View RSS Feed

nike123

  1. Presure-Entalpy chart explained

    Updated 07-08-2016 at 05:25 PM by nike123

    Tags: 1*17, dhpszvgt Add / Edit Tags
    Categories
    Uncategorized


  2. 9 superheat & subcooling scenarios

    Quote Originally Posted by nike123 View Post
    • LOW CHARGE = High superheat. Low suction pressure, indoor TD, subcooling, head pressure & compressor current draw.
    • OVER CHARGE = Low superheat. Normal indoor TD. High suction pressure, subcooling, head pressure & compressor current draw.
    • LOW INDOOR AIR FLOW = Low superheat & suction pressure. Low to normal head pressure. High indoor TD. High to normal subcooling. Not much effect on current draw.
    • MILD LOW OUTDOOR AIR FLOW = Low superheat & subcooling. High suction
    ...
    Categories
    Uncategorized
  3. Extending torque wrench correctly

  4. What is the purpose of having the capillary tube soldered to the suction line.

  5. Refrigerant circuit animation video

    Here is nice explanation:

    Updated 28-09-2013 at 08:10 AM by nike123

    Categories
    Uncategorized
Page 1 of 2 12 LastLast