It sounds as though you're trying to dehumidify. This seems strange since we usually design a meat room with extra evaporator surface (coil surface temp determines the dew point of the discharge air. Low air-to-coil TD gives better (ie, higher) relative humidity) and low speed fans to slow dessication.
Just as in a flower box, you don't want to disturb the air layer next to the surface of the product, since vapor exchange first occurs in that layer.
If you are trying to dehumidify, what is the source of the humidity? If you exceed certain air velocities across coils you will throw moisture off. Is there a spray-washing process or some humidity producing source in the same space?
Even if the access to the room is from a warm, humid space, the evap coils should be pulling it right out again. If the system couldn't handle the latent load, you ought to see it in failure to maintain sensible level as well, but you are able actually to install heaters. I'm confused. .......But that's okay, I'm used to it!
Also strange for me because we see it everywhere the way I described.