Re: Blast Freezer Questions
Hi rickmor,
The cooling capacity of the existing system will considerably decrease when you operate it at lower evaporating temperatures.
By simply installing an identical compressor/evaporator you are only doubling that smaller capacity. But, this does not take into account the actual capacity requirements of the blast freezing operation.
The cooling load for the blast freezing operation should be verified by calculations to determine if the second unit will be sufficient.
Re: Blast Freezer Questions
A double stage compressor will probably be required, being the suction vapor pressure so low at -45° Te..