Re: Contactor Coil Burning
loose connection can cause chattering , then the coil will burn out
Re: Contactor Coil Burning
Try looking elsewhere on your control circuit. You might have a faulty pressure switch or thermistor block which is making and breaking rapidly,this will cause the coil to overheat and possibly fail. If it is a defrost contractor look at your defrost termination control this can also cause chattering and eventually coil failure. Also you may want to check your neutral path as sometimes panel manufacturers link some of the neutrals together and just because your contactor neutral may look ok it might be further down the line where your fault is.
Re: Contactor Coil Burning
Check the coil voltage when the contractor is de-energised, obviously it should be zero, but any residual voltage (even a couple of volts) would produce heat in the coil without pulling the armature in & consequently burn it out.
Re: Contactor Coil Burning
i take it this has a neutral,not sure of your voltages over there between any two phases what voltage do you get and is it the same L1-L2,L2-L3,LI-L3,also L1-N etc,and when you say 30 amp contactor are you certain its up to the job in the amperage it can take is it the same as the original.
Re: Contactor Coil Burning
I would look for voltage surge from electronic card, maybe some small capacitors?
Re: Contactor Coil Burning
Hi
contactor coil burnout is usually due to either wrong voltage , or a missing neutral!!!
if the coil is totaly burnt and expanded, i would connect a neutral wire directly to the coil from the neutral bus.
if this is the only contactor with a problem in this board , i recommend you check the control circuit from output to coil input and make sure you arent feeding 400v by mistake or disconnecting neutral by mistake.
good luck
Re: Contactor Coil Burning
If electrical side checks out concentrate on lp/hp oil pressure switch if its short cycling at all it will cause strain on your contactor.
Re: Contactor Coil Burning
I had this same problem 3 times, the third time I realised that when I asked for the coil I asked for 400V when it should have been 230V. Strangely enough it worked when I first tested it, it was when I went back the third time I saw it didn't pull in it's self but when I pushed it in with screw driver it held and then chattered in and out rapidly.
Re: Contactor Coil Burning
I found a loose wire nut in a switch box a little away from the unit, thanks for suggestions, this was a mess to play with from the start
Re: Contactor Coil Burning
Loose wires can be a right pain to find as well.
Re: Contactor Coil Burning
just going blowing me trumpet!!
21-04-2013, 08:21 AM
http://www.refrigeration-engineer.co...tar14239_3.gifinstall monkey
Join DateOct 2007LocationmanchesterAge39Posts3,594Rep Power18
Re: Contactor Coil Burning
loose connection can cause chattering , then the coil will burn out
Re: Contactor Coil Burning
Good call install monkey. :-)