Hi no I didnt how would I do this?
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
New to the forum, and looking for any manuals, schematics, etc... on Noske-Kaeser refrigerated chemical trailers. The company that has them in my area got a 5 page printout from them but it is in German. I can't read German. Any help would be appreciated.
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hello, i'm new in the forum and i'm looking for Carrier and Thermo King manuals, if you have some please send me, i'll be very grateful.
My email: lukaspavalkis@gmail.com
Thanks in advance.
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
To be accurate i'm looking for Thermo King SLX, SL series and Carrier Vector, Maxima manuals. Thanks guys.
my email: lukaspavalkis@gmail.com
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Can anybody has a service manual for Thermoking MD200 And MDII? Specially the overhauling manual for the engine.Please I badly need it. This is my email address ruben_rumarate1@yahoo.com
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
drier is probably plugged
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Dear all,
I need some suppliers for reefer containers.
I am in oman.
Kindly give a mail to jeyakumar@sfomuscat.com
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi tjk2007
I did send an email to you.. How can i help you?
Regards
reefermerchanic
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi guys
i m at here ;)
Best regards
Reefermechanic
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
its most likely a micro problem,a place in cali will go thru it for ya at a very reasonable price,here is their #7074250108
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi all,
I want to know if there‘s any software to read the real-time Tsup and Tret of MP3000 & MP4000? I know LogManPC can read the USDA values of MP3000, but now, many MP3000 containers have no these data. And, the LogManIIPC just downloads recording data from the Data Recorder. So, can anybody help me?
my email:ap0505138@yahoo.com
Thanks!
Wenping
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Any one with the manual for Thermo king CB MAX + 20
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi guys, this is a bit of a random question, but I thought you guys would have the knowledge to help me!... I'm an amateur screenwriter with an interest in the shipping industry and working on a movie script about a guy who gets locked in a reefer.
I was thinking that in the script, the compressor would fail and the reefer would start to heat up inside. As a result of the rising temperature he has to get out of there fast.
Is there any way that the guy in the reefer could cause this? Like if he blocked the airflow intake or outlet, could it overload the compressor? Or if he drilled a hole in the reefer or damaged the seal, could the increased moisture ice the evaporator coils over and overload the compressor, causing it to fail? Could he damage the electrics from the inside and shut down the compressor somehow? (Although I can't think why he'd be messing with the electrics) Anyway, I've just been trying to do some research and find some possibilities.
I'm sure I'm overlooking a lot of practical realities but I have no idea what they are!
You can probably tell from my question that I don't have much knowledge in this area, so any help you guys could give me would be awesome!
Apologies in advance if this is in the wrong section or not the right kind of thing for the forum.
Tom
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hello there. A question please.
SB 200 TG Reefer unit. I want to replace the filter dryer on this thing. Do I need to do a pump down at compressor service valves only?
Thank you in advance.
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi guys.
How to change fahrenheit degrees to degrees Celsius in Thermoguard 5D52175G01?
Thanx :)
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi! All
Help me
I'm having problems with one machine SB3 SR +, cycle-sentry operating mode, the engine does not work for high-speed mode, but when operating at continue mode, works well for high-speed mode
Tks
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
I have reefer trailer with SB-210. I have just replaced filters and run pretrip. It failed with clearable alert "refrig capacity low". This unit is only used for heating so do I need to add refrig r404a or is it ok to leave it like that?
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hello Reefer Mechanic and others!
I am a newbie here and I am happy to be part of this forum.
Our 69NT40-541-322 have a problem on sup and ret temp. The sup cannot reach the set point of -23°C and it stays only at -20°C and ret at -18°C. When it was loaded the sup was -23°C and ret -19°C. My mate charge about 1kg of refrigerant even the DP already high but he suspect it has low charge. After the charging the sup and return goes up insted of going down and of course it alarmed HPS. He recover some to just below the limit of HP. We also observe some oil down of compressor and this compressor was recon because of the paint. We cannot find the leaking part by using electronic leak checker we did not find the leak. The next day i found it was off and main breaker was tripped off. We turned it on and observed. We obsrerved that warm air out of condenser fan was disappearing after few seconds of running, we change the drier. But still the sup and ret temp cannot reach set point. Here are some data I have:
Suction pressure -0.6 bar
Discharge pressure 20 bar
CD60 -18°C, we dont know this
Ambient 36°C
SMV 100
We tried defrost, plenty of water comes out but nothing change in temp after. We turned off the reefer but discharge pressue does not drop, it almost remain high but suction pressure goes up. By pump down the DP goes down. The reefer does not trip anymore. Tommorow i will check the DPRV by checking the pressure on discharge of compressor vs liquid-line. What do you think the problem is? Sorry for my grammar.
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Checked DPRV, 1bar diff, seems ok.
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hello everyone! It became necessary to replace the so-called Quench Expansion Valve (part n. 14-00212-03SV). Absolutely no desire to buy it for $ 200 plus shipping (such prices at us, unfortunately), when it is possible to replace the OEM. The only problem is unknown, its capacity. Does anyone know? If so please respond.
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hello everyone.
I am working on a Thermo King TS-300 with a code 17, which is "engine failed to crank". I manually tested the starter, and it is good. The 8S circuit from the relay board is also good.
Since I have an identical scrap unit handy, I tried a different relay board, microprocessor, cab command, cab command cable, and main on/off switch. None of those made a difference.
The unit will preheat and the buzzer sounds, but it does not crank. Also, it appears that the pull in circuit for the fuel solenoid does not have voltage either. There is voltage at the 2A terminal on the board.
I'm stumped. Has anyone dealt with this before? Thanks in advance for any assistance.
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
What voltage do you have at the feed to the solenoid of the starter,try disconnecting the feed and testing if you have a feed to it pretty sure there is a plug on this feed close to the starter maybe a break in the feed try a temporary cable from that 8s and see if it engages the starter ?
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
I have done that. If I put direct power on 8S, the starter cranks. That tells me the plug and circuit are good.
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Over here we use desperate battery for the unit,sometimes I believe in the states they tap into the truck battery,there is an extra heavy wire fitted to the battery not sure if it goes to number ,has this wire got good power/ connection ?
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Whoops spellchecker ,should have spelt seperate!!! not desperate?
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi Reefer Mechanic,
Could you please help me out, I have a transicold reefer 69NT40-541-301 of which display is blinking and unit is not working, Display comes and missing frequently.
Thanks in advance
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
All dears,
I have problem with MItsubishi Transport refrigeration unit with model CPE15-3B H?
I need help please
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hey I have a thermo king unit c-600 and keep getting the code 24
Heating circuit fault
Any help guys
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hello !
anyone have ISO 10368 pdf ?
i try to understand aspects of protocol RMM<->REF, used over RS232 interface.
best regards.
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Dear Friends,
Any body have carrier software program e.g 5365,5165,5364..... Please advice me how to get it......
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Help me Mitsubishi TU42D alarm codes
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
reefermechanic
Hi Friend. pls check Cd-18 and Cd-20 within codeselect menu via keypad. And also pls check the unit model number. Unit model label left side of compressor and reply to me. see you. reefermechanic.
Mate it also happened to us before, i am working at cma-cgm container vessel, we have bad card also before and some of my mate did not replace the battery on the card. We ask our superior about the issue and the technical team provide us sram to usb adapter, so this solves previuos issues of bard card since all the files for configuration is there together with all reefer brand. Everybody should have this,no more battery involve and windows based.
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hapag Lloyd and Cma-cgm also
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi Reefer Mechanic,
We got a problem on Starcool, a tricky Tsuc Invalid. We changed already the sensor, door and main controller. Resistance of sensor 19.32kohms and voltage from controller to sensor 1.3vdc. Already tightened the insulation of tsuc sensor location. We notiched that controller is hot due to high disc press, compared to other Starcools, controller is not hot because disc press only below 10bar. Temp is in-range. Also i notiched that most Starcools the high speed cond fan run to lower until 8bar, but this reefer use low speed fan to lower 16bar to 14bar. Can you help us on this tricky Tsuc Invalid?
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hello Caummer,
Try to check connection from controller to display panel and then restart the power. If still persist replace the display panel.