial adpter to joint cable communication with my laptop.
Is it cause that adapter so communication become interupt?or any other suggest
Any kind of response will be highly appreciated
Thank you
Hi Faruq,
you have to connect via rs232 only for carrier units..If you can not use rs232 connection you cant connect to the carrier reefer unit..
See you
reefer mechanic.
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi guys,I've got a problem with Carrier 69NT40-511-38 controller M-2.The unit is set up-4C but does not stop gaining temperature when it is -4C inside.There is no any alarm.
Please,give advice
Thanks in advance.