Could you apply the correct voltage to the LP switch to test the switch and controls work correctly?
Then trace back the wiring from the switch
What type of expansion valve are you using?
How does the rest of the system look? Subcooling, liquid line sight glass, filters and strainers
Hello,
As customers are requesting higher evap temps I am trying to determine the BTUH of our MT display cases at those requested temps. i.e 20°f,
Hello all
Can anyone point me in the right direction for fault code E41, (Compressor feedback, low pressure side)
plenty pressure
Re: Setting EPR and TXV
Are you calculating superheat on the evaporator pressure, upstream of EPR valve?
RANGER1 23-05-2024, 10:01 PM