In the bigger industrial machines it is not unusual to have no oil filter between the separator and the crankcase, but instead an oil filter between the crankcase and the oilpump (external or internal). That would be a filter without by-pass grade 40micron. However, after the oil pump there is a fine filter (10 - 20 micron) and that filter should be able to by-pass to prevent high pressures when gloged.
Well, Nico, I was thinking inside my box. :) Thanks for bringing up the industrial applications. Probably a differential alarm would complement the bypass filter setup?
In the scenario that I refer, when the PD between the crankcase and the discharge reached a particular point, the blow-by increased. Because the check valve in the oil return circuit prevented oil (pressure) from returning to the suction, the crankcase pressure would rise to a point that would near the discharge pressure during the pump down.
Would that be the check valve between the motor and compressor chambers?