Copeland Scroll Compressor
It's model ZR23K1-PFJN522
Single phase, 240v, 50z, 10.2A
R-22
Made 1994
This is going too cost the earth too run i know it but will it run okay on my house hold sparks or blow it?
Also im trying too find the full specs for it online but no luck at all with it!
Anyone able too help
Re: Copeland Scroll Compressor
I haven't seen other threads on this but I'm assuming its A/C that you are using it on.
Generally Coefficient of performance (COP) for an average A/C is about 2.5 - 3 which means that refrigeration power is approximately 2.5 - 3 times the kW of the input power in kW. At 240v and 10.2A, Watts = V x I ( 240v x 10.2A). Input power is 2.45kW. Lets work on the lower end of the efficiency and say that the COP is 2.5. Refig power= Input Power x COP (2.45kW x 2.5). Refrig power about 6.1kW.
If you can't find anything, this may get you started.
2 Attachment(s)
Is this OK?;)
Attachment 2646
Attachment 2647
What is use for this compressor?
In answer to your question, check your kettle, it runs at higher amperage than that compressor.
You might need to run it on a separate circuit so that you can put a motor rated circuit breaker in line with it for starting purposes.
1 Attachment(s)
You can find this model's full specification at emersonclimate.com.
However, here is the full specification of that compressor. The correct model number is ZR23K1-PFJ.
Scramjetman
You have missed mutiplying V x I by power factor - which for single phase compressor could be 0.85 to 0.9