Re: This a long one - AKV
This is something that not can be done with a TEV nor a AKV. Only wit a reducing compressor capacity or an evaporating pressure regulator.
Quote:
(3) float the condensing temperature (or pressure) downward during night time or raining days.
Correct but why not run it also low during the day.
Quote:
Reduction in Superheat
As electronic expansion valves are known to give bare minimum superheat[1,2], its use can reduce the degree of superheat and therefore reducing compressor power requirement. The saving on compressor power will depend on (i) type of refrigerant and its flow rate, (ii) compressor operating pressures and (iii) degree of superheat with original TXV.
For a given refrigerant, difference between TEV and AKV, needed compressor capacity is only related to superheat (flow is related to the load) There was a time ago a thread around low superheat and the problem that then arise with oil return.
Quote:
For refrigerant R22 operating at an evaporating temperature of –10oC, compressor power reduction due to decreasing superheat is estimated to be as follows:
Reduction in Superheat (oC) Reduction in Compressor Power (%)
5 1.8
10 3.7
15 5.4
20 7.1
Normal superheat is +/- 6K for a proper adjusted TEV. So you can lower maximum 3K with an AKV.
Quote:
4.2 Control of Evaporating Temperature
With the use of electronic expansion valve and evaporator controller, it is also possible to maintain the evaporating temperature and the compressor suction pressure without unnecessary overcool at low load period. For refrigerant R22 with a design evaporating temperature of –10oC, lowering of evaporating temperature to –15oC will cause the compressor power to increase by about 10.6%. For every 1oC drop in evaporating temperature, compressor power can be expected to increase by 2%.
Perhaps I understand this wrong but it’s jus the opposite way: when load reduces, evaporating drops. This can be prevented – at evaporator side – with an evaporator controller which will indeed stabilise evaporating pressure. But suction pressure will drop then dramatically. So the final result for the needed power will be the same. But they start to mix 2 different regulating devices, not only the AKV.
Quote:
4.3 Floating of Condensing Temperature
The combined applications of electronic expansion and the compressor controller enable the floating of condensing temperature according to outdoor ambient condition. When the outdoor temperature is dropping at night or during raining season, the condenser can operate at a lower condensing temperature.
The combination TEV/Suction pressure regulator will give +/- same result.
Quote:
For air-cooled condenser used in most cold storage plants, typical condensing temperature is chosen at 15oC higher than air inlet temperature to the condenser. If the design air inlet temperature is taken as 32oC, the design condensing temperature would be 47oC. Assuming an evaporating temperature of –10oC, the compressor will be pumping from 0.353 MPa to 1.805MPa or a compression ratio of 5.11. By floating the condensing temperature (and pressure) downward, power consumption by the compressor could be reduced.
We chose them at 10K. Those who select 15K asks for high power bills. Same should happen with a TEV, this statement is not only valid for an AKV.
Quote:
It can be concluded that with R22 designed to run between –10oC and 47oC, every 1oC drop in condensing temperature will save 1.5% of compressor power. In the Singapore context, maximum fluctuation in ambient temperature can be taken as 8oC. Energy saving in floating the condensing temperature can be substantial.
This is through, but condensing pressures were taken high for a Tev and low for an AKV to enlighten the benefits (?) of an AKV.
Quote:
4.4 Defrosting Cycle Control
The evaporator controller can also be programmed to activate the defrost circuit on demand only rather than following a fixed schedule. Although the direct energy saving on this improvement may be small, it can help to reduce the extra cooling load needed to cool down the evaporating tubes after the unnecessary defrosting.
Can also be done with other controllers.
Quote:
5.1 Saving Assessment
From our observation during the visit to the site, the installations of both control systems were properly done and both systems functioned normally and satisfactorily. The savings obtained during the different periods are relatively consistence (see table below). Savings of +/- 22%The percentage savings of energy for the different periods vary from 20.8% to 23.6% which are considered to be very consistent for this kind of energy conservation projects.
Those figures don’t say anything if they don’t state at what conditions the compressors were operating, especially the HP side. I don’t say they’re manipulated but I don’t believe the savings. They’re too big. The savings don’t come from the AKV alone.
Quote:
.
5.2 Other Observations and Comments
(3) System effectiveness is dependent on the proper installation and control parameter settings.
The same for a TEV
Re: This a long one - AKV
peter,
cant you see, they are making more money from selling AKV's!!
chemi
Re: This a long one - AKV
Quote:
Originally Posted by
chemi-cool
peter,
cant you see, they are making more money from selling AKV's!!
chemi
This is really correct!
Re: This a long one - AKV
Just noticed now the pro's never gave their opinion
Re: This a long one - AKV
Quote:
Originally Posted by
Peter_1
Just noticed now the pro's never gave their opinion
Maybe those days there is not much pro's as today! We will see in few days.;)
Re: This a long one - AKV
Quote:
Originally Posted by
Peter_1
Just noticed now the pro's never gave their opinion
Hello Peter:)
my opinion is that there is applications for AKV and TEV.
I would tend to use AKV for applications where suction pressure optomisation is possible, where multiple evaporators are used and where loads drop off at night or during low ambients. But only on the controller that uses a pressure transducer.
TEV I would use on large fixed loads, where the load is constant and where the ambients don't vary as much.
The advantage of AKV over TEV is it sets it's self up, the engineer does not need to optomise the superheat. If suction pressure optomisation is not required and the TEV's are properly set up I personally don't think there is any advantage using AKV's.
Just to note it is usually more cost effective to purchase AKV's and their controller when larger 30kw + per valve loads are to be considered.
One application where AKV's should not be used or should be not set up to modulate is where off coil humidity is important (fruit stsorage, serve over counters ect).
Kind Regards Andy:)