Re: Daikin VRV III U3 error
U3 with VRVII shows that the initial CHECK function has not been completed.
Do you VRVIII Design Guide ?
Re: Daikin VRV III U3 error
Thank you for your reply
would please explain what do you mean by internal check
Re: Daikin VRV III U3 error
press and hold the test button to perform a test run. this will last for approx 45 mins. Or do a quick test with mode 2 binary 3. When your test run has completed, all of the controllers will flash "p7" when this happens, press the return button on the condensing unit, and happy days. This is the quick way of commissioning, but the refrigerant containment function will not be available.
Re: Daikin VRV III U3 error
^^ Demonstrates the need to have the correct instruction manual to hand and also to read it.
Re: Daikin VRV III U3 error
Quote:
Originally Posted by
Suffolk Fridge
press and hold the test button to perform a test run. this will last for approx 45 mins. Or do a quick test with mode 2 binary 3. When your test run has completed, all of the controllers will flash "p7" when this happens, press the return button on the condensing unit, and happy days. This is the quick way of commissioning, but the refrigerant containment function will not be available.
Hi all.
Do the right long test too feed correctly the oil from the accumulator to the compressor and wait to reach the same temperature between the inlet and the outlet of the accumulator.
From factory there's a low oil level inside the inverter compressor to facilitate startup at low ambient condition and avoid stall prevention.
rgds
cool#9
2 Attachment(s)
Re: Daikin VRV III U3 error